Hi again, On 5/22/23 18:31, Willcox David via Nut-upsuser wrote:
Hmm. Is there maybe something there already that will do this? Maybe
kind of back-handed.
In drivers/dstate.c, I see:
1. In status_init(), if “driver.flag.ignorelb” is set in the driver
state, the “ignorelb” flag is set.
2. In status_set(), if ignorelb is set, and the status being set
(presumably from the UPS) is LB, it’s ignored. In other words, LB
reported by the UPS is ignored.
3. In status_commit(), if ignorelb is set, there’s code to compare
battery.charge against battery.charge.low and battery.runtime
against battery.runtime.low. If either is below the “low” setting, “
LB” is added to the status. (So “OL” would become “OL LB” and “OB"
would become “OB LB”. And note that the two “.low” settings can be
overridden in the config.
this looks exactly like the right place and functionality I would like to have, BUT
Am I missing something?
yes, probably the same trap I fell into, status_commit does not seem to be not called (at least from the dummy driver I use for testing) upon changing charge/runtime. I can only force a call by flipping OL/OB.
I sprinkled a bit of debug information [1] into status_commit and journald looks like
initial upsrw call to set dummy OL:May 24 08:23:24 gateway dummy-ups[284580]: [D2] entering setvar(ups.status, OL)
May 24 08:23:24 gateway dummy-ups[284580]: [D2] status_commit: Entering (1)May 24 08:23:24 gateway dummy-ups[284580]: [D2] status_commit: charge val/low 33/30'] May 24 08:23:24 gateway dummy-ups[284580]: [D2] status_commit: runtime val/low 200/180']
May 24 08:23:27 gateway dummy-ups[284580]: [D1] upsdrv_updateinfo... setting it OBMay 24 08:23:38 gateway dummy-ups[284580]: [D2] entering setvar(ups.status, OB)
May 24 08:23:38 gateway dummy-ups[284580]: [D2] status_commit: Entering (1)May 24 08:23:38 gateway dummy-ups[284580]: [D2] status_commit: charge val/low 33/30'] May 24 08:23:38 gateway dummy-ups[284580]: [D2] status_commit: runtime val/low 200/180']
May 24 08:23:42 gateway dummy-ups[284580]: [D1] upsdrv_updateinfo... changing run-timeMay 24 08:23:48 gateway dummy-ups[284580]: [D2] upsdrv_updateinfo: NO-OP: input file was already read once to the end May 24 08:23:49 gateway dummy-ups[284580]: [D2] entering setvar(battery.runtime, 100)
May 24 08:23:52 gateway dummy-ups[284580]: [D1] upsdrv_updateinfo... later changing charge May 24 08:37:28 gateway dummy-ups[284580]: [D2] send_to_one: sending PONG May 24 08:37:32 gateway dummy-ups[284580]: [D1] upsdrv_updateinfo...May 24 08:37:33 gateway dummy-ups[284580]: [D2] upsdrv_updateinfo: NO-OP: input file was already read once to the end May 24 08:37:33 gateway dummy-ups[284580]: [D2] entering setvar(battery.charge, 5)
May 24 08:37:37 gateway dummy-ups[284580]: [D1] upsdrv_updateinfo...May 24 08:37:38 gateway dummy-ups[284580]: [D2] upsdrv_updateinfo: NO-OP: input file was already read once to the end
and still no LB. But going back "OL", suddenly LB is added:May 24 09:21:48 gateway dummy-ups[284580]: [D2] entering setvar(ups.status, OL)
May 24 09:21:48 gateway dummy-ups[284580]: [D2] status_commit: Entering (1)May 24 09:21:48 gateway dummy-ups[284580]: [D2] status_commit: charge val/low 5/30'] May 24 09:21:48 gateway dummy-ups[284580]: [D2] status_commit: appending LB flag [charge '5' below '30']
Thus it seems somewhere in the state logic there ought to be a possibility to trigger this automatically (on changing charge/runtime while OB) but there is not.
Hopefully, someone with more knowledge than I have can chime in here :) Cheers Carsten[1] Please don't judge me by this, I still use printf and friends a lot for debugging (sorry for breaking lines, it's just for illustration):
@@ -1113,12 +1116,13 @@
/* write the status_buf into the externally visible dstate storage */
void status_commit(void)
{
+ upsdebugx(2, "%s: Entering (%d)", __func__, ignorelb);
while (ignorelb) {
const char *val, *low;
val = dstate_getinfo("battery.charge");
low = dstate_getinfo("battery.charge.low");
-
+ upsdebugx(2, "%s: charge val/low %s/%s']", __func__,
val, low);
if (val && low && (strtol(val, NULL, 10) < strtol(low,
NULL, 10))) {
snprintfcat(status_buf, sizeof(status_buf), " LB");
upsdebugx(2, "%s: appending LB flag [charge
'%s' below '%s']", __func__, val, low);
@@ -1127,6 +1131,7 @@
val = dstate_getinfo("battery.runtime");
low = dstate_getinfo("battery.runtime.low");
+ upsdebugx(2, "%s: runtime val/low %s/%s']", __func__,
val, low);
if (val && low && (strtol(val, NULL, 10) < strtol(low, NULL, 10))) {
snprintfcat(status_buf, sizeof(status_buf), " LB");
--
Dr. Carsten Aulbert, Max Planck Institute for Gravitational Physics,
Callinstraße 38, 30167 Hannover, Germany, Phone +49 511 762 17185
smime.p7s
Description: S/MIME Cryptographic Signature
_______________________________________________ Nut-upsuser mailing list [email protected] https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser