I tried removing the -D flags from the command and it still failed.

Here's the unit file:

[Unit]
Description=Network UPS Tools - power device monitor and shutdown controller
After=local-fs.target network.target nut-server.service
OnFailure=systemd-monitor@%n.service

[Service]
ExecStart=/usr/sbin/upsmon
PIDFile=/run/upsmon.pid
Type=forking

[Install]
WantedBy=multi-user.target

On Mon, Aug 30, 2021 at 3:35 PM Jim Klimov <[email protected]> wrote:
>
> On August 30, 2021 12:02:14 AM UTC, Nathan Dehnel via Nut-upsuser 
> <[email protected]> wrote:
> >The systemd service fails even though the output seems to indicate
> >that nut-monitor is communicating successfully with the UPS.
> >
> >Gentoo Linux
> >
> >Nut v2.7.4-r7 (installed from distro package)
> >
> >UPS: Tripplite SU1500RTXLCD2U (controlled by pfsense)
> >
> >journalctl output:
> >
> >-- Boot 93e0d5b24bac491994a2ea5cce08cdcc --
> >Aug 16 23:45:40 gentoodesktop systemd[1]: Starting Network UPS Tools -
> >power device monitor and shutdown controller...
> >░░ Subject: A start job for unit nut-monitor.service has begun
> >execution
> >░░ Defined-By: systemd
> >░░ Support: https://gentoo.org/support/
> >░░
> >░░ A start job for unit nut-monitor.service has begun execution.
> >░░
> >░░ The job identifier is 107.
> >Aug 16 23:45:40 gentoodesktop upsmon[1943]: kill: No such process
> >Aug 16 23:45:40 gentoodesktop upsmon[1943]:    0.000000        UPS:
> >tripplite1@pfsense (slave) (power value 1)
> >Aug 16 23:45:40 gentoodesktop upsmon[1943]:    0.000019        UPS:
> >heartbeat@localhost (monitoring only)
> >Aug 16 23:45:40 gentoodesktop upsmon[1943]:    0.000051        Using
> >power down flag file /etc/killpower
> >Aug 16 23:45:40 gentoodesktop upsmon[1943]:    0.000127        debug
> >level is '8'
> >Aug 16 23:45:40 gentoodesktop upsmon[1944]:    0.003931        Trying
> >to connect to UPS [tripplite1@pfsense]
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.452582        UPS
> >[tripplite1@pfsense]: connect failed: No such host
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.452600
> >do_notify: ntype 0x0005 (COMMBAD)
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.452725        Trying
> >to connect to UPS [heartbeat@localhost]
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.453032        Can not
> >connect to localhost in SSL, continue uncrypted
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457065        Logged
> >into UPS heartbeat@localhost
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457104
> >pollups: heartbeat@localhost
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457110
> >get_var: heartbeat@localhost / status
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457142
> >parse_status: [OL]
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457148        parsing:
> >[OL]
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457151
> >ups_on_line: heartbeat@localhost (first time)
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457154        Current
> >power value: 1
> >Aug 16 23:45:52 gentoodesktop upsmon[1944]:   12.457157        Minimum
> >power value: 1
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.457224        Trying
> >to connect to UPS [tripplite1@pfsense]
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.457992        Can not
> >connect to pfsense in SSL, continue uncrypted
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458515        Logged
> >into UPS tripplite1@pfsense
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458525
> >pollups: tripplite1@pfsense
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458529
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458629
> >parse_status: [OL]
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458637
> >do_notify: ntype 0x0004 (COMMOK)
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458640
> >Communications with UPS tripplite1@pfsense established
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458811        parsing:
> >[OL]
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458822
> >ups_on_line: tripplite1@pfsense (first time)
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458824
> >pollups: heartbeat@localhost
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458826
> >get_var: heartbeat@localhost / status
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458880
> >parse_status: [OL]
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458887        parsing:
> >[OL]
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458890
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458892        Current
> >power value: 1
> >Aug 16 23:45:57 gentoodesktop upsmon[1944]:   17.458894        Minimum
> >power value: 1
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/0: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/1: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/11: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/8: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/4: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2076]: wall: /dev/pts/9: No such
> >file or directory
> >Aug 16 23:45:57 gentoodesktop upsmon[2075]: Network UPS Tools upsmon
> >2.7.4
> >Aug 16 23:46:00 gentoodesktop upsmon[1947]: Failed to connect to
> >parent and failed to create parent: No such file or directory
> >Aug 16 23:46:00 gentoodesktop upssched[1947]: Failed to connect to
> >parent and failed to create parent: No such file or directory
> >Aug 16 23:46:00 gentoodesktop upsmon[1946]: Network UPS Tools upsmon
> >2.7.4
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.458958
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.458973
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459248
> >parse_status: [OL]
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459251        parsing:
> >[OL]
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459253
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459255
> >pollups: heartbeat@localhost
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459257
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459293
> >parse_status: [OL]
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459296        parsing:
> >[OL]
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459299
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459301        Current
> >power value: 1
> >Aug 16 23:46:04 gentoodesktop upsmon[1944]:   22.459304        Minimum
> >power value: 1
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459380
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459394
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459677
> >parse_status: [OL]
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459681        parsing:
> >[OL]
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459682
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459684
> >pollups: heartbeat@localhost
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459686
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459722
> >parse_status: [OL]
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459725        parsing:
> >[OL]
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459727
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459729        Current
> >power value: 1
> >Aug 16 23:46:07 gentoodesktop upsmon[1944]:   27.459731        Minimum
> >power value: 1
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.459807
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.459822
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460038
> >parse_status: [OL]
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460041        parsing:
> >[OL]
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460043
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460044
> >pollups: heartbeat@localhost
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460046
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460086
> >parse_status: [OL]
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460088        parsing:
> >[OL]
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460089
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460091        Current
> >power value: 1
> >Aug 16 23:46:12 gentoodesktop upsmon[1944]:   32.460093        Minimum
> >power value: 1
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.140972
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.140986
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141227
> >parse_status: [OL]
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141230        parsing:
> >[OL]
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141232
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141234
> >pollups: heartbeat@localhost
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141236
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141286
> >parse_status: [OL]
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141288        parsing:
> >[OL]
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141290
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141292        Current
> >power value: 1
> >Aug 16 23:46:19 gentoodesktop upsmon[1944]:   39.141294        Minimum
> >power value: 1
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141355
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141371
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141610
> >parse_status: [OL]
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141613        parsing:
> >[OL]
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141615
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141617
> >pollups: heartbeat@localhost
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141618
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141652
> >parse_status: [OL]
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141654        parsing:
> >[OL]
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141656
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141658        Current
> >power value: 1
> >Aug 16 23:46:24 gentoodesktop upsmon[1944]:   44.141659        Minimum
> >power value: 1
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141723
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141737
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141981
> >parse_status: [OL]
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141985        parsing:
> >[OL]
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141987
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141989
> >pollups: heartbeat@localhost
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.141990
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.142026
> >parse_status: [OL]
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.142028        parsing:
> >[OL]
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.142030
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.142032        Current
> >power value: 1
> >Aug 16 23:46:29 gentoodesktop upsmon[1944]:   49.142034        Minimum
> >power value: 1
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142098
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142116
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142405
> >parse_status: [OL]
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142411        parsing:
> >[OL]
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142415
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142418
> >pollups: heartbeat@localhost
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142420
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142463
> >parse_status: [OL]
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142466        parsing:
> >[OL]
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142468
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142471        Current
> >power value: 1
> >Aug 16 23:46:34 gentoodesktop upsmon[1944]:   54.142473        Minimum
> >power value: 1
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142539
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142560
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142807
> >parse_status: [OL]
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142810        parsing:
> >[OL]
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142812
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142815
> >pollups: heartbeat@localhost
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142817
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142859
> >parse_status: [OL]
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142862        parsing:
> >[OL]
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142865
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142867        Current
> >power value: 1
> >Aug 16 23:46:39 gentoodesktop upsmon[1944]:   59.142869        Minimum
> >power value: 1
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.142936
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.142961
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143253
> >parse_status: [OL]
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143263        parsing:
> >[OL]
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143267
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143271
> >pollups: heartbeat@localhost
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143275
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143339
> >parse_status: [OL]
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143343        parsing:
> >[OL]
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143346
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143349        Current
> >power value: 1
> >Aug 16 23:46:44 gentoodesktop upsmon[1944]:   64.143353        Minimum
> >power value: 1
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143418
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143432
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143670
> >parse_status: [OL]
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143673        parsing:
