Hello!
I left this line uncommented in powercom-hid.c for battery voltage:
{ "battery.voltage", 0, 0, "UPS.Battery.Voltage", NULL, "%.2f", 0, NULL },
and got some data different from the input voltage values
The Powercom support staff gave the following response to my question:
Dear Alex,
First of all , thank you for purchasing PCM MRT-3000 ups.
Regarding of your question, see our reply in below
==> Please take your data with below rules :
• DEX : 5378
• HEX : 1502 (Low : 15 / High : 02)
• Battery one cell voltage : [High + (Low/100)] : 2.21
• Battery voltage : 2.21 * 6 * 6 = 79.56 Vol (1 package with 6 cells /
MRT has 6 packages)
Best regards
Sandy Chang, Powercom Taiwan HQ
-----Original Message-----
From: Alex Rydzewski [mailto:[email protected]]
Sent: Thursday, January 12, 2023 5:47 PM
To:[email protected]
Subject: MRT-3000 USB battery.voltage
Hello!
I have the MRT-3000 UPS and try to get real battery voltage through USB.
USB protocol reference has specify for battery.voltage:
report id | Usage | Usage Name | Data Access | Length
26 0X8430 Battery Voltage R/O 3 Byte
But I get for this position the next data:
0.544555 [D4] Entering libusb_get_report
0.549533 [D3] Report[get]: (3 bytes) => 1a 02 15
0.549550 [D5] PhyMax = 0, PhyMin = 0, LogMax = 9216, LogMin = 2304
0.549561 [D5] Unit = 00000000, UnitExp = 0
0.549569 [D5] Exponent = 0
0.549576 [D5] hid_lookup_path: 00840004 -> UPS
0.549583 [D5] hid_lookup_path: 00840012 -> Battery
0.549591 [D5] hid_lookup_path: 00840030 -> Voltage
0.549603 [D1] Path: UPS.Battery.Voltage, Type: Feature,
ReportID: 0x1a, Offset: 0, Size: 16, Value: 5378
Suggest me, please, how I can interpret the battery.voltage value "5378? How I
can get real battery.voltage data?
Perhaps it is possible implement this algorithm to "nut" project for a
UPS like this?
On 10.01.23 19:14, Jim Klimov wrote:
I suppose that should have read "correct battery.voltage" ;)
Not sure really - this is the standard endpoint for that info, so
firmware is broken for USB HID power device support.
If you start the driver with higher debug verbosity, it prints the
reports from USB. If you can decipher those (online tools exist but I
don't have a link handy), maybe some other field (possibly with an
untranslated hex name) conveys data that looks like what you need.
Jim
On Tue, Jan 10, 2023, 18:09 Alex Rydzewski <[email protected]> wrote:
Thank You for your attention, Jim!
I compiled and ran the 2.8.0 version with this part uncomment
* { "battery.voltage", 0, 0, "UPS.PowerSummary.Voltage", NULL,
"%.2f", 0, NULL },
* { "battery.voltage", 0, 0, "UPS.Battery.Voltage", NULL,
"%.2f", 0, NULL },
* { "battery.voltage.nominal", 0, 0,
"UPS.PowerSummary.ConfigVoltage", NULL, "%.0f", HU_FLAG_STATIC,
NULL },
* { "battery.voltage.nominal", 0, 0,
"UPS.Battery.ConfigVoltage", NULL, "%.0f", HU_FLAG_STATIC, NULL },
from powercom-hid.c, and it is so, it is duplicates for
output.voltage.
Is there anything I can do to find the correct output.voltage?
On 10.01.23 14:12, Jim Klimov wrote:
Hello,
One thing that pops out in your report is that NUT 2.7.2 is
used, which is pretty old now. If you have a chance to install
2.8.0 or newer (custom build of current git master) to confirm if
the problem is still there, it could be helpful.
Other than that, current source says at
https://github.com/networkupstools/nut/blob/1deab1638322e9e64a0cf3200dadc93dbe3a3f41/drivers/powercom-hid.c#L362-L368
that "battery.voltage" is served in USB reports, but is not
useful (same as output voltage). Nearby, "battery.runtime" and
"battery.mfr.date" do come from USB reports, but per
https://github.com/networkupstools/nut/issues/1644 the latter was
previously wrongly reported as "battery.date" (for replacement).
Note that generally fixes are based on user reports about devices
which misbehaved; if a vendor has multiple devices with different
behaviors (including bug fixes in newer firmwares) it can get
messy and need some more elaborate fixes :-\
Something in your question does ring a bell - please revise
https://github.com/networkupstools/nut/issues?q=label%3APowercom
<https://github.com/networkupstools/nut/issues?q=+label%3APowercom>
and/or https://github.com/networkupstools/nut/issues?q=powercom
to see if that was discussed earlier in more detail.
Hope this helps,
Jim Klimov
On Tue, Jan 10, 2023 at 11:42 AM Alex Rydzewski
<[email protected]> wrote:
Hello!
I have not been able to get the battery.voltage data from the
Powercom
Macan MRT-3000, although there is data in the log that does
not match
the value I see on the device's display. Please tell me how I
can
control this. And please tell me, if possible, how to get the
absolute
value of the load on this device.
Debug log is attached
~ # upsc 004-0D9F-000
Init SSL without certificate database
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 30
battery.date: 2014/01/15 I'm not sure that it is
right
battery.runtime: 800 Is this data from the
device or
from the driver?
battery.type: PbAc
battery.voltage.high: 81.60
battery.voltage.low: 63.60
battery.voltage.nominal: 75.60
device.mfr: POWERCOM Co.,LTD
device.model: HID UPS Battery
device.serial: 004-0D9F-000
device.type: ups
driver.name <http://driver.name>: usbhid-ups
driver.version: 2.7.2
driver.version.data: PowerCOM HID 0.4
driver.version.internal: 0.38
...
--
З найкращими побажаннями, Олександр Ридзевський |With best
regards, Mr. Alexander Rydzewski, |С наилучшими
пожеланиями, Александр Рыдзевский
Системний та мережевий інженер, Elyland ltd. |System and
Network Engineer at Elyland ltd. |Системный и сетевой
инженер, Elyland ltd.
--
З найкращими побажаннями, Олександр Ридзевський |With best regards, Mr. Alexander Rydzewski, |С наилучшими пожеланиями, Александр Рыдзевский
Системний та мережевий інженер, Elyland ltd. |System and Network
Engineer at Elyland ltd. |Системный и сетевой инженер, Elyland ltd.
--
З найкращими побажаннями, Олександр Ридзевський |With best regards, Mr.
Alexander Rydzewski, |С наилучшими пожеланиями, Александр Рыдзевский
Системний та мережевий інженер, Elyland ltd. |System and Network Engineer at
Elyland ltd. |Системный и сетевой инженер, Elyland ltd.
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser