Hi Arnaud,

Here's the upsc output. I Can confirm that shutdown is working too at the 
moment - we have to do further testing. But currently I'm running on the 
unpatched 2.4.1 version with bcmxcp.


dacoks20dx:~# upsc hpr1...@localhost
ambient.temperature: 53
ambient.temperature.high: 75
battery.charge: 89
battery.runtime: 1476
battery.voltage: 36.38
driver.name: bcmxcp
driver.parameter.baud_rate: 9600
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS1
driver.version: 2.4.1
driver.version.internal: 0.21
input.frequency: 50.34
input.frequency.high: 55
input.frequency.low: 45
input.frequency.nominal: 50
input.transfer.boost.high: 207
input.transfer.high: 266
input.transfer.low: 194
input.transfer.trim.low: 243
input.voltage: 228
input.voltage.nominal: 230
outlet.1.delay.shutdown: -1
outlet.1.delay.start: 0
outlet.1.id: 1
outlet.1.status: On
outlet.2.delay.shutdown: -1
outlet.2.delay.start: 1
outlet.2.id: 2
outlet.2.status: On
output.current:  1.9
output.current.nominal:  6.4
output.frequency: 50.34
output.phases: 1
output.voltage: 228
output.voltage.nominal: 230
ups.alarm: BATTERIES_DISCONNECTED
ups.beeper.status: muted
ups.firmware: Cont:02.00 Inve:02.00
ups.load:  29.3
ups.model: HP R1500 G2 1500VA
ups.power: 439
ups.power.nominal: 1500
ups.serial: 3C88431991
ups.status: ALARM OL



-----Ursprüngliche Nachricht-----
Von: Arnaud Quette [mailto:[email protected]]
Gesendet: Donnerstag, 18. Februar 2010 18:39
An: Schupfer Stephan
Cc: [email protected]
Betreff: Re: [Nut-upsuser] HP R1500 G2 UPS

2010/2/18 Schupfer Stephan <[email protected]>:
> Hi Arnaud,
>
> Thank you for that info -  that was quite important to me to know to get it 
> working - so now i have communication over serial port with bcmxcp.


can you please confirm that at least shutdown is working.
sending back an upsc output would also be nice.

while waiting for the USB side completion, I'll add the serial
compatibility for 2.4.2 (due for tomorrow!).

cheers,
Arnaud
--
Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.free.fr/

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to