Hi Jayson,

I forward your request to the right place.
Carlos (or some other) will have an answer, or at least some questions for you.

-- Arnaud

2008/6/27 Jayson Anderson <[EMAIL PROTECTED]>:
> Greetings Arnaud,
>
> I wrote you some time ago about whether NUT would support the Belkin
> F6H550-UPS device in the future.
>
> You had replied and mentioned to send you info if I had any success; I did
> dig in further with version 2.2.2 (i was using 2.2.1 when I wrote the
> initial email in mid-March 2008)
>
> I managed to get the device sort-of working, but i'm getting the
> "unsupported combination of battery voltage..." error when attempting to
> bring upsdrvctl online.
>
> I am sending you some output to see if it will be of any help to you. I am
> not certain of the configuration of the UPS battery quantity/voltage. If you
> wish, I can take it apart to try and glean some more info. The
> package/instructions do not contain and solid data on this matter.
>
> Here is some output; if you need anymore or have any suggestions to bring
> the batteries into spec with NUT, let me know.
>
> Thanks graciously for your time.
>
> Kind Regards,
> Jayson
>
> PS: check out the voltage reading on "present voltage".  strange!
>
> ------stuff-------
>
> [EMAIL PROTECTED] bin]# /usr/local/ups/bin/megatec_usb -DDD -a ups1
> Network UPS Tools 2.2.2 - Megatec protocol driver 1.5.14 [megatec_usb]
> Carlos Rodrigues (c) 2003-2008
>
> Serial-over-USB transport layer for Megatec protocol driver [megatec_usb]
> Andrey Lelikov (c) 2006, Alexander Gordeev (c) 2006-2007, Jon Gough (c) 2007
>
> debug level is '3'
> Checking device (0000/0000) (005/001)
> - VendorID: 0000
> - ProductID: 0000
> - Manufacturer: unknown
> - Product: unknown
> - Serial Number: unknown
> - Bus: 005
> Trying to match device
> Device does not match - skipping
> Checking device (0000/0000) (004/001)
> - VendorID: 0000
> - ProductID: 0000
> - Manufacturer: unknown
> - Product: unknown
> - Serial Number: unknown
> - Bus: 004
> Trying to match device
> Device does not match - skipping
> Checking device (0665/5161) (003/004)
> - VendorID: 0665
> - ProductID: 5161
> - Manufacturer: Cypress Semiconductor
> - Product: USB to Serial
> - Serial Number: unknown
> - Bus: 003
> Trying to match device
> Device matches
> Starting UPS detection process...
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.9 119.9 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.0 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.0 NNN 60.2 13.6 N/.A 00001001]
> 0 out of 5 detection attempts failed (minimum failures: 2).
> Cancelling any pending shutdown or battery test.
> Asking for UPS information [I]...
> I => FAILED [short read]
> I detail: (0 bytes) =>
> Megatec protocol UPS detected.
> Parameter [ignoreoff]: [false]
> Asking for UPS power ratings [F]...
> F => OK [#120.0 005 12.00 60.0]
> 12.0V battery, present voltage (8549026304.0V) outside of supported
> intervals.
> This UPS has an unsupported combination of battery voltage/number of
> batteries.
> Cannot calculate charge percentage for this UPS.
> Done setting up the UPS.
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.2 NNN 60.2 13.6 N/.A 00001001]
> dstate_init: sock /var/state/ups/megatec_usb-ups1 open on fd 5
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.5 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.5 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.5 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.5 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.2 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.9 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.7 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 120.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.4 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
> Asking for UPS status [Q1]...
> Q1 => OK [(119.8 119.8 121.6 NNN 60.1 13.6 N/.A 00001001]
>
> [EMAIL PROTECTED] etc]#  /usr/local/ups/bin/upsc [EMAIL PROTECTED]
> battery.voltage: 0.00
> battery.voltage.nominal: 12.0
> driver.name: megatec_usb
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/usbdev3.4
> driver.version: 2.2.2
> driver.version.internal: 1.5.14
> input.frequency: 0.0
> input.frequency.nominal: 60.0
> input.voltage: 119.8
> input.voltage.fault: 119.8
> input.voltage.maximum: 119.8
> input.voltage.minimum: 119.8
> input.voltage.nominal: 120.0
> output.voltage: 120.8
> ups.beeper.status: disabled
> ups.delay.shutdown: 0
> ups.delay.start: 2
> ups.load: 0.0
> ups.mfr: unknown
> ups.model: unknown
> ups.serial: unknown
> ups.status: OL
> ups.type: online
>
>

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to