Hi all,

I just acquired a new UPS and have been trying to get it to work with NUT. It's 
an Eaton/Powerware 9120 700i with both USB and RS-232 interfaces.

I first tried the USB interface (using bcmxcp_usb) and found that the UPS 
worked fine for a few minutes but then NUT lost communication and didn't get it 
back. In addition the UPS itself seemed to lock up at one point such that the 
inverter shut off and the front panel buttons didn't work - I had to remove the 
batteries to reset it.

So I moved on to try the serial port instead. Here the UPS also regularly loses 
the connection but at least it doesn't lock the UPS right up - maybe that was a 
fluke. If I restart the driver, the communication is regained for a few minutes 
but then drops again. Below are excerpts from running '/lib/nut/bcmxcp -DDD -a 
pw9120'.

Any ideas?

Many thanks,
Chris

   0.000000     debug level is '3'
   0.000659     Attempting to autodect baudrate
   1.591977     Receive error (PW_COMMAND_START_BYTE): 0!!!

   2.592977     Receive error (PW_COMMAND_START_BYTE): 0!!!

   3.593976     Receive error (PW_COMMAND_START_BYTE): 0!!!

   3.593992     No response from UPS on /dev/ttyS0 with baudrate 1200
   5.184976     Receive error (PW_COMMAND_START_BYTE): 0!!!

   6.185976     Receive error (PW_COMMAND_START_BYTE): 0!!!

   7.186975     Receive error (PW_COMMAND_START_BYTE): 0!!!

   7.186991     No response from UPS on /dev/ttyS0 with baudrate 2400
   8.777973     Receive error (PW_COMMAND_START_BYTE): 0!!!

   9.778973     Receive error (PW_COMMAND_START_BYTE): 0!!!

  10.779975     Receive error (PW_COMMAND_START_BYTE): 0!!!

  10.779991     No response from UPS on /dev/ttyS0 with baudrate 4800
  11.728905     Connected to UPS on /dev/ttyS0 with baudrate 9600
  11.985634     Length of meter map: 82

  11.985646     Index   Offset  Format  NUT

  11.985652     0021    0000    f0      None
  11.985656     0023    0004    f0      ups.power
  11.985660     0027    0008    41      output.frequency
  11.985663     0028    0012    41      input.frequency
  11.985667     0033    0016    51      battery.voltage
  11.985671     0034    0020    f0      battery.charge
  11.985675     0035    0024    e2      battery.runtime
  11.985679     0056    0028    f0      input.voltage
  11.985682     0062    0032    f0      ambient.temperature
  11.985686     0065    0036    41      output.current
  11.985689     0068    0040    41      output.current.nominal
  11.985693     0071    0044    f0      None
  11.985696     0078    0048    f0      output.voltage
  11.985699     

