On 7/9/07, Arnaud QUETTE <[EMAIL PROTECTED]> wrote:
> > My UPS is a: Upsonic CXR1000   (made in Oz, probably rebranded
> monitoring)
> > Driver: Megatec
> >
> > Works perfectly!
[snip]
> I'll add your model to the supported ones once Carlos has validated
> everything is fine.

I can do that.

>From the output shown, I can see that the driver doesn't calculate the
battery charge percentage for your UPS. This seems to be related to
the fact that the nominal values (aka: UPS ratings) are also missing,
which makes this an unfixable issue on the driver's side.

You can, however, pass the battvolts parameter to the driver (in
ups.conf) and the calculation will be done based on those values. For
example "battvolts = 20:27" means "battery.voltage" is 27V when the
UPS is full, and 20V when the UPS is empty. You can also check the
manpage.

-- 
Carlos Rodrigues