I have little useful wisdom, but: Phil Chadwick <[email protected]> writes:
> I have NUT installed on FreeBSD 13.0-RELEASE-p11. It's installed from a > standard package, derived from nut-2.7.4.tar.gz. That's now out of date; 2.8.0 is out. (I don't have any reason to think that is related to your issue.) > I am suffering from a bug regarding the "ondelay" setting in ups.conf: > > https://github.com/networkupstools/nut/issues/625 > > The "ondelay" setting in ups.conf is applied to "ups.delay.start" inside the > UPS non-volatile memory. > > The difference between CP1500EPFCLCD UPSs and others is: > > - other UPSs apply ups.delay.start seconds AFTER wall power returns; and > - the CP1500EPFCLCD applies ups.delay.start seconds AFTER shutdown. > > So if I set "offdelay = 90" and "ondelay = 100" the UPS re-starts 10 seconds > after it shuts down. The only way to stop this (and leave the UPS shut down > until wall power returns) is to set "ondelay = 0". > > This means that the CP1500EPFCLCD (and probably similar CyberPower UPSs) have > no option to delay the power up load. It's always immediate. So there is > no chance to charge the batteries, or allow another UPS to bring up the > network first. Probably you don't want to do this and shouldn't (vs getting a UPS that works correctly), but it would seem possible to have a microcontroller that boots and waits a bit and then closes a relay, so that your loads don't get power for a while even though the UPS is onl