Hi

an other test in real life (UPS sold in 2022)

ONBATT at 7h54
ONLINE at 7h58

root@minet:~# grep " ups" /var/log/syslog


Apr  4 07:53:05 minet upsmon[8374]: Onduleur UPS1@localhost en mode Secours sur batterie
Apr  4 07:53:05 minet upssched[24512]: Executing command: ONBATT
Apr  4 07:53:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 07:53:05 minet upssched[24538]: Timer daemon started
Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-5 (300 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-10 (600 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-15 (900 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-20 (1200 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-25 (1500 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-30 (1800 seconds) Apr  4 07:53:05 minet upssched[24538]: New timer: BATT-STATUS-60 (3600 seconds) Apr  4 07:54:30 minet upsmon[8374]: Onduleur UPS1@localhost batterie trop basse Apr  4 07:54:30 minet upsmon[8374]: FSD set on UPS UPS1@localhost failed: ERR ACCESS-DENIED
Apr  4 07:54:30 minet upsmon[8374]: Executing automatic power-fail shutdown
Apr  4 07:54:30 minet upssched[24585]: Executing command: LOWBATT-INFO
Apr  4 07:54:30 minet upssched-cmd-received-NOTIFYTYPE: LOWBATT
Apr  4 07:54:35 minet upsmon.conf: Je ne veux pas arreter ce serveur
Apr  4 07:58:05 minet upssched[24538]: Event: BATT-STATUS-5
Apr  4 07:58:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:03:05 minet upssched[24538]: Event: BATT-STATUS-10
Apr  4 08:03:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:08:05 minet upssched[24538]: Event: BATT-STATUS-15
Apr  4 08:08:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:13:05 minet upssched[24538]: Event: BATT-STATUS-20
Apr  4 08:13:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:18:05 minet upssched[24538]: Event: BATT-STATUS-25
Apr  4 08:18:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:23:05 minet upssched[24538]: Event: BATT-STATUS-30
Apr  4 08:23:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:53:05 minet upssched[24538]: Event: BATT-STATUS-60
Apr  4 08:53:05 minet upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  4 08:53:20 minet upssched[24538]: Timer queue empty, exiting


root@minet:~# upsc -V       => Network UPS Tools upscmd 2.7.2

root@minet:~# upsc UPS1
Init SSL without certificate database
battery.charge: 90
battery.charge.low: 20
battery.runtime: 895
battery.type: PbAc
device.mfr: EATON
device.model: Ellipse PRO 650
device.serial: G354M26707
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.7.2
driver.version.data: MGE HID 1.33
driver.version.internal: 0.38
input.frequency: 50.0
input.transfer.high: 285
input.transfer.low: 165
input.voltage: 237.0
input.voltage.extended: no
outlet.1.desc: PowerShare Outlet 1
outlet.1.id: 2
outlet.1.status: on
outlet.1.switchable: no
outlet.2.desc: PowerShare Outlet 2
outlet.2.id: 3
outlet.2.status: on
outlet.2.switchable: no
outlet.desc: Main Outlet
outlet.id: 1
outlet.switchable: no
output.frequency: 50.0
output.frequency.nominal: 50
output.voltage: 238.0
output.voltage.nominal: 230
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 01.16.0020
ups.load: 24
ups.mfr: EATON
ups.model: Ellipse PRO 650
ups.power: 147
ups.power.nominal: 650
ups.productid: ffff
ups.realpower: 99
ups.serial: G354M26707
ups.status: OL CHRG
ups.timer.shutdown: 0
ups.timer.start: 0
ups.vendorid: 0463

upssched.conf
# info2client
AT ONLINE * EXECUTE ONLINE
# info2admin only
AT ONLINE * CANCEL-TIMER BATT-STATUS-5
AT ONLINE * CANCEL-TIMER BATT-STATUS-10
AT ONLINE * CANCEL-TIMER BATT-STATUS-15
AT ONLINE * CANCEL-TIMER BATT-STATUS-20
AT ONLINE * CANCEL-TIMER BATT-STATUS-25
AT ONLINE * CANCEL-TIMER BATT-STATUS-30
AT ONLINE * CANCEL-TIMER BATT-STATUS-60
AT ONLINE * START-TIMER LINE-STATUS-5 300
AT ONLINE * START-TIMER LINE-STATUS-10 600
AT ONLINE * START-TIMER LINE-STATUS-15 900
AT ONLINE * START-TIMER LINE-STATUS-20 1200
AT ONLINE * START-TIMER LINE-STATUS-25 1500
AT ONLINE * START-TIMER LINE-STATUS-30 1800
AT ONLINE * START-TIMER LINE-STATUS-60 3600
#
# info2client
AT ONBATT * EXECUTE ONBATT
# info2admin only
AT ONBATT * CANCEL-TIMER LINE-STATUS-5
AT ONBATT * CANCEL-TIMER LINE-STATUS-10
AT ONBATT * CANCEL-TIMER LINE-STATUS-15
AT ONBATT * CANCEL-TIMER LINE-STATUS-20
AT ONBATT * CANCEL-TIMER LINE-STATUS-25
AT ONBATT * CANCEL-TIMER LINE-STATUS-30
AT ONBATT * CANCEL-TIMER LINE-STATUS-60
AT ONBATT * START-TIMER BATT-STATUS-5 300
AT ONBATT * START-TIMER BATT-STATUS-10 600
AT ONBATT * START-TIMER BATT-STATUS-15 900
AT ONBATT * START-TIMER BATT-STATUS-20 1200
AT ONBATT * START-TIMER BATT-STATUS-25 1500
AT ONBATT * START-TIMER BATT-STATUS-30 1800
AT ONBATT * START-TIMER BATT-STATUS-60 3600

