On Wed, Mar 01, 2006 at 08:26:02AM -0600, Brady Chang wrote:
> SNMPv2-SMI::mib-2.33.1.4.1.0 = INTEGER: 3
This one is the crucial one ...
If we translate it using the MIB it is
$ snmptranslate -Td -m+UPS-MIB SNMPv2-SMI::mib-2.33.1.4.1.0
UPS-MIB::upsOutputSource.0
upsOutputSource OBJECT-TYPE
-- FROM UPS-MIB
SYNTAX INTEGER {other(1), none(2), normal(3), bypass(4),
battery(5), booster(6), reducer(7)}
MAX-ACCESS read-only
STATUS current
DESCRIPTION "The present source of output power. The enumeration
none(2) indicates that there is no source of output
power (and therefore no output power), for example,
the system has opened the output breaker."
::= { iso(1) org(3) dod(6) internet(1) mgmt(2) mib-2(1) upsMIB(33)
upsObjects(1) upsOutput(4) upsOutputSource(1) 0 }
or
UPS-MIB::upsOutputSource.0 = INTEGER: normal(3)
So the UPS does not say that it is on battery, which means that there is
no way for NUT to say it
/Niels
--