> >[OL]
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143676
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143678
> >pollups: heartbeat@localhost
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143680
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143721
> >parse_status: [OL]
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143724        parsing:
> >[OL]
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143727
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143730        Current
> >power value: 1
> >Aug 16 23:46:51 gentoodesktop upsmon[1944]:   69.143732        Minimum
> >power value: 1
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.143797
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.143818
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144094
> >parse_status: [OL]
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144097        parsing:
> >[OL]
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144099
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144100
> >pollups: heartbeat@localhost
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144103
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144143
> >parse_status: [OL]
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144147        parsing:
> >[OL]
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144150
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144153        Current
> >power value: 1
> >Aug 16 23:46:54 gentoodesktop upsmon[1944]:   74.144155        Minimum
> >power value: 1
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144221
> >pollups: tripplite1@pfsense
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144249
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144484
> >parse_status: [OL]
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144489        parsing:
> >[OL]
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144491
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144494
> >pollups: heartbeat@localhost
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144497
> >get_var: heartbeat@localhost / status
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144554
> >parse_status: [OL]
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144558        parsing:
> >[OL]
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144560
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144563        Current
> >power value: 1
> >Aug 16 23:46:59 gentoodesktop upsmon[1944]:   79.144566        Minimum
> >power value: 1
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144636
> >pollups: tripplite1@pfsense
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144664
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144934
> >parse_status: [OL]
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144942        parsing:
> >[OL]
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144945
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144947
> >pollups: heartbeat@localhost
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.144950
> >get_var: heartbeat@localhost / status
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.145008
> >parse_status: [OL]
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.145013        parsing:
> >[OL]
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.145015
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.145018        Current
> >power value: 1
> >Aug 16 23:47:04 gentoodesktop upsmon[1944]:   84.145021        Minimum
> >power value: 1
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145087
> >pollups: tripplite1@pfsense
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145107
> >get_var: tripplite1@pfsense / status
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145389
> >parse_status: [OL]
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145394        parsing:
> >[OL]
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145397
> >ups_on_line: tripplite1@pfsense (no change)
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145399
> >pollups: heartbeat@localhost
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145404
> >get_var: heartbeat@localhost / status
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145450
> >parse_status: [OL]
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145453        parsing:
> >[OL]
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145455
> >ups_on_line: heartbeat@localhost (no change)
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145458        Current
> >power value: 1
> >Aug 16 23:47:09 gentoodesktop upsmon[1944]:   89.145460        Minimum
> >power value: 1
> >Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service: start
> >operation timed out. Terminating.
> >Aug 16 23:47:12 gentoodesktop upsmon[1944]:   91.852466        Signal
> >15: exiting
> >Aug 16 23:47:12 gentoodesktop upsmon[1944]:   91.852486
> >Dropping connection to UPS [tripplite1@pfsense]
> >Aug 16 23:47:12 gentoodesktop upsmon[1944]:   91.852556
> >Dropping connection to UPS [heartbeat@localhost]
> >Aug 16 23:47:12 gentoodesktop upsmon[1944]: Network UPS Tools upsmon
> >2.7.4
> >Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service: Failed
> >with result 'timeout'.
> >░░ Subject: Unit failed
> >░░ Defined-By: systemd
> >░░ Support: https://gentoo.org/support/
> >░░
> >░░ The unit nut-monitor.service has entered the 'failed' state with
> >result 'timeout'.
> >Aug 16 23:47:12 gentoodesktop systemd[1]: Failed to start Network UPS
> >Tools - power device monitor and shutdown controller.
> >░░ Subject: A start job for unit nut-monitor.service has failed
> >░░ Defined-By: systemd
> >░░ Support: https://gentoo.org/support/
> >░░
> >░░ A start job for unit nut-monitor.service has finished with a
> >failure.
> >░░
> >░░ The job identifier is 107 and the job result is failed.
> >Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service:
> >Triggering OnFailure= dependencies.
> >Aug 16 23:47:12 gentoodesktop systemd[1]: nut-monitor.service:
> >Consumed 2.054s CPU time.
> >░░ Subject: Resources consumed by unit runtime
> >░░ Defined-By: systemd
> >░░ Support: https://gentoo.org/support/
> >░░
> >░░ The unit nut-monitor.service completed and consumed the indicated
> >resources.
> >
> >_______________________________________________
> >Nut-upsuser mailing list
> >[email protected]
> >https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
> I did not have experience with Gentoo lateely, but by symptoms this looks 
> like a service defined maybe as "forking" but behaving as "simple"  - e.g. 
> starting with customized `upsmon -D` which keeps it foregrounded and not 
> forking?
>
> There was also an issue a few months ago that the PID files for root and 
> non-root processes of the client could be misleading for frameworks like 
> systemd.
>
> Hope these OTOH ideas help,
> Jim
>
> --
> Typos courtesy of K-9 Mail on my Android

_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to