On 6/22/2010 10:36 AM, Chris Boot wrote:
I just acquired a new UPS and have been trying to get it to work with NUT. It's 
an Eaton/Powerware 9120 700i with both USB and RS-232 interfaces.

So I moved on to try the serial port instead. Here the UPS also regularly loses 
the connection but at least it doesn't lock the UPS right up - maybe that was a 
fluke. If I restart the driver, the communication is regained for a few minutes 
but then drops again. Below are excerpts from running '/lib/nut/bcmxcp -DDD -a 
pw9120'.
I had a similar problem using bcmxcp with an HP3000 XP unit.

Ultimately what fixed it was adding:

     pollinterval = 5

to the definition for the unit in ups.conf.

A value as low as 3 (compared to the default 2) seemed to be enough to fix the problem, I went to 5 for some extra margin. I think that sometimes the poll cycle takes more than two seconds and the next poll somehow steps on the tail of the previous one. Not sure if this is the same thing you are experiencing, but the symptom is the same.

David