Citeren Igor R <[email protected]>: > We are using the equipment "MUSTEK PowerMust 3000 NetGuard RM". That is > using Megatec protocol. But unfortunately not all the data can be viewed > correctly when dumping from utility "upsc". > > For example: > > upsbox# upsc mus...@localhost > battery.voltage: 108.00 > battery.voltage.nominal: 96.0 > driver.name: megatec > driver.parameter.pollinterval: 2 > driver.parameter.port: /dev/cuad0 > driver.version: 2.4.1 > driver.version.internal: 1.6 > input.frequency: 50.0 > input.frequency.nominal: 50.0 > input.voltage: 227.0 > input.voltage.fault: 227.0 > input.voltage.maximum: 228.8 > input.voltage.minimum: 224.1 > input.voltage.nominal: 220.0 > output.voltage: 227.0 > ups.beeper.status: enabled > ups.delay.shutdown: 0 > ups.delay.start: 2 > ups.load: 30.0 > ups.mfr: unknown > ups.model: unknown > ups.serial: unknown > ups.status: OL > ups.temperature: 60.6 > ups.type: standby
Nothing wrong with the above. What data that isn't correct in your opinion are you referring to? > Also when starting NUT program we can see the following messages: > > upsbox# /usr/local/etc/rc.d/nut start > Network UPS Tools - UPS driver controller 2.4.1 > Network UPS Tools - Megatec protocol driver 1.6 (2.4.1) > Megatec protocol UPS detected. > This UPS has an unsupported combination of battery voltage/number of > batteries. > Cannot calculate charge percentage for this UPS. > Starting nut. You need to read the documentation and FAQ first, before asking for help. How to make the above messages disappear is described in 'man 8 megatec'. > As far as we understand this model of the equipment is not being supported > currently. Could you please inform me who do I need refer to to add this > equipment to the list of supported ones? You're doing a fine job now, the mailing list is the first place you go to when asking for help. Best regards, Arjen -- Please keep list traffic on the list _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser