Hello Arjen. Arjen de Korte wrote: > Still, it would be a good idea to test with 'upsmon -c fsd' first. You > want to make sure that shutdown command is sent to the UPS when going > down. Preferably when the system is *not* powered by the UPS, to see that > the system is halted before the power is lost. There is no need to deplete > the battery for that. > > This will have to tested anyway, since you also want to verify that you're > not vulnerable to power races (see 'docs/shutdown.txt'). If the UPS is > briefly shut-off and restarted automatically, you're fine. The next > experiment should be the same command again, but now with the power to the > UPS removed. Now the UPS should remain off until your apply the mains > again. > > The last test is if everything works correctly if you create a power > outage when the system is powered by the UPS, but only if you've made sure > that the above steps are OK.
Thank you for the suggestions. I will perform my testing as you have described. Maybe this should be in the FAQ? I was not able to find info on testing as good as what you wrote above. Thanks, Tobias _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser