> This is a configurable value, setting the runtime remaining on battery > before the low battery warning is raised. > > It looks like the driver uses the UPS-MIB::upsConfigLowBattTime OID > for this. According to IETF 1628, the units of this value is minutes. > So in order to correctly display this in the units NUT uses (seconds) > we need to multiply by 60 (similar to the > UPS-MIB::upsEstimatedMinutesRemaining that is used for > battery.runtime). > > So I guess what the UPS is trying to tell you, is that the runtime > remaining is before it will report battery low, is 60 seconds. > Depending on your UPS you might be able to change this value though > the 'upsrw' command (see 'man 8 upsrw'). Remember to input this value > in minutes for the time being, until we have fixed this.
rcs-manage-1:/var/log # upsrw phys-eaton [battery.runtime.low] Remaining battery runtime when UPS switches to LB (seconds) Type: UNKNOWN (unrecognized) I suspect from this that it may not be configurable. Thoughts ? Cheers Stuart _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/mailman/listinfo/nut-upsuser