  11.985702     Length of alarm map: 27

  11.985705     Index   Alarm   Supported

  11.985710     -001    INVERTER_AC_OVER_VOLTAGE        No
  11.985714     -001    INVERTER_AC_UNDER_VOLTAGE       No
  11.985717     -001    INVERTER_OVER_OR_UNDER_FREQ     No
  11.985720     -001    BYPASS_AC_OVER_VOLTAGE  No
  11.985724     -001    BYPASS_AC_UNDER_VOLTAGE No
  11.985727     -001    BYPASS_OVER_OR_UNDER_FREQ       No
  11.985730     0000    INPUT_AC_OVER_VOLTAGE   Yes
  11.985733     0001    INPUT_AC_UNDER_VOLTAGE  Yes
  11.985737     0002    INPUT_UNDER_OR_OVER_FREQ        Yes
  11.985740     0003    OUTPUT_OVER_VOLTAGE     Yes
  11.985744     0004    OUTPUT_UNDER_VOLTAGE    Yes
  11.985747     -001    OUTPUT_UNDER_OR_OVER_FREQ       No
  11.985750     0005    REMOTE_EMERGENCY_PWR_OFF        Yes
  11.985753     -001    REMOTE_GO_TO_BYPASS     No
  11.985756     -001    BUILDING_ALARM_6        No
  11.985760     -001    BUILDING_ALARM_5        No
  11.985763     -001    BUILDING_ALARM_4        No
  11.985766     -001    BUILDING_ALARM_3        No
  11.985770     -001    BUILDING_ALARM_2        No
  11.985773     -001    BUILDING_ALARM_1        No
  11.985777     -001    STATIC_SWITCH_OVER_TEMP No
  11.985780     -001    CHARGER_OVER_TEMP       No
  11.985783     -001    CHARGER_LOGIC_PWR_FAIL  No
  11.985786     -001    CHARGER_OVER_VOLTAGE_OR_CURRENT No
  11.985790     -001    INVERTER_OVER_TEMP      No
  11.985793     0006    OUTPUT_OVERLOAD Yes
  11.985796     -001    RECTIFIER_INPUT_OVER_CURRENT    No
  11.985799     -001    INVERTER_OUTPUT_OVER_CURRENT    No
  11.985803     -001    DC_LINK_OVER_VOLTAGE    No
  11.985806     -001    DC_LINK_UNDER_VOLTAGE   No
  11.985809     -001    RECTIFIER_FAILED        No
  11.985812     0007    INVERTER_FAULT  Yes
  11.985815     -001    BATTERY_CONNECTOR_FAIL  No
  11.985819     -001    BYPASS_BREAKER_FAIL     No
  11.985822     0008    CHARGER_FAIL    Yes
  11.985825     -001    RAMP_UP_FAILED  No
  11.985828     -001    STATIC_SWITCH_FAILED    No
  11.985831     -001    ANALOG_AD_REF_FAIL      No
  11.985835     -001    BYPASS_UNCALIBRATED     No
  11.985838     -001    RECTIFIER_UNCALIBRATED  No
  11.985841     -001    OUTPUT_UNCALIBRATED     No
  11.985844     -001    INVERTER_UNCALIBRATED   No
  11.985848     -001    DC_VOLT_UNCALIBRATED    No
  11.985851     -001    OUTPUT_CURRENT_UNCALIBRATED     No
  11.985854     -001    RECTIFIER_CURRENT_UNCALIBRATED  No
  11.985857     -001    BATTERY_CURRENT_UNCALIBRATED    No
  11.985860     -001    INVERTER_ON_OFF_STAT_FAIL       No
  11.985864     -001    BATTERY_CURRENT_LIMIT   No
  11.985867     -001    INVERTER_STARTUP_FAIL   No
  11.985870     -001    ANALOG_BOARD_AD_STAT_FAIL       No
  11.985873     -001    OUTPUT_CURRENT_OVER_100 No
  11.985878     -001    BATTERY_GROUND_FAULT    No
  11.985881     -001    WAITING_FOR_CHARGER_SYNC        No
  11.985885     -001    NV_RAM_FAIL     No
  11.985888     -001    ANALOG_BOARD_AD_TIMEOUT No
  11.985891     -001    SHUTDOWN_IMMINENT       No
  11.985894     0009    BATTERY_LOW     Yes
  11.985897     0010    UTILITY_FAIL    Yes
  11.985901     0011    OUTPUT_SHORT_CIRCUIT    Yes
  11.985904     0012    UTILITY_NOT_PRESENT     Yes
  11.985907     -001    FULL_TIME_CHARGING      No
  11.985911     -001    FAST_BYPASS_COMMAND     No
  11.985914     -001    AD_ERROR        No
  11.985917     -001    INTERNAL_COM_FAIL       No
  11.985920     -001    RECTIFIER_SELFTEST_FAIL No
  11.985924     -001    RECTIFIER_EEPROM_FAIL   No
  11.985927     -001    RECTIFIER_EPROM_FAIL    No
  11.985930     -001    INPUT_LINE_VOLTAGE_LOSS No
  11.985933     0013    BATTERY_DC_OVER_VOLTAGE Yes
  11.985936     -001    POWER_SUPPLY_OVER_TEMP  No
  11.985939     -001    POWER_SUPPLY_FAIL       No
  11.985943     -001    POWER_SUPPLY_5V_FAIL    No
  11.985946     -001    POWER_SUPPLY_12V_FAIL   No
  11.985949     0014    HEATSINK_OVER_TEMP      Yes
  11.985953     -001    HEATSINK_TEMP_SENSOR_FAIL       No
  11.985956     -001    RECTIFIER_CURRENT_OVER_125      No
  11.985959     -001    RECTIFIER_FAULT_INTERRUPT_FAIL  No
  11.985967     -001    RECTIFIER_POWER_CAPASITOR_FAIL  No
  11.985970     -001    INVERTER_PROGRAM_STACK_ERROR    No
  11.985973     -001    INVERTER_BOARD_SELFTEST_FAIL    No
  11.985976     -001    INVERTER_AD_SELFTEST_FAIL       No
  11.985980     -001    INVERTER_RAM_SELFTEST_FAIL      No
  11.985983     -001    NV_MEMORY_CHECKSUM_FAIL No
  11.985986     -001    PROGRAM_CHECKSUM_FAIL   No
  11.985990     -001    INVERTER_CPU_SELFTEST_FAIL      No
  11.985993     -001    NETWORK_NOT_RESPONDING  No
  11.985996     -001    FRONT_PANEL_SELFTEST_FAIL       No
  11.985999     -001    NODE_EEPROM_VERIFICATION_ERROR  No
  11.986003     -001    OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
  11.986006     -001    OUTPUT_DC_OVER_VOLTAGE  No
  11.986009     -001    INPUT_PHASE_ROTATION_ERROR      No
  11.986012     -001    INVERTER_RAMP_UP_TEST_FAILED    No
  11.986016     -001    INVERTER_OFF_COMMAND    No
  11.986019     -001    INVERTER_ON_COMMAND     No
  11.986022     -001    TO_BYPASS_COMMAND       No
  11.986025     -001    FROM_BYPASS_COMMAND     No
  11.986029     -001    AUTO_MODE_COMMAND       No
  11.986032     -001    EMERGENCY_SHUTDOWN_COMMAND      No
  11.986035     -001    SETUP_SWITCH_OPEN       No
  11.986039     -001    INVERTER_OVER_VOLT_INT  No
  11.986042     -001    INVERTER_UNDER_VOLT_INT No
  11.986045     -001    ABSOLUTE_DCOV_ACOV      No
  11.986049     -001    PHASE_A_CURRENT_LIMIT   No
  11.986052     -001    PHASE_B_CURRENT_LIMIT   No
  11.986055     -001    PHASE_C_CURRENT_LIMIT   No
  11.986058     -001    BYPASS_NOT_AVAILABLE    No
  11.986061     -001    RECTIFIER_BREAKER_OPEN  No
