At 9:11 AM +0200 7/27/09, Arnaud Quette wrote:
2009/7/27 Maurice Volaski <<mailto:[email protected]>[email protected]>

This mib used to work, so is there a way to go back to the version prior to this one without downgrading the whole package?


yes, only take the snmp-ups driver from the previous working release.

2.2.2 and 2.0.5 also complain but with fewer errors. 1.5.15 does not complain, so it's the one I added. Oddly, this old version doesn't seem to like that /var/state/ups directory is owned by user nut. I had to manually pass "-u nut" to upsdrvctl to get it to work.

Anyway, now that the script is starting, I'm seeing "failed - got [ERR ACCESS-DENIED]" errors from upsmon, and I don't know why. I noted that the configuration has changed. It seems ACLs and ACCEPT are no longer used and have been replaced with LISTEN, but I have set that.

provide us back with an SNMP walk so that we can check the exact issue and find a suitable solution.
this might have something to do with the ".0" suffix...
starting with the RFC1628 MIB entry point (ie 1.3.6.1.2.1.33) is sufficient.

mib-2.33.1.1.1.0 = STRING: "Liebert Corporation"
mib-2.33.1.1.2.0 = STRING: "GXT2-2000RT120                "
mib-2.33.1.1.3.0 = STRING: "GXT2MR15E-2K3K                "
mib-2.33.1.1.4.0 = STRING: "2.200.1"
mib-2.33.1.1.5.0 = STRING: "upswallleft"
mib-2.33.1.2.1.0 = INTEGER: 2
mib-2.33.1.2.2.0 = INTEGER: 0
mib-2.33.1.2.3.0 = INTEGER: 6
mib-2.33.1.2.4.0 = INTEGER: 100
mib-2.33.1.2.5.0 = INTEGER: 553
mib-2.33.1.3.1.0 = Counter32: 0
mib-2.33.1.3.2.0 = INTEGER: 1
mib-2.33.1.3.3.1.2.1 = INTEGER: 600
mib-2.33.1.3.3.1.3.1 = INTEGER: 114
mib-2.33.1.4.1.0 = INTEGER: 3
mib-2.33.1.4.2.0 = INTEGER: 600
mib-2.33.1.4.3.0 = INTEGER: 1
mib-2.33.1.4.4.1.2.1 = INTEGER: 120
mib-2.33.1.4.4.1.3.1 = INTEGER: 112
mib-2.33.1.5.1.0 = INTEGER: 600
mib-2.33.1.5.2.0 = INTEGER: 1
mib-2.33.1.5.3.1.2.1 = INTEGER: 114
mib-2.33.1.6.1.0 = Gauge32: 0
mib-2.33.1.7.1.0 = OID: mib-2.33.1.7.7.1
mib-2.33.1.7.2.0 = INTEGER: 1
mib-2.33.1.7.3.0 = INTEGER: 6
mib-2.33.1.7.4.0 = ""
mib-2.33.1.7.5.0 = Timeticks: (0) 0:00:00.00
mib-2.33.1.7.6.0 = INTEGER: 0
mib-2.33.1.8.1.0 = INTEGER: 1
mib-2.33.1.8.2.0 = INTEGER: 0
mib-2.33.1.8.3.0 = INTEGER: 0
mib-2.33.1.8.4.0 = INTEGER: 0
mib-2.33.1.8.5.0 = INTEGER: 1
mib-2.33.1.9.1.0 = INTEGER: 120
mib-2.33.1.9.2.0 = INTEGER: 600
mib-2.33.1.9.3.0 = INTEGER: 120
mib-2.33.1.9.4.0 = INTEGER: 600
mib-2.33.1.9.5.0 = INTEGER: 2000
mib-2.33.1.9.7.0 = INTEGER: 2
mib-2.33.1.9.8.0 = INTEGER: 2
--

Maurice Volaski, [email protected]
Computing Support, Rose F. Kennedy Center
Albert Einstein College of Medicine of Yeshiva University

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to