Arjen de Korte wrote:
Citeren Seann Clark <[EMAIL PROTECTED]>:

This output is after everything has been shut down and all NUT related items killed out of memory after a init script being run to stop the main items. The output of the debug is:
debug level is '3'
Trying binary protocol...
read: (20 bytes) => 2e 4f 50 31 35 30 30 20 20 20 20 2e 78 2e 3c 2e 35 31
30 30
CyberPower UPS with binary protocol on /dev/ttyS0 detected

The autodetection for the protocol works at least, it is reporting an OP1500 model.

send: (3 bytes) => 52 02 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 04 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 08 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 18 0d
read: (2 bytes) => 52 00

Here a couple of settings from the UPS are read. It is using the table for the OP series, so this is correct too.

send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7d 00 22 2e d6 80 b1 2e 09 f6 00 ff 0d
dstate_init: sock /var/run/nut/powerpanel-cyberpower-ups open on fd 6
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7c 00 21 2e d6 7f b1 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7d 00 22 2e d6 80 b1 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7d 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d

We succeeded to poll for the status four times in a row (without retries), so the communication is fine so far.

send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!

...but here the problems start.

It looks like we suddenly have developed a communication problem here, the UPS doesn't want to talk/listen to us anymore. Usually this has to do with the cable power for the UPS. Currently, the 'powerpanel' driver clears RTS and sets DTR. I noticed that both the 'cyberpower' and 'nitram' drivers set both. Could you try if changing line 93 in powerpanel.c to

    ser_set_rts(upsfd, 1);

fixes the problem? I suspect that clearing RTS might be a mistake here.

Best regards, Arjen
--Please keep list traffic on the list
After compiling the modified driver I am seeing this:

Tue Oct 28-11:33:[EMAIL PROTECTED]:drivers> ./powerpanel -DDD -u nut -a cyberpower-ups
Network UPS Tools -  CyberPower text/binary protocol UPS driver 0.23 (2.2.2)
Warning: This is an experimental driver.
Some features may not function correctly.

debug level is '3'
Trying binary protocol...
read: (4 bytes) => 2e 09 f6 ff
Expected 20 bytes but only got 4
read: (20 bytes) => 2e 4f 50 31 35 30 30 20 20 20 20 2e 78 2e 3c 2e 35 31
30 30
CyberPower UPS with binary protocol on /dev/ttyS0 detected
send: (3 bytes) => 52 02 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 04 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 08 0d
read: (2 bytes) => 52 00
send: (3 bytes) => 52 18 0d
read: (2 bytes) => 52 00
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7e 00 21 2e d6 80 b2 2e 09 f6 00 ff 0d
dstate_init: sock /var/state/ups/powerpanel-cyberpower-ups open on fd 6
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7e 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7c 00 22 2e d6 7f b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7b 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7e 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7c 00 21 2e d6 81 b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: (14 bytes) => 23 7d 00 22 2e d6 80 b2 2e 09 f6 00 ff 0d
send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!
send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!
send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!
send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!
send: (2 bytes) => 44 0d
read: timed out
Communications with UPS lost: Status read failed!
^CSignal 2: exiting

So that didn't fix the issue, but judging from your statements, related to it, it wasn't expected to really solve it, more just to change it to be more like the old driver that 'works'. It looks like it got a few more reads into that though before failing on the status.


Regards,
Seann

Attachment: smime.p7s
Description: S/MIME Cryptographic Signature

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to