Since I emailed originally, I've swapped out the CP1350AVR for a CP1500AVR,
but here is the information you asked for on the CP1500.  Let me know if
anything else is needed.

Here's the shutdown command:
sudo upsdrvctl -t shutdown
Network UPS Tools - UPS driver controller 2.4.3
*** Testing mode: not calling exec/kill
   0.000000
If you're not a NUT core developer, chances are that you're told to enable
debugging
to see why a driver isn't working for you. We're sorry for the confusion,
but this is
the 'upsdrvctl' wrapper, not the driver you're interested in.

Below you'll find one or more lines starting with 'exec:' followed by an
absolute
path to the driver binary and some command line option. This is what the
driver
starts and you need to copy and paste that line and append the debug flags
to that
line (less the 'exec:' prefix).

   0.000258    Shutdown UPS: cyberpower1500
   0.000271    exec: /lib/nut/usbhid-ups -a cyberpower1500 -k

The forced shutdown upsmon -c fsd worked.

Running upsc cyberpower1...@localhost gives the following:
battery.charge: 100
battery.charge.low: 10
battery.charge.warning: 20
battery.mfr.date: CPS
battery.runtime: 2651
battery.runtime.low: 300
battery.type: PbAcid
battery.voltage: 13.7
battery.voltage.nominal: 12
device.mfr: CPS
device.model:  CP 1500C
device.type: ups
driver.name: usbhid-ups
driver.parameter.pollfreq: 30
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.version: 2.4.3
driver.version.data: CyberPower HID 0.3
driver.version.internal: 0.34
input.transfer.high: 140
input.transfer.low: 90
input.voltage: 122.0
input.voltage.nominal: 120
output.voltage: 122.0
ups.beeper.status: enabled
ups.delay.shutdown: 20
ups.delay.start: 30
ups.load: 13
ups.mfr: CPS
ups.model:  CP 1500C
ups.productid: 0501
ups.realpower.nominal: 388
ups.status: OL
ups.test.result: Done and passed
ups.timer.shutdown: -60
ups.timer.start: 0
ups.vendorid: 0764

On Fri, Nov 19, 2010 at 3:48 PM, Arnaud Quette <[email protected]>wrote:

> Hi Patrick,
>
> 2010/11/15 Patrick O'Malley
>
> I've confirmed that the CyberPower CP1350AVRLCD works with nut using
>> the USB port and the usbhid-ups driver.  It is not on your list.
>> Thanks!
>>
>
> have you checked all variables, and most of all that shutdown works as
> expected?
> ie http://new.networkupstools.org/user-manual.html#Testing_shutdowns
>
> please also send us an upsc output.
> I will wait for these to commit the patch.
>
> thanks for your report,
> Arnaud
> --
> Linux / Unix Expert R&D - Eaton - http://www.eaton.com/mgeops
> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/
> Debian Developer - http://www.debian.org
> Free Software Developer - http://arnaud.quette.free.fr/
>
>


-- 
Patrick O'Malley
Graduate Student
Mechanical Engineering
The Catholic University of America
Washington, DC 20064
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser

Reply via email to