I am glad to see this is not just me having such problems.  I want to find
the root cause for all of those who suffer this bug.  If I have the USB
cable plugged in while the systems boot, it's a 50/50 chance of working, or
power cycling.  If it does work, then I live in fear of the next reboot!
-Adam

Nut version:
nut            2.7.4-8

On Tue, Feb 2, 2021 at 8:06 AM Fairfax, Charles A. via Nut-upsuser <
nut-upsuser@alioth-lists.debian.net> wrote:

> Sorry, the list address got dropped on prior send.
>
> Charles Fairfax
>
> -----Original Message-----
> From: Fairfax, Charles A.
> Sent: Tuesday, February 2, 2021 9:18 AM
> To: David Zomaya <david_zom...@tripplite.com>; Adam Talbot <
> ajtalb...@gmail.com>
> Subject: RE: [Nut-upsuser] [EXTERNAL] Tripp Lite "Remote Shutdown" when
> USB cable is attached
>
> I don't know that my experience is helpful except that I had what sounds
> like a similar experience with a similar UPS in October of 2016.  I was
> attaching a Raspberry Pi (Raspbian wheezy) with NUT 2.6.4 to a TrippLite
> SU3000XLCD via USB and the UPS shut down, dropping the load.  I had never
> seen this  happen before with the 8 or so other older model TrippLite UPSs
> I have in service.
>
> Unfortunately I was not at liberty to perform much troubleshooting owing
> to the nature of the load and don't have another UPS of the same model.  I
> tried serial communication but was not successful.  Eventually I did get
> the UPS link to work.   If I remember correctly I booted the Pi after
> connecting the USB cable.  It has been working since and I have not
> unplugged the USB cable.
>
> Have you tried booting the computer after connecting the USB cable?
>
> -----Original Message-----
> From: Nut-upsuser <nut-upsuser-bounces+fairfaxc=
> missouri....@alioth-lists.debian.net> On Behalf Of David Zomaya via
> Nut-upsuser
> Sent: Monday, February 1, 2021 4:43 PM
> To: Adam Talbot <ajtalb...@gmail.com>; nut-upsuser@alioth-lists.debian.net
> Subject: Re: [Nut-upsuser] [EXTERNAL] Tripp Lite "Remote Shutdown" when
> USB cable is attached
>
> I don't have a quick answer for you but I'll be in the office later this
> week and can grab a model with the same protocol and run a test on one of
> my Ubuntu boxes (which should be close enough to your Pi setup).
>
>
> Thank you,
> David Zomaya
> Tripp Lite
>
>
>
>
>
>
>
>
> From: Nut-upsuser <nut-upsuser-bounces+david_zomaya=
> tripplite....@alioth-lists.debian.net> on behalf of Adam Talbot via
> Nut-upsuser <nut-upsuser@alioth-lists.debian.net>
> Sent: Monday, February 1, 2021 3:39 PM
> To: nut-upsuser@alioth-lists.debian.net
> Subject: [EXTERNAL] [Nut-upsuser] Tripp Lite "Remote Shutdown" when USB
> cable is attached
>
> This is an EXTERNAL email. Please take a moment and think before clicking
> any links or opening any attachments from this email. If suspicious, please
> forward to ishelpd...@tripplite.com for review.
> I am kinda stuck on this one.  Whenever I attach (USB to a linux box) my
> TrippLite UPS, it "REMOTE SHUTDOWN".  This is a new problem that has
> cropped up in the last 6 months.  At first I thought it was a NUT
> configuration issue, but now I believe this  to be some kind of kernel
> bug?  When I plug in the UPS, I can see the system logs show the UPS, then
> everything powers off.
>
>
> UPS LCD shows the below error when I plug in the USB cable:
> "OUTPUT OFF"
> "REMOTE SHUTDOWN"
>
>
> I tested this against 2 different X86 boxes and a Raspberry Pi. All cause
> the same result in the UPS.  Only one box (nas) has NUT installed and
