I would like to solicit some feedback re: the battery.runtime.lowconfiguration settings through NUT. I was able to set the value using the 'upsrw' command but when I did a 'upsc' the configuration seems incorrect. Please see below for details. Thank you

OS name and version:
    Description:    Debian GNU/Linux 12 (bookworm)
    Release:        12
    Codename:       bookworm

exact NUT version:
    Version: 2.8.0-7

NUT installation method:
    apt install nut

exact device name and related information:
https://www.cyberpowersystems.com/product/ups/battery-backup/cst150uc/
    device.model: CST150UC
    driver.version: 2.8.0
    driver.version.data: CyberPower HID 0.6
    driver.version.internal: 0.47
    driver.version.usb: libusb-1.0.26 (API: 0x1000109)
    ups.vendorid: 0764

supported UPS variables (default values PRIOR to configuration change attempt)
    upsrw CST150UC
            [battery.charge.low]
            Remaining battery level when UPS switches to LB (percent)
            Type: STRING
            Maximum length: 10
            Value: 10

            [battery.runtime.low]
            Remaining battery runtime when UPS switches to LB (seconds)
            Type: STRING
            Maximum length: 10
            Value: 300

            [ups.delay.shutdown]
            Interval to wait after shutdown with delay command (seconds)
            Type: STRING
            Maximum length: 10
            Value: 20

            [ups.delay.start]
            Interval to wait before (re)starting the load (seconds)
            Type: STRING
            Maximum length: 10
            Value: 30

set UPS variables (system will shutdown when 60 minutes of runtime is left)
    upsrw -s battery.runtime.low=3600 -w CST150UC@localhost
    SUCCESS

upsc CST150UC@localhost
    battery.charge: 100
    battery.charge.low: 10
    battery.charge.warning: 20
    battery.mfr.date: CPS
    battery.runtime: 5125
    battery.runtime.low: 16
    battery.type: PbAcid
    battery.voltage: 25.8
    battery.voltage.nominal: 24
    device.mfr: CPS
    device.model: CST150UC
    device.serial:
    device.type: ups
    driver.name: usbhid-ups
    driver.parameter.offdelay: 60
    driver.parameter.pollfreq: 30
    driver.parameter.pollinterval: 2
    driver.parameter.port: auto
    driver.parameter.synchronous: auto
    driver.version: 2.8.0
    driver.version.data: CyberPower HID 0.6
    driver.version.internal: 0.47
    driver.version.usb: libusb-1.0.26 (API: 0x1000109)
    input.voltage: 122.0
    input.voltage.nominal: 120
    output.voltage: 122.0
    ups.beeper.status: disabled
    ups.delay.shutdown: 60
    ups.delay.start: -1
    ups.load: 10
    ups.mfr: CPS
    ups.model: CST150UC
    ups.productid: 0601
    ups.realpower.nominal: 900
    ups.serial:
    ups.status: OL
    ups.test.result: No test initiated
    ups.timer.shutdown: -60
    ups.timer.start: -60
    ups.vendorid: 0764

The value changed to battery.runtime.low: 16, instead of 3600. I don't understand why, because executing the command resulted in SUCCESS.

In comparison executing (never powers on the load, even when main power returns)
upsrw -s ups.delay.start=-1 -w CST150UC@localhost
resulted in the correct value being set.

I hope someone will be able to provide some guidance. : )

Thank you