On the road now so gotta come back to main question later, but for now -
why 2.8.0-rc3 (not "r3")? There is a newer final release, or current
master... just asking.

Notably, there was a fix in master last week or so that moght help woth
some broken large queries for SNMPv2/v3... No idea if that's your case
though. Error messages from clients might help.

Jim

On Wed, Oct 26, 2022, 17:57 Andre Mueller via Nut-upsuser <
[email protected]> wrote:

>
> Hello
>
> Becoming somewhat "desperate" I configured and tested (for hours) to get
> a NUT-Server/Client 2.8.0r3 installation to work together with a
> CyberPower OLS1500 UPS over SNMP v3.
>
> As NUT-packages for  ubuntu are still at version 2.7.4 and this
> NUT-SNMP-driver does not report very much information from the
> CyberPower UPS, I decided to compile/install from source the 2.8.0r3
> version with the following configure settings:
>
>
> ./configure --with-snmp --with-cgi --with-scanner  -with-docs
> --with-user=root --with-group=nut  --sysconfdir=/etc/nut/
>
>
> now with version 2.8.0r3 I get over upsc full information from my ups
> (named ups00) over SNMP. Also NUT-cgi reports full information and is
> refreshed accordingly.
>
>
> /usr/local/ups/bin/upsc ups00
> battery.charge: 100
> battery.current: 1
> battery.runtime: 2880
> battery.runtime.elapsed: 0
> battery.voltage: 54.60
> battery.voltage.nominal: 48
> device.contact: Administrator
> device.description: UPS SNMP Card
> device.location: Server Room
> device.mfr: CYBERPOWER
> device.model: OLS1500ERT2UA
> device.serial: 3003070Z30000042
> device.type: ups
> driver.name: snmp-ups
> driver.parameter.pollinterval: 1
> driver.parameter.port: 192.168.1.10
> driver.parameter.secLevel: authPriv
> driver.parameter.snmp_version: v3
> driver.parameter.synchronous: auto
> driver.version: 2.8.0-rc3
> driver.version.data: cyberpower MIB 0.51
> driver.version.internal: 1.21
> input.frequency: 49.90
> input.voltage: 232.50
> output.current: 1
> output.frequency: 49.90
> output.voltage: 232.50
> ups.delay.reboot: 0
> ups.delay.shutdown: 180
> ups.delay.start: 0
> ups.firmware: OS02RV07
> ups.load: 17
> ups.mfr: CYBERPOWER
> ups.model: OLS1500ERT2UA
> ups.serial: 3003070Z30000042
> ups.status:
>
>
> Also the NUT-Server (v2.8.0r3) seems to works correct and 3 NUT-clients
> (1 local, 2 remote) can login correctly to the NUT-Server and to the ups00.
>
>
> nut-server[1069]: User [email protected] logged into UPS [ups00]
> upsd[1069]: User [email protected] logged into UPS [ups00]
> nut-server[1069]: User [email protected] logged into UPS [ups00]
> upsd[1069]: User [email protected] logged into UPS [ups00]
> nut-server[1069]: User [email protected] logged into UPS [ups00]
> upsd[1069]: User [email protected] logged into UPS [ups00]
>
>
> Unfortunately all NUT-clients (also the local NUT-client) are reporting
> directly after the first refresh and then continuously, that they have
> lost connenctions to the ups00 but they are still loggedin to the
> NUT-Server.
>
> ...
> nut-monitor[1078]: UPS ups00@localhost is unavailable
> nut-monitor[29503]: Network UPS Tools upsmon 2.8.0-rc3
> ...
>
> So my question is, what could be "wrong" in configuration and/or
> installation, that all clients (local or remote) are reporting that they
> have lost connection to the ups00 and that it is not unavailable?
>
>
> Many thanks in advance for any hint, best
>
>
>
>
>
>
>
>
> _______________________________________________
> Nut-upsuser mailing list
> [email protected]
> https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser
>
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to