  11.986065     -001    BATTERY_CONTACTOR_OPEN  No
  11.986068     -001    INVERTER_CONTACTOR_OPEN No
  11.986071     -001    BYPASS_BREAKER_OPEN     No
  11.986074     -001    INV_BOARD_ACOV_INT_TEST_FAIL    No
  11.986077     -001    INVERTER_OVER_TEMP_TRIP No
  11.986081     -001    INV_BOARD_ACUV_INT_TEST_FAIL    No
  11.986084     -001    INVERTER_VOLTAGE_FEEDBACK_ERROR No
  11.986087     -001    DC_UNDER_VOLTAGE_TIMEOUT        No
  11.986091     -001    AC_UNDER_VOLTAGE_TIMEOUT        No
  11.986094     -001    DC_UNDER_VOLTAGE_WHILE_CHARGE   No
  11.986097     -001    INVERTER_VOLTAGE_BIAS_ERROR     No
  11.986100     -001    RECTIFIER_PHASE_ROTATION        No
  11.986103     -001    BYPASS_PHASER_ROTATION  No
  11.986107     -001    SYSTEM_INTERFACE_BOARD_FAIL     No
  11.986110     -001    PARALLEL_BOARD_FAIL     No
  11.986113     -001    LOST_LOAD_SHARING_PHASE_A       No
  11.986116     -001    LOST_LOAD_SHARING_PHASE_B       No
  11.986120     -001    LOST_LOAD_SHARING_PHASE_C       No
  11.986123     -001    DC_OVER_VOLTAGE_TIMEOUT No
  11.986126     -001    BATTERY_TOTALLY_DISCHARGED      No
  11.986129     -001    INVERTER_PHASE_BIAS_ERROR       No
  11.986133     -001    INVERTER_VOLTAGE_BIAS_ERROR_2   No
  11.986136     -001    DC_LINK_BLEED_COMPLETE  No
  11.986139     -001    LARGE_CHARGER_INPUT_CURRENT     No
  11.986143     -001    INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
  11.986146     -001    LOSS_OF_REDUNDANCY      No
  11.986149     -001    LOSS_OF_SYNC_BUS        No
  11.986152     -001    RECTIFIER_BREAKER_SHUNT_TRIP    No
  11.986156     -001    LOSS_OF_CHARGER_SYNC    No
  11.986159     -001    INVERTER_LOW_LEVEL_TEST_TIMEOUT No
  11.986162     -001    OUTPUT_BREAKER_OPEN     No
  11.986165     -001    CONTROL_POWER_ON        No
  11.986169     -001    INVERTER_ON     No
  11.986172     -001    CHARGER_ON      No
  11.986175     -001    BYPASS_ON       No
  11.986178     -001    BYPASS_POWER_LOSS       No
  11.986181     -001    ON_MANUAL_BYPASS        No
  11.986185     -001    BYPASS_MANUAL_TURN_OFF  No
  11.986188     -001    INVERTER_BLEEDING_DC_LINK_VOLT  No
  11.986191     -001    CPU_ISR_ERROR   No
  11.986195     -001    SYSTEM_ISR_RESTART      No
  11.986198     -001    PARALLEL_DC     No
  11.986201     -001    BATTERY_NEEDS_SERVICE   No
  11.986204     -001    BATTERY_CHARGING        No
  11.986208     0015    BATTERY_NOT_CHARGED     Yes
  11.986211     -001    DISABLED_BATTERY_TIME   No
  11.986214     -001    SERIES_7000_ENABLE      No
  11.986217     -001    OTHER_UPS_ON    No
  11.986220     -001    PARALLEL_INVERTER       No
  11.986224     -001    UPS_IN_PARALLEL No
  11.986227     -001    OUTPUT_BREAKER_REALY_FAIL       No
  11.986230     -001    CONTROL_POWER_OFF       No
  11.986233     -001    LEVEL_2_OVERLOAD_PHASE_A        No
  11.986236     -001    LEVEL_2_OVERLOAD_PHASE_B        No
