Hi,
Thanks for the confirmation regarding the FSD flag.
I tried to use nut-ipmipsu for this, since the PSUs were picked up by
nut-scanner on my test server. But I wasn't successful in configuring
the driver correctly, or maybe it's not yet compatible with my chassis
at its current version. I'll try to work on that in the next few days.
If not I'll dive in upssched to see if a solution lies there.
Thanks
Arthur Desplanches
On 4/17/22 01:13, Jim Klimov wrote:
As far as I know the FSD flag by design can only be raised; many
phrases refer to it as "latching" - much for the same reasons as you
outlined: people usually want the datacenter in a predictable
hands-off state. If something begins to shut down due to critical
power state of the UPS, everything should power-cycle and come up
together and in order. So the only way to clear FSD is to restart the
daemons raising it.
Note some UPSes and their smart drivers would treat as critical any
situation where battery charge is under a certain threshold - even if
online and charging at the moment, since the UPS is too depleted for a
safe shutdown if power is lost again.
I wonder if you can fiddle with ipmi-psu driver for your case. NUT has
a way to treat blade chassis as an ePDU for the blades. Maybe you can
get upsmon to monitor an UPS and the other PSU on redundant-PSU systems.
Also see if some smarter scripting with upssched (as the handler of
signals from upsmon for complex situations) can help...
Hope this helps,
Jim Klimov
On Fri, Apr 15, 2022, 14:17 Arthur Desplanches <[email protected]>
wrote:
Hi,
I'm working on deploying NUT for our main server room, and I've put
myself in a situation where there could be an edge case that I don't
really like, and so I'm asking for a bit of guidance.
Most of the deploymentis fairly standard according to the
documentation
(big thanks for its exhaustiveness, by the way), the main change
is my
shutdown script. It checks if we have power on both PSUs using
IPMI, and
if this is the case, it doesn't shut down (in any other case it
does :
ipmi doesn't work, only one PSU is receiving power, only one PSU
exists
on the machine, etc). We did this because about 90% of our
machines have
dual redundant PSUs, with one on the UPS, the other on mains buton a
separate circuit. So we could have a situation where the UPS loses
power, but we still have some on a secondary circuit.
We choose to accept the fact that if the secondary circuit loses
power
after our NUT server sent a force shutdown sequence, we may have a
bad
shutdown at this point.
What could happen in this situation, is that a machine that is a
nut-server (A) still has the FSD flag running (because it didn't shut
itself down) even after power comes back and some machines
restart. In
this case, the upsmon on the freshly started machines will see the
flag
and then shut themselves down again.
Our workaround currently would be to be aware of this and restart
nut-server and then nut-monitor on the machine A before starting back
any of its clients that is currently down.
Is there any idea of a better way to handle this edge case ? Or a
better
way to articulate this ? Maybe a way to automatically clear the
FSD flag ?
Thanks for the help
Arthur
--
Arthur Desplanches
Sysadmin @ BUF Compagnie (buf.com <http://buf.com>)
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
--
Arthur Desplanches