> On 6/4/06, Arjen de Korte <[EMAIL PROTECTED]> wrote:
> >
> > At least here in the Netherlands, quite a few (cheap) UPSes are sold
> > nowadays that sport high VA ratings, but really lack the battery
> > capacity needed to power even a modest load for more than a few minutes.
> > Clay should avoid these at all cost.
> 
> MGE rather usefully do a runtime calculator where you put in the power
> draw and required runtime and it suggests options from their range.
> 
> Worked like a charm when I used it, however there's a gotcha.  An ups
> with a 28 minute runtime may signal LB at 19 minutes, resulting in a
> shutdown sometime sooner than you expect :)
> 
> If you need a 20 minute actual runtime you'll probably need a 30
> minute theoretical runtime.
> 
        Warning on that. Even though the Ellipse Pulsar 1200 I bought
said it would do 90 minutes, its pretty much "hard coded" to just do a 
countdown and shutdown within 20-30. Even if you deplete the battery 
completely, when you start it up it thinks its at 86% charged. You can't
go by what the MGE calc says and what you'll get for all models.

                        Tuc