May be, I don't know. My UPS doesn't autopower on after charging its
batteries full.
Anyway how do I test it? There has to be some specific way of shutting
down to see if that works or not.
01.01.2023 20:41, Jim Klimov пише:
With some APC rack SmartUPSes of early 2000's, as well as some larger
Eaton devices, I remember them auto-powering on the load only after
they charge "enough" (configurable in Eatons at least) to run for say
10 minutes - so they can tell the load to power off and hold it up
long enough to guarantee safe shutdown if another outage happens. So
those do turn on, but after an hour or so. Can this be your case?
Jim
On Sun, Jan 1, 2023, 19:00 Gennadiy Poryev via Nut-upsuser
<[email protected]> wrote:
Yes, that one. It made me thinking there might be some sidetrick
to do an actual shutdown.return even if it is currently reported
as not available.
Yes, I know all these technicalities. Fortunately, load.off.delay
works as expected in my case, with a granularity of a second,
because of course I live-tested it. Determinate or not, 15 seconds
turned out to be enough for all servers to shutdown themselves so
by the time load is turned off, nothing is working from it. That
is not the problem.
No, the power won't return that quick. It usually takes 3 to 4
hours. Local specifics, so no power races in this case. Not the
problem also.
I am not newbie to the Linux world as I use Gentoo throughout, but
I wasn't able to quickly figure out how to setup
upsmon(+upssched?) to perform the tasks I need. The workflow I
need seems to be marginal compared to the typical scenarios.
Custom solution also allows me to integrate things like SMS
notification in the process.
But once again, this is not the problem.
The problem is getting UPS to turn on the load as soon as power
mains returns. Servers will start automatically. If a way to do
this with my model is discovered, I will modify my daemon to use
it instead of just load.off.delay'ing.
So, where do I look/dig ? Or is this a dead end and I better buy
other UPS model with an actual support?
Best regards,
G.
So the daemon I wrote connects to upsd and monitors
input.voltage and
ups.status. BTW had to override pollinterval = 1 and pollfreq
= 1 in
ups.conf to make input.voltage report input voltage in more
or less
real-time instead of cached.
The code logic is such that as soon as input.voltage goes below
input.transfer.low and ups.status goes from OL to OB the farm
shutdown
is initiated and ups is issued INSTCMD load.off.delay command
and is
smart enough to shut itself down too.
So far this part of the project works OK -- the farm turns
itself off
nicely and unattended.
BUT.
There seem to be lack of facility to do shutdown.return
though. Still
have to to that manually each time.
I've attached upsc/upscmd/upsrw outputs but so far haven't
figured out a
combination that might do the trick. Provided my UPS can do
it, of
course, but why shouldn't it?
From what I've read in the certain discussion on this
maillist that
occurred 12 years ago and from nut documentation I suspect
the hope is
not lost and it is possible to somehow hack in proper
shutdown.return
But my expertise ends here. Should anyone help me run all the
debug mode
magic I've read of and make good use of it, my thankfullness
will have
no bounds.
Best regards,
G.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser