Phil Scarr wrote: >>> I have a new CPS UPS connected via USB. Everything is working fine, >>> except the UPS is showing a value of 120% charged. >> This probably means that the HID path 'UPS.PowerSummary.RemainingCapacity' >> has a very different meaning for CyberPower devices, than it has for APC >> where it indicates the battery charge. It also means, that we might have >> to make a separate subdriver to deal with this (I was already afraid of >> that from looking at the very different HID paths it uses).
In retrospect, the value may be actually correct. This parameter tells you the actual amount of charge the battery can hold in relation to the design capacity. If this is indeed a new (battery) system, the first can be *higher* than the latter, depending on the rate of discharge that was used in measuring the actual capacity. [...] > Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, Value: 12.000000 > Path: UPS.PowerSummary.Voltage, Type: Feature, Value: 21.400000 This here is actually the only surprise I see. This looks way too high for a 12V battery and too low for a 24V battery (it could be a 3 x 6V battery system, but I have never seen such a configuration). Can you measure the battery voltage? I still believe it would be better to create a separate subdriver for CyberPower, if only for the reason that it is easier to maintain if each VendorID has it's own subdriver. Best regards, Arjen PS Please keep the mailinglist posted. _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser