> I'm new to this list and I have a question concerning using the genericups > driver > (type 22) with the Cyberpower 485 in serial mode. > > When running the driver in debug mode: > > genericups -a myupsname_genericups22 -DDDDDD > > I observe the following statuses as the mains power dies, switching over > to battery > power, and then letting it discharge. > > Initially, with mains power on, status = OL. > > When mains power goes off, and we run on battery, status = OB. > > When battery level drops sufficiently the UPS starts beeping, and status = > OB OL. > > Shortly before battery dies the UPS beeps more frequently, status = OB OL.
This is all what we expect. > Battery dies, then status = OB, and then changes to OL. Could be the circuit that is controlling looses power. Since this UPS uses 'contact' closure signalling, there always will be a status (even if the UPS is not actively controlling the modem control lines). > When power is restored, status toggles from OB to OL to OB to OL a few > times and > then stays at OL. Possibly some kind of internal test, nothing to be worried about. > I assume that at the point we get OB OL this is the place we would be > shutting down > the computer? See the FAQ. > Why when the battery is discharged do we see the status OL? Is this just a > limitation > of using the genericups driver instead of one that is more appropriate for > my UPS? See above. Nothing to be worried about. After the UPS signals OB LB and the server picks this up, this state will be latched and there is no way back. > I did try using the powerpanel driver but that timed out and did not find > the UPS. Apparently, your UPS only supports 'contact closure' signalling or the cable used doesn't have the necessary wires for smart signalling. > Genericups type 7 seems to work the same as type 22. If you look in the manual page for the genericups driver, you'll find the signalling is identical. Adding type 22 was a mistake (since it isn't different from type 7), but since it has been like that for a couple of releases, we can't correct this without breaking things. > Is the genericups driver one that simply monitors the CTS, DTR etc. > signals? If so > should I care about these signals polarities, or does what I am already > seeing > indicate that everything is working as well as I can expect (that is > without having a > driver exactly for my UPS)? Spot on. Everything is fine and dandy. Best regards, Arjen -- Eindhoven - The Netherlands Key fingerprint - 66 4E 03 2C 9D B5 CB 9B 7A FE 7E C1 EE 88 BC 57 _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser