I'll be back one more time
perhaps I found the reason of these errors

Nov 13 11:09:22 mezenc upsmon[3865]: Poll UPS [EMAIL PROTECTED] failed -
Data stale

it happens when daemon upsd et upsmon are started after the boot 
obviously, there isn't any errors when upsd and upsmon are started at boot 

following later ...


-----Message d'origine-----
De : goudard sabine 
Envoyé : mardi 13 novembre 2007 11:24
À : '[EMAIL PROTECTED]'
Cc : '[email protected]'
Objet : trouble with ups mge evolution2200 and mandriva 2007 - nut 2.2 +
PSP


 Hello,
I'll be back with my MGE Evolution 2200 connected with RS232

I upgrade nut 2.0.1 in nut 2.2 + psp
as you ask me

PSP autodetect my UPS and autoconfigure NUT.

not really diffcult !

So I didn't change anything but I always have in my syslog these event
Nov 13 11:09:22 mezenc upsmon[3865]: Poll UPS [EMAIL PROTECTED] failed -
Data stale
Nov 13 11:09:27 mezenc upsmon[3865]: Poll UPS [EMAIL PROTECTED] failed -
Data stale

and my server shut down 

what can I do ?

Thanks for your help

-----Message d'origine-----
De: Arnaud Quette
A: goudard sabine
Cc: Arjen de Korte; [email protected]
Date: 25/10/2007 23:06
Objet: Re: [Nut-upsuser] trouble with ups mge evolution2200 and mandriva
2007 - nut 2.01

Bonjour Sabine,

I'll add some more comments to Arjen's answer.

2007/10/16, Arjen de Korte <[EMAIL PROTECTED]>:
>
> > hello,
> > at first I'm sorry my english isn't perfect but I tried to be clear
> >
> > I work with mandriva 2007 and with nut 2.0.1 installed with urpmi
> > my UPS is a MGE Evolution 2200 connected with RS232
>
> First of all, upgrade to nut-2.2.0. The version you have now is well
past
> its 'use by' date.

this is true.
You can find 2.2.0 packages, along with the MGE PSP here:
http://www.mgeups.com/download/soft/explore/eng/ptp/ptp_sol.htm
or
urpmi.addmedia mgeups http://opensource.mgeups.com/stable/mdvlinux/
with hdlist.cz

The PSP will autodetect your UPS and autoconfigure NUT.
So you might prefer it.

> > in my ups.conf
> > I try to use mge-utalk driver and also mge-shut
> > both seem to work
> > I don't really known which I add to use
> >
> > It's the first point.
>
> We now (nut-2.2.0) recommend to use 'newmge-shut' or 'mge-shut'
drivers if

I've just made a statement about this: use mge-shut for the moment!

> you use a serial connection and 'usbhid-ups' if you use a USB
connection.
> You should only use mge-utalk if this is all your UPS supports.
>
> > As I saw on web site, I add maxage 25 in upsd.conf and DEADTIME 25
in
> > upsmon.conf
> > to avoid
> > Data for UPS [EMAIL PROTECTED] is stale - check driver
> > poll UPS [EMAIL PROTECTED] failed - data stale
> > UPS [EMAIL PROTECTED] data is no longer stale
> > Communications with ups [EMAIL PROTECTED] established
> >
> > it doesn't change any thing ; when I had these event in syslog my
computer
> > stop even if I don't put this in upsmon.conf
> >
> > It's the second point.
>
> The advisory on the website is no longer applicable and should be
removed.
> This used to be needed in very old versions (well before nut-1.4.0).
What
> you're seeing is unrelated to this problem, therefor the fix doesn't
work.
> A workaround for this was introduced in nut-2.0.5 and the final
solution
> will be in nut-2.2.1.

exactly. Moreover, this website is under heavy rewrite / update (part
of the MGE UPS dismantling, and the MGE Office Protection Systems
creation).

you should try to set pollinterval=10 in ups.conf

the default value (2 seconds) was fine with dumb / non verbose
protocols, but tends to overload unnecessarily the bus on both the
host and device side. Moreover, this kind of smart units supports
notification (the UPS sends info by itself, so less need to read
periodically)

> > The third point
> > with my conf all the commands upsc, upsmon, upsrw etc etc ... are OK
> > the connection with driver is OK
> > but when the battery is ON DISCHARG, I've an event in syslog and
after a
> > moment my computer stop
>
> I'm not quite sure what kind of problem you have. Does the computer
> shutdown cleanly (which is what should happen if the battery is
getting
> low) or does the UPS suddenly turn off (which would be bad)? In any
case,
> prior to shutting down, the upsmon client should mention that the UPS
is
> critical (UPS status flags "OB+LB"). Can you confirm that this is
> reported?
>
> > If I put a script in NOTIFYCMD parameter, this script isn't executed
> >
> > what is wrong
> >
> > upsmon.conf
> > MONITOR [EMAIL PROTECTED] 1 ups azerty master
> > MINSUPPLIES 1
> > SHUTDOWNCMD "/sbin/shutdown -h now"
> > NOTIFYCMD /etc/ups/upsalert
> > POWERDOWNFLAG /etc/ups/killpower
> > NOTIFYMSG ONBATT "L'onduleur %s est sur batterie"
> > NOTIFYMSG ONLINE "L'onduleur %s est alimenté"
> > NOTIFYFLAG ONBATT SYSLOG+EXEC
> > NOTIFYFLAG ONLINE SYSLOG+EXEC
> >
> > thanks for your help
>
> Most likely cause is a permissions problem. Is the STATEPATH directory
> writable by the user running upsmon? Is the NOTIFYCMD executable by
this
> user? Also, please post the contents of this script.

I agree with Arjen's audit.
You should really give a try to the PSP, since it deals with all these
points.
Then get back to us if the problem still exists.

Arnaud
-- 
Free Software Developer - http://arnaud.quette.free.fr/
Debian Developer - http://people.debian.org/~aquette/
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Ubuntu Media Center (UMC) Project Leader -
https://launchpad.net/~umc-team

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to