While fundamentally working, I'm having a few issues with the driver...
The default voltage quads (for every model) are way off... Showing
~95v when it should be ~117V. I've changed the 4th/final coefficient
to +5.0, but haven't tested extensively (with fluctuating voltages).
The input/output voltage appears to be swapped _most of the time_.
When doing a battery test, or when unplugged, the input stays steady,
and the _output_ voltage reports a drop to ~15V. OTOH, when the UPS
is shutdown, the ordering appears correct, as the input stays steady,
and the output shows ~5V.
For the above, the Powercom upsmon software appears to special-case
those ~5/15V results, and on the next update, report it as 0V. I have
no idea how to even special-case the screwy input/output-swapping
behavior...
./powercom -a ups0 -DDD
Network UPS Tools - PowerCom protocol UPS driver 0.12 (2.4.1-2308)
0.000000 debug level is '3'
0.001406 Flow control disable
0.150003 Detected: BNT-other-500AP , 120V
0.153986 Values of arguments:
0.154001 manufacturer : 'PowerCom'
0.154009 model name : 'BNT-other-500AP'
0.154015 serial number : 'Unknown'
0.154022 line voltage : '120'
0.154029 type : 'BNT-other'
0.154036 number of bytes from UPS: '16'
0.154042 method of flow control : 'no_flow_control'
0.154051 validation sequence: '{{8,0},{8,0},{8,0}}'
0.154059 shutdown arguments: '{{1,30},y}'
0.154073 frequency calculation coefficients: '{0.000208,0.000000}'
0.154084 load percentage calculation coefficients:
'{1.447400,0.000000,0.859400,0.000000}'
0.154101 battery percentage calculation coefficients:
'{5.000000,0.326800,-825.000000,0.465110,0.000000}'
0.154110 voltage calculation coefficients: '{0.954500,5.000000}'
0.305927 input.frequency (raw data): [raw: 80]
0.305966 input.frequency: 60.09
0.305974 output.frequency (raw data): [raw: 80]
0.305987 output.frequency: 60.09
0.305994 ups.load (raw data): [raw: 0]
0.306008 ups.load: 0.0
0.306015 battery.charge (raw data): [raw: 197]
0.306027 battery.charge: 100.0
0.306035 input.voltage (raw data): [raw: 119]
0.306048 input.voltage: 118.6
0.306055 output.voltage (raw data): [raw: 26]
0.306067 output.voltage: 29.8
0.306079 STATUS: OB TEST
0.306338 dstate_init: sock /var/state/ups/powercom-ups0 open on fd 5
0.453868 input.frequency (raw data): [raw: 80]
0.453907 input.frequency: 60.09
0.453914 output.frequency (raw data): [raw: 80]
0.453925 output.frequency: 60.09
0.453931 ups.load (raw data): [raw: 0]
0.453944 ups.load: 0.0
0.453950 battery.charge (raw data): [raw: 195]
0.453961 battery.charge: 100.0
0.453968 input.voltage (raw data): [raw: 119]
0.453979 input.voltage: 118.6
0.453986 output.voltage (raw data): [raw: 26]
0.453997 output.voltage: 29.8
0.454008 STATUS: OB TEST
1.853474 new connection on fd 6
2.457023 input.frequency (raw data): [raw: 80]
2.457070 input.frequency: 60.09
2.457077 output.frequency (raw data): [raw: 80]
2.457088 output.frequency: 60.09
2.457095 ups.load (raw data): [raw: 0]
2.457108 ups.load: 0.0
2.457115 battery.charge (raw data): [raw: 191]
2.457140 battery.charge: 95.0
2.457147 input.voltage (raw data): [raw: 119]
2.457159 input.voltage: 118.6
2.457167 output.voltage (raw data): [raw: 25]
2.457185 output.voltage: 28.9
2.457197 STATUS: OB TEST
4.456188 input.frequency (raw data): [raw: 80]
4.456240 input.frequency: 60.09
4.456248 output.frequency (raw data): [raw: 80]
4.456259 output.frequency: 60.09
4.456266 ups.load (raw data): [raw: 0]
4.456279 ups.load: 0.0
4.456286 battery.charge (raw data): [raw: 193]
4.456656 battery.charge: 100.0
4.456673 input.voltage (raw data): [raw: 119]
4.456686 input.voltage: 118.6
4.456693 output.voltage (raw data): [raw: 119]
4.456849 output.voltage: 118.6
4.456978 STATUS: OL
6.455365 input.frequency (raw data): [raw: 80]
6.455420 input.frequency: 60.09
6.455428 output.frequency (raw data): [raw: 80]
6.455439 output.frequency: 60.09
6.455445 ups.load (raw data): [raw: 0]
6.455458 ups.load: 0.0
6.455465 battery.charge (raw data): [raw: 193]
6.455476 battery.charge: 100.0
6.455483 input.voltage (raw data): [raw: 119]
6.455494 input.voltage: 118.6
6.455500 output.voltage (raw data): [raw: 119]
6.455511 output.voltage: 118.6
6.455522 STATUS: OL
For anyone wondering, I wouldn't recommend these units to anyone else.
A 400W dumb/"personal" UPS from APC/CyberPower/Tripp-Lite is likely
just as capable, and certainly built better...
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser