And something else, that previously eluded from my thoughts:my "notifyme"
script,i.e the script that is executed at an ups.status="OB" event, is:
echo `date` >> /root/upsLog
echo " No power, shutting down the system!" >> /root/upsLog
sleep 30
control=`/usr/local/ups/bin/upsc [EMAIL PROTECTED] ups.status`
if [ $control != OL ]
then
/usr/local/ups/sbin/upsmon -c fsd
fi
I changed "telinit 0 " to "upsmon -c fsd", following the advice of Mr Selinger
from the mailing list. Besides, I added "shutdownArguments={{1,0},y}" to
ups.conf, as you advised me. With this configuration, if the system works
correctly, according to me things should go like that in case of a prolonged
power failure:
power failure->ups.status=="OB"->"upsmon -c fsd"->system shutdown(normal
shutdown, involving runnint the shutdown scripts in rc.0->UPS shutdown one
minute after the "upsmon -c fsd" command was issued. I deliberately set one
minute time lapse between the issuing of the forced shutdown and the UPS
shutdown, so that there is enough time for the system to run the shutdown
scripts before shutting down. However, when I tested it, the system went down,
but the UPS did not. So I think the UPS doesnot recognise the "upsmon -c fsd"
command correctly. Am I right, or I am mistaken?
Thank you very much for your attention. I am looking forward to your answer.
Regards,
Martin
-----------------------------------------------------------------