On 2/7/06, Damon Pullen <[EMAIL PROTECTED]> wrote: > Our problem is this. When the server runs the backup processes it becomes > loaded.
Is this a network backup, or local (to a tape drive, or something similar)? > During this time UPSC takes up to 30 seconds to return with an answer from > UPSD regarding the status of each UPS. Since we have two UPS's the combined > interrogation time can blow out to 75 seconds. > > Is there any way we can speed up this interrogation time or, at least, > determine where the performance issue lies (i.e. with UPSD or UPSC)? You could use tcpdump (or the Solaris equivalent; I seem to remember using another program for packet capture) along with strace or truss to pinpoint the problem. Together, these tools will let you see when the packets are sent from upsc to upsd. You will probably want to use a capture filter with tcpdump (monitor TCP port 3493 and UDP port 161), and use the '-t' option of strace to get the time of each system call. One possibility is that your network transmit queues are too deep, and the packets are sitting in a buffer for a while as the backup traffic is sent. Or, if it is local disk I/O, you may have to lower the priority of the backup process (since most OSes, by default, do not schedule disk I/O with priorities that account for the system-specific delay in waiting for disk reads and writes). -- - Charles Lepple _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser