If the Windows comment is accurate (i.e. does not happen under windows) then
disregard this comment.  Otherwise...

We've seen a UPS with a new set of batteries, reporting full charge.  Then
when under load (upon power failure) the unit shuts off.  The root cause was
one of the 4 batteries in the unit was defective.  Although it showed full
voltage, it collapsed under load causing the UPS to turn off immediately.
Replacing the battery solved the problem.

MD 

-----Original Message-----
From: [EMAIL PROTECTED]
[mailto:[EMAIL PROTECTED] On Behalf Of Doug
Reynolds
Sent: Friday, September 15, 2006 5:27 PM
To: Peter Selinger
Cc: [email protected]
Subject: Re: [Nut-upsuser] Shutdown after 5 minutes?

Peter Selinger wrote:
> After what's been said here, and the data that Rob sent, it seems that
> the UPSs are faulty; I cannot think of any reason why they should yank
> the power after 5 minutes, without any warning sign, and with brand
> new batteries. Even stranger that it still does this when the power is
> interrupted only briefly. It does not appear to be a driver problem,
> as the situation still occurs even when no computer is attached at
> all.
>
> On the other hand, did someone say that it does *not* do this under
> Windows?  That seems bizarre. Perhaps there is some proactive (and
> doubtlessly top-secret) command by which the driver must tell the UPS
> not to shut down?
>
> I would advise to stay away from this brand of UPS.
thanks for the warning.. :)

I've been needing to snoop on the com port when the windows program is 
running.  It _doesn't_ appear to do it when it is being monitored with 
windows.