Roger Price wrote:

> No surprise here, it's just more n00b fumbling.  The correct answer, which 
> is provided by the rpm but which I wrongly ignored, is:
> 
> # /etc/ups/upssched.conf
> CMDSCRIPT /usr/sbin/upssched-cmd
> PIPEFN /var/lib/ups/upssched/upssched.pipe
> LOCKFN /var/lib/ups/upssched/upssched.lock ...
> 
> I created directory /var/lib/ups/upssched since it hadn't happened 
> automatically.  Should it happen?  I see no mention in nut-2.2.2-pre2.spec 
> %install or %post.

I'm busy with fixing the .spec file, based on the input you're 
providing. It should be created automatically, although yours doesn't at 
the moment.

> I restarted nut with the command
>     rcupsd restart 
> disconnected the UPS from the wall and after 120 secs the command 
> 'shutdown -h +2' kicked in and a further 2 minutes later the machine 
> shutdown.
> 
> An immediate re-connection to the wall does not restart the machine.

Be patient, it will restart (but not immediately).

> I had to wait for the UPS itself to power off before a wall reconnection 
> would restart UPS and PC.

The UPS will reboot automatically. Please try again by running (with the 
mains plugged in)

        # upsmon -c fsd

It takes about half a minute before the UPS powers down (seen 'man 8 
usbhid-ups'). After that, the output should be off for about ten seconds 
and then power up again.

Best regards, Arjen

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to