Hello.

A customer of mine has the above model.
It reports being manufactured in late 2009 and it's connected via USB cable. Also it has no front panel (except some basic status LEDs) where I could go about configuring it.

So what driver should I use?

IIUC apcsmart is only for serial line (and ModBus is out of the question), so I'm using usbhid-ups.

This is more or less able to comunicate but:
_ no matter what, the battery charge is alway 100% (even when obviously this can't be and the front panel shows otherwise);
_ input voltage works seems to be the only parameter that changes;
_ still the UPS status is always "OL" and NUT won't log anything if I disconnect the power cable (so I guess it won't turn off the machine when needed).

Is there anything I can do?
I'm using NUT 2.8.2.

Below I'm pasting a full upsc output taken after 30' of no input power.

 bye & Thanks
        av.

-----------------------
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 50
battery.mfr.date: 2009/09/01
battery.runtime: 8400
battery.runtime.low: 120
battery.temperature: 11.7
battery.type: PbAc
battery.voltage: 50.2
battery.voltage.nominal: 48.0
device.mfr: American Power Conversion
device.model: Smart-UPS 2200
device.serial: xxxxxxxxxxxx
device.type: ups
driver.debug: 0
driver.flag.allow_killpower: 0
driver.name: usbhid-ups
driver.parameter.pollfreq: 15
driver.parameter.pollinterval: 2
driver.parameter.pollonly: true
driver.parameter.port: auto
driver.parameter.synchronous: auto
driver.state: quiet
driver.version: 2.8.2
driver.version.data: APC HID 0.100
driver.version.internal: 0.53
driver.version.usb: libusb-1.0.0 (API: 0x1000102)
input.sensitivity: high
input.transfer.high: 253
input.transfer.low: 208
input.transfer.reason: input voltage out of range
input.voltage: 0.0
output.current: 0.52
output.frequency: 50.0
output.voltage: 229.6
output.voltage.nominal: 230.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.firmware: 654.18.I
ups.firmware.aux: 7.4
ups.load: 5.8
ups.mfr: American Power Conversion
ups.mfr.date: 2009/09/01
ups.model: Smart-UPS 2200
ups.productid: 0002
ups.serial: xxxxxxxxxxxx
ups.status: OL
ups.test.result: No test initiated
ups.timer.reboot: -1
ups.timer.shutdown: -1
ups.timer.start: -1
ups.vendorid: 051d