> configured.
>
>
> UPS is a Tripp Lite SU3000RTXLCD2U.
>
>
> I am totally stumped on this one.  Below is a dump of basically all my
> specs.  Any ideas?
> -Adam
>
>
>
> root@nas:~# uname -a
> Linux nas 5.4.78-2-pve #1 SMP PVE 5.4.78-2 (Thu, 03 Dec 2020 14:26:17
> +0100) x86_64 GNU/Linux
>
> root@nas:~# cat /etc/nut/nut.conf
> MODE=netserver
> root@nas:~# cat /etc/nut/ups.conf
> [ups1]
> driver=usbhid-ups
> port=auto
> root@nas:~# cat /etc/nut/upsd.conf
> LISTEN 127.0.0.1 3493
> LISTEN 10.1.1.2
> root@nas:~# cat /etc/nut/upsmon.conf
> root@nas:~# cat /etc/nut/upssched.conf
> root@nas:~#
>
> root@nas:~# cat /etc/debian_version
> 10.7
>
>
>
> Before all this broke, I was able to monitor the UPS and get the following
> info:
> battery.charge: 100
> battery.charge.low: 20
> battery.charge.warning: 20
> battery.runtime: 6662
> battery.temperature: 29.9
> battery.type: PbAc
> battery.voltage: 81.0
> battery.voltage.nominal: 72.0
> device.mfr: TRIPPLITE
> device.model: TRIPPLITE UPS
> device.serial: XXXXXXXXXXXXXX
> device.type: ups
> driver.name:  usbhid-ups
> driver.parameter.pollfreq: 30
> driver.parameter.pollinterval: 2
> driver.parameter.port: auto
> driver.parameter.synchronous: no
> driver.version: 2.7.4
> driver.version.data: TrippLite HID 0.82
> driver.version.internal: 0.41
> input.frequency: 60.0
> input.transfer.high: 150.0
> input.transfer.high.max: 150
> input.transfer.high.min: 145
> input.transfer.low: 55.0
> input.transfer.low.max: 60
> input.transfer.low.min: 55
> input.voltage: 123.0
> input.voltage.nominal: 120
> output.current: 1.9
> output.frequency: 60.0
> output.frequency.nominal: 60
> output.voltage: 120.0
> output.voltage.nominal: 120
> ups.beeper.status: enabled
> ups.delay.shutdown: 20
> ups.delay.start: 30
> ups.firmware: 64
> ups.load: 8
> ups.mfr: TRIPPLITE
> ups.model: TRIPPLITE UPS
> ups.power: 226.0
> ups.power.nominal: 3000
> ups.productid: 4004
> ups.serial: 2620ELCPS87A200020
> ups.status: OL
> ups.test.result: Done and passed
> ups.timer.reboot: 0
> ups.timer.shutdown: -1
> ups.timer.start: 0
> ups.vendorid: 09ae
> ups.watchdog.status: 0
>
>
> root@nas:/var/log# zcat messages.*.gz | grep -i tripp
> Jan 15 11:05:05 nas kernel: [    1.571857] usb 3-1: Product: TRIPPLITE UPS
> Jan 15 11:05:05 nas kernel: [    1.571858] usb 3-1: Manufacturer: TRIPPLITE
> Jan 15 11:05:05 nas kernel: [    1.629210] hid-generic
> 0003:09AE:4004.0001: hiddev0,hidraw0: USB HID v1.11 Device [TRIPPLITE
>   TRIPPLITE UPS   ] on usb-0000:2e:00.3-1/input0
>
>
>
> ________________________________
>  This message is for the addressee's use only. It may contain confidential
> information. If you receive this message in error, please delete it and
> notify the sender. Tripp Lite disclaims all warranties and liabilities, and
> assumes no responsibility for viruses which may infect an email sent to you
> from Tripp Lite and which damage your electronic systems or information. It
> is your responsibility to maintain virus detection systems to prevent
> damage to your electronic systems and information.
>
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser@alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
> _______________________________________________
> Nut-upsuser mailing list
> Nut-upsuser@alioth-lists.debian.net
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
_______________________________________________
Nut-upsuser mailing list
Nut-upsuser@alioth-lists.debian.net
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to