  11.986240     -001    LEVEL_2_OVERLOAD_PHASE_C        No
  11.986243     -001    LEVEL_3_OVERLOAD_PHASE_A        No
  11.986246     -001    LEVEL_3_OVERLOAD_PHASE_B        No
  11.986249     -001    LEVEL_3_OVERLOAD_PHASE_C        No
  11.986252     -001    LEVEL_4_OVERLOAD_PHASE_A        No
  11.986256     -001    LEVEL_4_OVERLOAD_PHASE_B        No
  11.986259     -001    LEVEL_4_OVERLOAD_PHASE_C        No
  11.986262     0016    UPS_ON_BATTERY  Yes
  11.986265     0017    UPS_ON_BYPASS   Yes
  11.986268     -001    LOAD_DUMPED     No
  11.986272     -001    LOAD_ON_INVERTER        No
  11.986275     -001    UPS_ON_COMMAND  No
  11.986278     -001    UPS_OFF_COMMAND No
  11.986282     0018    LOW_BATTERY_SHUTDOWN    Yes
  11.986285     -001    AUTO_ON_ENABLED No
  11.986289     -001    SOFTWARE_INCOMPABILITY_DETECTED No
  11.986292     -001    INVERTER_TEMP_SENSOR_FAILED     No
  11.986295     -001    DC_START_OCCURED        No
  11.986299     -001    IN_PARALLEL_OPERATION   No
  11.986302     -001    SYNCING_TO_BYPASS       No
  11.986305     -001    RAMPING_UPS_UP  No
  11.986308     -001    INVERTER_ON_DELAY       No
  11.986312     -001    CHARGER_ON_DELAY        No
  11.986315     -001    WAITING_FOR_UTIL_INPUT  No
  11.986318     -001    CLOSE_BYPASS_BREAKER    No
  11.986322     -001    TEMPORARY_BYPASS_OPERATION      No
  11.986325     -001    SYNCING_TO_OUTPUT       No
  11.986328     -001    BYPASS_FAILURE  No
  11.986331     -001    AUTO_OFF_COMMAND_EXECUTED       No
  11.986334     -001    AUTO_ON_COMMAND_EXECUTED        No
  11.986338     0019    BATTERY_TEST_FAILED     Yes
  11.986341     -001    FUSE_FAIL       No
  11.986344     -001    FAN_FAIL        No
  11.986347     0020    SITE_WIRING_FAULT       Yes
  11.986351     -001    BACKFEED_CONTACTOR_FAIL No
  11.986354     -001    ON_BUCK No
  11.986357     -001    ON_BOOST        No
  11.986360     -001    ON_DOUBLE_BOOST No
  11.986363     0021    BATTERIES_DISCONNECTED  Yes
  11.986366     -001    UPS_CABINET_OVER_TEMP   No
  11.986370     -001    TRANSFORMER_OVER_TEMP   No
  11.986373     -001    AMBIENT_UNDER_TEMP      No
  11.986376     0022    AMBIENT_OVER_TEMP       Yes
  11.986379     -001    CABINET_DOOR_OPEN       No
  11.986382     -001    CABINET_DOOR_OPEN_VOLT_PRESENT  No
  11.986386     -001    AUTO_SHUTDOWN_PENDING   No
  11.986389     -001    TAP_SWITCHING_REALY_PENDING     No
  11.986392     -001    UNABLE_TO_CHARGE_BATTERIES      No
  11.986396     -001    STARTUP_FAILURE_CHECK_EPO       No
  11.986399     -001    AUTOMATIC_STARTUP_PENDING       No
  11.986402     -001    MODEM_FAILED    No
  11.986405     -001    INCOMING_MODEM_CALL_STARTED     No
  11.986408     -001    OUTGOING_MODEM_CALL_STARTED     No
  11.986411     -001    MODEM_CONNECTION_ESTABLISHED    No
  11.986415     -001    MODEM_CALL_COMPLETED_SUCCESS    No
  11.986418     

