On 2022-06-05 09:06, Phil Chadwick wrote:
Hi,
I have a CyberPower CP1500EPFCLCD.
I live in a rural location and experience frequent power failures.
I run a nut server on a FreeBSD host named "sherman". It has a USB
connection to the CP1500EPFCLCD, using the usbhid-ups driver. I don't
use
nut clients, preferring to use one-shot root privileged ssh keys to
execute
remote commands (i.e. shutdown) on the "network peers" of the nut
server.
The CP1500EPFCLCD has firmware "issues", and I expect that there's a
very
good chance that the CP1300EPFCLCD is the same.
The USB connection experiences a transient disconnect when power drops.
If the connection loss lasts couple sec max I guess it's something I and
NUT
can live with, since as you mention it doesn't seem to affect how NUT
operates.
I received another reply from the list that mentioned that for the 900VA
model
there was no problem with the USB connection. I have to wonder whether
that is
a result of the ephemeral connection loss.
The major firmware issue I tripped over is with "ups.delay.start".
See:
https://alioth-lists.debian.net/pipermail/nut-upsuser/2018-October/011253.html
The nut manual says set ups.delay.start (default 30) as the interval to
wait
before restarting the load (seconds) [AFTER UPS power returns]. The
CyberPower CP1500EPFCLCD UPS restarts ups.delay.start seconds after the
UPS
is shutdown REGARDLESS of the wall power status. i.e. regardless of
mains
status:
- ondelay=0, UPS powers on the load when mains return
- ondelay=-1, UPS never powers on the load, even when mains return
- ondelay=xx, UPS powers on the load after xx (roughly) seconds
after UPS shutdown is executed.
I have reported this issues to CyberPower support, but got no
satisfactory
resolution. It's a serious problem...
This bug makes using "battery.charge.low" pretty much impossible,
because
with a low battery you need to re-charge the battery AFTER wall power
returns and BEFORE restarting the load to power up the clients -- lest
you go into an infinite shutdown/reboot loop. The faulty handling of
ups.delay.start prevents the battery from re-charging to a workable
level
after discharge (unless you set ondelay=-1, which means you can't power
up automatically).
Can you share a link to where the manual describes ups.delay.start? I
found
some information but not the complete description you mention here.
For ondelay=0 what happens? The load instantly returns on UPS shutdown
or
the bug doesn't trigger?