I lost power for about 40 seconds. From what I can see NUT quickly shut down the system and boot it back up when power was restored. That also worked. Everything worked as designed, except I would expect such a brief shutdown to be survivable.

The only question mark in my mind is that the battery should've been enough to last those measly 40 seconds. Output of upsc is below. This is about an hour after the power was restored, and I see that battery.charge is only 29, and it is slowly increasing.

So, I think is that my batteries are due for a replacement. I would've wanted to see what was logged during the outage, but I can't find anything in journalctl for nut-monitor or nut-server. This is Ubuntu 24. Should there be something logged, somewhere?

battery.charge: 29
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2939
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 27.3
battery.voltage.nominal: 24
device.mfr: CPS
device.model: CP1500AVRLCDa
device.serial: BHQLW7002402
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 10
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.1
driver.version.data: CyberPower HID 0.8
driver.version.internal: 0.52
driver.version.usb: libusb-1.0.27 (API: 0x100010a)
input.voltage: 120.0
input.voltage.nominal: 120
output.voltage: 120.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 6
ups.mfr: CPS
ups.model: CP1500AVRLCDa
ups.productid: 0501
ups.realpower.nominal: 900
ups.serial: BHQLW7002402
ups.status: OL CHRG
ups.test.result: No test initiated
ups.timer.shutdown: -60
ups.timer.start: -60
ups.vendorid: 0764

Attachment: pgpTxOiB65AZZ.pgp