> Citeren Rene Bartsch <[email protected]>:
>
>> Command: "/lib/nut/apcsmart -a su900i -DDDDD"
>>
>> ----------------------------------------- snip
>> -------------------------------------------------
>>
>> Network UPS Tools - APC Smart protocol driver 2.00 (2.4.1)
>> APC command table version 2.0
>> debug level is '5'
>> send_to_all: SETINFO ups.mfr "APC"
>> Attempting firmware lookup
>> Attempting to contact older Smart-UPS version
>> Firmware: [7QI]
>
> That's all we need for now.
>
> I've just added support for this version, assuming that it is similar
> to the Smart UPS 900 firmware [7TD] we already support. We have
> confirmed that this is the case for the 600 and 1250 models, so this
> probably goes for the 900 as well.
>
> I've added support for all variations of the [678][QT][DI] models now,
> so if you grab the latest version from the SVN trunk, you should be
> fine. Please let us know if this works for you.
>
> Best regards, Arjen
> --
> Please keep list traffic on the list
>
>


Command: "upsc su900i"

------------------------------------------ snip 
-----------------------------------------------

battery.alarm.threshold: 0
battery.charge: 100.0
battery.charge.restart: 10
battery.date: 11/02/01
battery.runtime: 4440
battery.runtime.low: 120
battery.voltage: 27.67
battery.voltage.nominal: 024
driver.name: apcsmart
driver.parameter.cable: 940-0024C
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyUSB0
driver.version: 2.4.1
driver.version.internal: 2.03
input.frequency: 50.00
input.quality: FF
input.sensitivity: H
input.transfer.high: 253
input.transfer.low: 196
input.transfer.reason: O
input.voltage: 229.4
input.voltage.maximum: 231.8
input.voltage.minimum: 229.4
output.voltage: 229.4
output.voltage.nominal: 225
ups.delay.shutdown: 180
ups.delay.start: 300
ups.id: UPS_IDEN
ups.load: 006.2
ups.mfr: APC
ups.mfr.date: 02/18/93
ups.serial: 00016325
ups.status: OL
ups.temperature: 045.9
ups.test.interval: 0
ups.test.result: NO


------------------------------------------ snap 
-----------------------------------------------


Many thanks for the fast help! :)

Best regards,

Renne



_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to