On 10/27/07, Drew Vonada-Smith <[EMAIL PROTECTED]> wrote:
> OS is ClarkConnect 4.2, which is based on CentOS4/RHEL 4.

Which version of the kernel?

Do you know if anything like SELinux or grsecurity are enabled?

> upsdrvctl -u root start upsserver
>
>
>
> all looks OK on results:
>
> Network UPS Tools - UPS driver controller 2.2.0-
>
> Network UPS Tools: 0.28 USB communication driver 0.28 - core 0.30 (2.2.0-)
>
> Detected a UPS: American Power Conversion/Smart-UPS 1500 RM FW:617.3.D USB
> FW:8.1
>
> Using subdriver: APC/CyberPower HID 0.9

This confirms your suspicion that usbhid-ups is the correct driver.

> But when I run:
>
> upsd –u root
>
>
>
> I get:
>
> Network UPS Tools upsd 2.2.0-
>
> not listening on 192.168.0.20 port 3493

First, is there anything that might have already bound to that port?
(An old copy of NUT, for instance?)

I think you can find out by running "lsof -n | grep 3493" as root.

You can also get more verbose debugging output by specifying "-DDD" on
the upsd command line.

If that doesn't work - what does config.log say about IPv6 support?

-- 
- Charles Lepple