On Jun 17, 2011, at 5:57 PM, [email protected] wrote:

On 06/17/2011 12:31 AM, Arnaud Quette wrote:
2011/6/16 Charles Lepple <[email protected]>

On Jun 15, 2011, at 5:40 PM, [email protected] wrote:
(...)
Is it consistently disconnecting every 20 seconds? That almost sounds like
some proprietary extension to the HID protocol - the UPS expects the
computer to send something that only the CyberPower software knows to send.


in this case, doing an usbsnoop run is the way to go:
http://lists.alioth.debian.org/pipermail/nut-upsdev/2010-February/004528.html

It seems the usbhid-ups driver already knows how to make the UPS happy. Once the driver has successfully connected to the UPS, the disconnect/ reconnect cycle
stops and the UPS stays connected and communicating from then on.

It only misses connecting if the device is given enough time to disconnect
(presumably because it timed out after 20sec).

By the way, this is fairly broken behavior on the part of the UPS firmware. There are standards-compliant ways for a USB device to suspend after inactivity while still remaining connected to the bus.

I don't know if this UPS has upgradeable firmware, but if it were mine, I'd let the manufacturer know.

Unless the administrator can guarantee to _always_ connect to the device within 20sec of boot, the usbhid-ups needs to delay a second or two and then retry, 2 or 3 times, before giving up on finding the CyberPower subdriver based UPS.

What if you add the loop in the script that starts the driver (through upsdrvctl)? That might be easier to prototype.

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to