# info2client
AT REPLBATT * ONBATT * EXECUTE REPLBATT
AT NOCOMM * EXECUTE NOCOMM
AT FSD * EXECUTE FSD
AT SHUTDOWN * EXECUTE SHUTDOWN

# info2admin only
AT LOWBATT * EXECUTE LOWBATT-INFO
AT COMMOK * EXECUTE COMMOK-INFO
AT COMMBAD * EXECUTE COMMBAD-INFO

and part of upssched-cmd

=============================
echo -e "$NOTIFYTYPE" | logger -t upssched-cmd-received-NOTIFYTYPE

case "$1-$Battery_status" in

       ONLINE-*|ONBATT-*|REPLBATT-*|SHUTDOWN)
               Message_for_client
               ;;
=============================

Le 02/04/2025 à 09:02, Jim Klimov a écrit :
Well, either I misunderstood what you wrote or (my initially written post follows, probably misguided at start) I think your log contradicts your statements:

> when my bash script receive events from TIMER like  LINE-STATUS-xx
> NOTIFYTYPE is always ONBATT
> in all other cases, NOTIFYTYPE is TRUE and same as it was called by upsmon

in the log I see :

* Initial ONBATT:

Apr  1 17:07:39  upsmon[652]: Onduleur UPS1@localhost en mode Secours sur batterie
Apr  1 17:07:39  upssched[9126]: Executing command: ONBATT
Apr  1 17:07:39  upssched-cmd-received-NOTIFYTYPE: ONBATT
Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-5
...
Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-5 (300 seconds)
...

* Handler for BATT-STATUS-5 fired and issued ONBATT after 5 min:

Apr  1 17:12:39  upssched[8783]: Event: BATT-STATUS-5
Apr  1 17:12:39  upssched-cmd-received-NOTIFYTYPE: ONBATT

* Loss of comms (NUT driver down?):

Apr  1 17:13:06  upsd[7074]: Data for UPS [UPS1] is stale - check driver

Apr  1 17:13:09  upsmon[652]: Poll UPS [UPS1@localhost] failed - Data stale Apr  1 17:13:09  upsmon[652]: Perte de communication avec Onduleur UPS1@localhost
Apr  1 17:13:09  upssched[9277]: Executing command: COMMBAD-INFO
Apr  1 17:13:09  upssched-cmd-received-NOTIFYTYPE: COMMBAD

* Restarted comms and ONLINE (note there is a lag between upsd seeing the driver/data is back, and upsmon polling seeing and propagating that):

Apr  1 17:13:09  upsd[7074]: UPS [UPS1] data is no longer stale

Apr  1 17:13:14  upsmon[652]: Retablissement des communications avec UPS1@localhost Apr  1 17:13:14  upsmon[652]: Onduleur UPS1@localhost en mode Secteur : recharge batterie en cours
Apr  1 17:13:14  upssched[9307]: Executing command: ONLINE
Apr  1 17:13:14  upssched[9306]: Executing command: COMMOK-INFO
Apr  1 17:13:14  upssched-cmd-received-NOTIFYTYPE: COMMOK
Apr  1 17:13:14  upssched-cmd-received-NOTIFYTYPE: ONLINE
Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-10
...
Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-5 (300 seconds)
...

So in fact I see many different NOTIFYTYPE values and none is "TRUE".

* Oh, NOW I think I get what you meant:

Apr  1 17:18:14  upssched[8783]: Event: LINE-STATUS-5
Apr  1 17:18:14  upssched-cmd-received-NOTIFYTYPE: ONBATT


Just in case, which NUT version is involved?

Jim



On Tue, Apr 1, 2025 at 5:42 PM RemiG <[email protected]> wrote:

    HI

    i'am using schema upsmon call : NOTIFYCMD /sbin/upssched

    and this part of upsschede strategy (working fine)

    device.model: Ellipse ECO 650

    root@---:~# cat /etc/nut/upssched.conf
    # Network UPS Tools - upssched.conf sample file