  11.986421     Length of Config_block: 80

  11.986424     Length of statistics map: 0

  11.986427     Length of command list: 26

  11.986430     Length of outlet_block: 14

  11.986433     Length of alarm_block: 22

  12.016909     init_outlet(14), res=14
  12.016919     Number of outlets: 2

  12.016924     Number of bytes: 6

  12.016927     Outlet number: 1

  12.016934     Outlet state: 1

  12.016940     Auto delay off: -1

  12.016946     Auto delay on: 0

  12.016951     Outlet number: 2

  12.016957     Outlet state: 1

  12.016966     Auto delay off: -1

  12.016972     Auto delay on: 0

  12.172925     entering init_command_map()
  12.216908     Command list block supported.
  12.324932     init_outlet(14), res=14
  12.324942     Number of outlets: 2

  12.324946     Number of bytes: 6

  12.324950     Outlet number: 1

  12.324954     Outlet state: 1

  12.324962     Auto delay off: -1

  12.324967     Auto delay on: 0

  12.324972     Outlet number: 2

  12.324976     Outlet state: 1

  12.324981     Auto delay off: -1

  12.324986     Auto delay on: 0

  12.385001     dstate_init: sock /var/run/nut/bcmxcp-pw9120 open on fd 5
  12.489410     init_outlet(14), res=14
  12.489425     Number of outlets: 2

  12.489429     Number of bytes: 6

  12.489433     Outlet number: 1

  12.489438     Outlet state: 1

  12.489443     Auto delay off: -1

  12.489447     Auto delay on: 0

  12.489452     Outlet number: 2

  12.489456     Outlet state: 1

  12.489460     Auto delay off: -1

  12.489469     Auto delay on: 0

  12.548921     new connection on fd 6
  14.492907     init_outlet(14), res=14
  14.492921     Number of outlets: 2

  14.492925     Number of bytes: 6

  14.492929     Outlet number: 1

  14.492934     Outlet state: 1

  14.492938     Auto delay off: -1

  14.492943     Auto delay on: 0

  14.492947     Outlet number: 2

  14.492951     Outlet state: 1

  14.492955     Auto delay off: -1

  14.492960     Auto delay on: 0

  16.492911     init_outlet(14), res=14
  16.492925     Number of outlets: 2

  16.492929     Number of bytes: 6

  16.492932     Outlet number: 1

  16.492938     Outlet state: 1

  16.492942     Auto delay off: -1

  16.492947     Auto delay on: 0

  16.492951     Outlet number: 2

  16.492955     Outlet state: 1

  16.492960     Auto delay off: -1

  16.492968     Auto delay on: 0

>>>> SNIP <<<<

 693.012911     init_outlet(14), res=14
 693.012926     Number of outlets: 2

 693.012930     Number of bytes: 6

 693.012934     Outlet number: 1

 693.012939     Outlet state: 1

 693.012944     Auto delay off: -1

 693.012949     Auto delay on: 0

 693.012953     Outlet number: 2

 693.012957     Outlet state: 1

 693.012965     Auto delay off: -1

 693.012971     Auto delay on: 0

 695.016909     init_outlet(14), res=14
 695.016922     Number of outlets: 2

 695.016926     Number of bytes: 6

 695.016930     Outlet number: 1

 695.016935     Outlet state: 1

 695.016939     Auto delay off: -1

 695.016944     Auto delay on: 0

 695.016948     Outlet number: 2

 695.016953     Outlet state: 1

 695.016957     Auto delay off: -1

 695.016966     Auto delay on: 0

 697.912479     Receive error (PW_COMMAND_START_BYTE): 0!!!

 698.913478     Receive error (PW_COMMAND_START_BYTE): 0!!!

 699.914478     Receive error (PW_COMMAND_START_BYTE): 0!!!

 699.914497     Communications with UPS lost: Error executing command
 699.914503     Short read from UPS
 700.915481     Receive error (PW_COMMAND_START_BYTE): 0!!!

 701.916480     Receive error (PW_COMMAND_START_BYTE): 0!!!

 702.917479     Receive error (PW_COMMAND_START_BYTE): 0!!!

 702.917498     Communications with UPS lost: Error executing command
 702.917503     Short read from UPS
 703.918608     Receive error (PW_COMMAND_START_BYTE): 0!!!

 704.919479     Receive error (PW_COMMAND_START_BYTE): 0!!!

 705.920478     Receive error (PW_COMMAND_START_BYTE): 0!!!

 705.920495     Communications with UPS lost: Error executing command
 705.920500     Short read from UPS
 706.921604     Receive error (PW_COMMAND_START_BYTE): 0!!!

 707.922479     Receive error (PW_COMMAND_START_BYTE): 0!!!

 708.923479     Receive error (PW_COMMAND_START_BYTE): 0!!!

-- 
Chris Boot
[email protected]


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to