Thanks for that, Charles. The "ignorelb" setting did exactly what I needed. 
Although, as it turns out, I didn't need it :-/ I'm new to NUT so this is a new 
install and I didn't know that the driver would actually shutdown the UPS; this 
is why the power ran out before the shutdown of my remote systems had 
completed. By disabling that functionality, the original 5 mins was sufficient. 
I don't need the UPS shutdown functionality, I just need everything cleanly 
shutdown before the battery runs out. 

Thanks again.

> On 24 Feb 2021, at 14:03, Charles Lepple <[email protected]> wrote:
> 
> On Feb 24, 2021, at 4:02 AM, Peter Bishop via Nut-upsuser 
> <[email protected]> wrote:
>> 
>> I have an APC BR1500GI and want to run my devices for the longest possible 
>> period. Consequently I want to use the battery.runtime.low setting, 
>> sufficient to allow my devices to shutdown. The APC has a setting of 5 
>> minutes for this purpose but I want to change this to 10 minutes, so have 
>> added the “override.battery.runtime.low = 600” setting to the ups.conf file. 
>> However, this override doesn’t appear to be causing the NUT setup to 
>> initiate a shutdown.
>> 
>> Does the “override.battery.runtime.low” work for this purpose or does it 
>> just change the value being displayed by upsc? If it’s the latter, is there 
>> a way to achieve the override for the low battery setting? For testing 
>> purposes I changed this value to “2500”, switched off the mains, and 
>> monitored the “battery.runtime” value. It dropped below “2500” (and remained 
>> there) but the “battery is low” message was never generated.
> 
> The override.* settings can cover both cases. If you just provide 
> override.battery.runtime.low, you are just replacing what is sent from the 
> driver to upsd, and then on to clients like upsc. (In particular, this 
> doesn't send any settings adjustments back to the UPS.) Since upsmon is 
> watching ups.status for the UPS-provided LB bit (by default), this isn't 
> sufficient to modify shutdown behavior.
> 
> The subtle difference in examples like this:
> 
>   
> https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Falioth-lists.debian.net%2Fpipermail%2Fnut-upsuser%2F2020-August%2F011977.html&amp;data=04%7C01%7C%7C09b7427293084d87c1a208d8d8ccec7a%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637497721942032252%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=yG%2BP5BARevtBvoJ2vjYvg11sCJgWG8p6Gr1dNxTrnUs%3D&amp;reserved=0
> 
> is the use of "ignorelb" in concert with "override.battery.runtime.low".
> 
> I also ran across this thread while looking up info on the BR1500GI:
> 
>   
> https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Falioth-lists.debian.net%2Fpipermail%2Fnut-upsuser%2F2020-November%2F012172.html&amp;data=04%7C01%7C%7C09b7427293084d87c1a208d8d8ccec7a%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637497721942032252%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=CGNtzukW%2FPj8dZSKI6br6VPwjzx2Z9bwGcFVhTmTNCI%3D&amp;reserved=0
> 
> I don't think we resolved the shutdown issue (or got debug logs to dig 
> deeper).
> 
>> 
>> Required information:
>> 
>>                OS: Linux **** 5.4.83+ #1379 Mon Dec 14 13:06:05 GMT 2020 
>> armv6l GNU/Linux
>>                NUT version: 2.7.4-8
>>                NUT installation: package
>>                UPS: APC BR1500GI
> 
> Thanks, appreciate the info!
> 
>> 
>> Thanks.
>> _______________________________________________
>> Nut-upsuser mailing list
>> [email protected]
>> https://apac01.safelinks.protection.outlook.com/?url=https%3A%2F%2Falioth-lists.debian.net%2Fcgi-bin%2Fmailman%2Flistinfo%2Fnut-upsuser&amp;data=04%7C01%7C%7C09b7427293084d87c1a208d8d8ccec7a%7C84df9e7fe9f640afb435aaaaaaaaaaaa%7C1%7C0%7C637497721942032252%7CUnknown%7CTWFpbGZsb3d8eyJWIjoiMC4wLjAwMDAiLCJQIjoiV2luMzIiLCJBTiI6Ik1haWwiLCJXVCI6Mn0%3D%7C1000&amp;sdata=DbHwKj%2FdmBvqsS6w3DPEKWZcXewixzXbtIwPBVN1wpQ%3D&amp;reserved=0
> 
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to