    CMDSCRIPT /opt/nut/bin/upssched-cmd

    PIPEFN /var/run/nut/upssched.pipe
    LOCKFN /var/run/nut/upssched.lock

    #
    ============================================================================
    # info2client
    AT ONLINE * EXECUTE ONLINE
    # info2admin only
    AT ONLINE * CANCEL-TIMER BATT-STATUS-5
    AT ONLINE * CANCEL-TIMER BATT-STATUS-10
    AT ONLINE * CANCEL-TIMER BATT-STATUS-15
    AT ONLINE * CANCEL-TIMER BATT-STATUS-20
    AT ONLINE * CANCEL-TIMER BATT-STATUS-25
    AT ONLINE * CANCEL-TIMER BATT-STATUS-30
    AT ONLINE * CANCEL-TIMER BATT-STATUS-60
    AT ONLINE * START-TIMER LINE-STATUS-5 300
    AT ONLINE * START-TIMER LINE-STATUS-10 600
    AT ONLINE * START-TIMER LINE-STATUS-15 900
    AT ONLINE * START-TIMER LINE-STATUS-20 1200
    AT ONLINE * START-TIMER LINE-STATUS-25 1500
    AT ONLINE * START-TIMER LINE-STATUS-30 1800
    AT ONLINE * START-TIMER LINE-STATUS-60 3600
    #
    # info2client
    AT ONBATT * EXECUTE ONBATT
    # info2admin only
    AT ONBATT * CANCEL-TIMER LINE-STATUS-5
    AT ONBATT * CANCEL-TIMER LINE-STATUS-10
    AT ONBATT * CANCEL-TIMER LINE-STATUS-15
    AT ONBATT * CANCEL-TIMER LINE-STATUS-20
    AT ONBATT * CANCEL-TIMER LINE-STATUS-25
    AT ONBATT * CANCEL-TIMER LINE-STATUS-30
    AT ONBATT * CANCEL-TIMER LINE-STATUS-60
    AT ONBATT * START-TIMER BATT-STATUS-5 300
    AT ONBATT * START-TIMER BATT-STATUS-10 600
    AT ONBATT * START-TIMER BATT-STATUS-15 900
    AT ONBATT * START-TIMER BATT-STATUS-20 1200
    AT ONBATT * START-TIMER BATT-STATUS-25 1500
    AT ONBATT * START-TIMER BATT-STATUS-30 1800
    AT ONBATT * START-TIMER BATT-STATUS-60 3600

    when my bash script receive events from TIMER like  LINE-STATUS-xx
    NOTIFYTYPE is always ONBATT

    in all other cases, NOTYFYTYPE is TRUE and same as it was called
    by upsmon

    what is  wrong ?

    my parsed log for this situation :
    ===============
    Apr  1 17:07:39  upsmon[652]: Onduleur UPS1@localhost en mode
    Secours sur batterie
    Apr  1 17:07:39  upssched[9126]: Executing command: ONBATT
    Apr  1 17:07:39  upssched-cmd-received-NOTIFYTYPE: ONBATT
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-5
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-10
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-15
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-20
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-25
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-30
    Apr  1 17:07:39  upssched[8783]: Cancelling timer: LINE-STATUS-60
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-5 (300
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-10 (600
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-15 (900
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-20 (1200
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-25 (1500
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-30 (1800
    seconds)
    Apr  1 17:07:39  upssched[8783]: New timer: BATT-STATUS-60 (3600
    seconds)
    Apr  1 17:12:39  upssched[8783]: Event: BATT-STATUS-5
    Apr  1 17:12:39  upssched-cmd-received-NOTIFYTYPE: ONBATT
    Apr  1 17:13:06  upsd[7074]: Data for UPS [UPS1] is stale - check
    driver
    Apr  1 17:13:09  upsmon[652]: Poll UPS [UPS1@localhost] failed -
    Data stale
    Apr  1 17:13:09  upsmon[652]: Perte de communication avec Onduleur
    UPS1@localhost
    Apr  1 17:13:09  upssched[9277]: Executing command: COMMBAD-INFO
    Apr  1 17:13:09  upssched-cmd-received-NOTIFYTYPE: COMMBAD
    Apr  1 17:13:09  upsd[7074]: UPS [UPS1] data is no longer stale
    Apr  1 17:13:14  upsmon[652]: Retablissement des communications
    avec UPS1@localhost
    Apr  1 17:13:14  upsmon[652]: Onduleur UPS1@localhost en mode
    Secteur : recharge batterie en cours
    Apr  1 17:13:14  upssched[9307]: Executing command: ONLINE
    Apr  1 17:13:14  upssched[9306]: Executing command: COMMOK-INFO
    Apr  1 17:13:14  upssched-cmd-received-NOTIFYTYPE: COMMOK
    Apr  1 17:13:14  upssched-cmd-received-NOTIFYTYPE: ONLINE
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-10
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-15
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-20
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-25
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-30
    Apr  1 17:13:14  upssched[8783]: Cancelling timer: BATT-STATUS-60
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-5 (300
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-10 (600
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-15 (900
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-20 (1200
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-25 (1500
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-30 (1800
    seconds)
    Apr  1 17:13:14  upssched[8783]: New timer: LINE-STATUS-60 (3600
    seconds)
    Apr  1 17:18:14  upssched[8783]: Event: LINE-STATUS-5
    Apr  1 17:18:14  upssched-cmd-received-NOTIFYTYPE: ONBATT

-- # admin linux only ;-)

    _______________________________________________
    Nut-upsuser mailing list
    [email protected]
    https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

--
# admin linux only ;-)
_______________________________________________
Nut-upsuser mailing list
[email protected]
https://alioth-lists.debian.net/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to