G'day!

On 30 Jul 2011 at 22:54, Arnaud Quette wrote:

> 
> And once again want to emphasize - UPS does not go to state 'data stale'
> (loss of communication) after switching to battery since we can
> immediately
> read its status, for example, with the command 'upsc'.
> 
> but since upsmon launches the system shutdown, there is something 
> triggering it!

Yes, and I'm very interested learn what it is :-)

> 
> fake_lowbatt doesn't exist in usbhid-ups. 

My mistake again - I found fake_lowbatt in another driver.

> you're probably facing a data mapping mismatch.

Very similar to that...

> 
> the best would be to monitor this a bit more closely.
> prefer to remove your PC from the UPS for those tests!
> set SHUTDOWNCMD to empty or something not hurting (gedit)

Changed SHUTDOWNCMD "date >> /var/log/nutlog"

> and restart 
> upsmon and the driver in debug mode (ie "usbhid-ups -DDD -a ..."), in 
> separate consoles.
> 
> then test a power failure, and send us back the results, along with your
> configuration (passwd trimmed!)

Here is debug results (long) for "usbhid-ups -DDD -a xen-home -u ups" while 
power failure:

===
[root@xen-home bin]# ./usbhid-ups -a xen-home -u ups -DDD
Network UPS Tools - Generic HID driver 0.35 (2.6.1)
USB communication driver 0.31
   0.000000     debug level is '3'
   0.000708     upsdrv_initups...
   0.001344     Checking device (1D6B/0002) (001/001)
   0.001401     - VendorID: 1d6b
   0.001411     - ProductID: 0002
   0.001421     - Manufacturer: Linux 2.6.32.12-
0.7.1.xs5.6.100.323.170596xen ehci_hcd
   0.001431     - Product: EHCI Host Controller
   0.001440     - Serial Number: 0000:00:12.2
   0.001448     - Bus: 001
   0.001457     Trying to match device
   0.001482     Device does not match - skipping
   0.001497     Checking device (1D6B/0001) (006/001)
   0.001534     - VendorID: 1d6b
   0.001544     - ProductID: 0001
   0.001553     - Manufacturer: Linux 2.6.32.12-
0.7.1.xs5.6.100.323.170596xen ohci_hcd
   0.001562     - Product: OHCI Host Controller
   0.001571     - Serial Number: 0000:00:16.0
   0.001580     - Bus: 006
   0.001588     Trying to match device
   0.001599     Device does not match - skipping
   0.001610     Checking device (1D6B/0002) (002/001)
   0.001644     - VendorID: 1d6b
   0.001654     - ProductID: 0002
   0.001663     - Manufacturer: Linux 2.6.32.12-
0.7.1.xs5.6.100.323.170596xen ehci_hcd
   0.001672     - Product: EHCI Host Controller
   0.001681     - Serial Number: 0000:00:13.2
   0.001689     - Bus: 002
   0.001697     Trying to match device
   0.001707     Device does not match - skipping
   0.001719     Checking device (0D9F/00A4) (005/002)
   0.015623     - VendorID: 0d9f
   0.015661     - ProductID: 00a4
   0.015671     - Manufacturer: POWERCOM Co.,LTD
   0.015681     - Product:   UPS  WOW--500U FW3.A4
   0.015691     - Serial Number: 3A4-0000-0001
   0.015700     - Bus: 005
   0.015709     Trying to match device
   0.015726     Device matches
   0.019628     HID descriptor, method 1: (9 bytes) => 09 21 00 01 00 01 22 
eb 02
   0.019667     HID descriptor, method 2: (9 bytes) => 09 21 00 01 00 01 22 
eb 02
   0.019677     HID descriptor length 747
   0.044650     Report Descriptor size = 747
   0.044704     Report Descriptor: (747 bytes) => 05 84 09 04 a1 01 09 24 
a1 02 85 01 09 fe
   0.044726      79 01 75 08 95 01 15 00 26 ff 00 b1 22 85 02 09 ff 79 02 
b1 22 85 03 09 fd
   0.044747      79 03 b1 22 05 85 85 04 09 8f 79 03 b1 22 85 05 09 89 79 
04 b1 22 85 07 09
   0.044767      8b b1 22 85 08 09 2c 25 03 b1 22 85 09 09 83 25 64 b1 22 
09 67 b1 22 85 0a
   0.044787      09 66 81 22 09 66 b1 a2 85 0b 09 8c b1 22 85 0c 09 29 b1 
a2 85 0d 09 85 75
   0.044807      10 27 ff ff 00 00 b1 a2 85 0e 09 68 81 22 09 68 b1 a2 05 
ff 85 0f 09 57 75
   0.044827      10 16 00 00 27 ff ff 00 00 b1 a2 85 10 09 56 75 10 16 00 
00 27 ff ff 00 00
   0.044847      b1 a2 05 84 85 11 09 40 75 10 15 64 26 e6 00 b1 22 85 12 
09 30 75 10 16 00
   0.044867      00 26 2c 01 b1 a2 85 13 09 5a 75 08 15 01 25 03 b1 a2 09 
02 a1 02 05 85 85
   0.044888      14 09 44 75 01 15 00 25 01 81 a2 09 44 b1 a2 09 45 81 a2 
09 45 b1 a2 09 d0
   0.044907      81 a2 09 d0 b1 a2 09 d1 81 a2 09 d1 b1 a2 09 42 81 a2 09 
42 b1 a2 09 43 81
   0.044927      a2 09 43 b1 a2 09 4b 81 a2 09 4b b1 a2 09 db 81 a2 09 db 
b1 a2 05 84 09 68
   0.044947      81 a2 09 68 b1 a2 09 69 81 a2 09 69 b1 a2 09 73 81 a2 09 
73 b1 a2 09 65 81
   0.044967      a2 09 65 b1 a2 95 03 81 01 b1 01 95 01 06 86 ff 09 80 81 
a2 09 80 b1 a2 c0
   0.044988      c0 05 84 09 12 a1 00 85 15 09 58 75 08 25 06 b1 a2 85 16 
09 70 25 06 b1 a2
   0.045008      05 85 85 17 09 85 75 10 27 ff ff 00 00 b1 a2 85 18 09 66 
75 08 15 00 25 64
   0.045027      b1 a2 05 84 85 19 09 40 75 10 15 64 26 e6 00 b1 22 85 1a 
09 30 75 10 16 00
   0.045048      00 26 2c 01 b1 a2 05 ff 85 1b 09 56 75 10 16 00 00 27 ff 
ff 00 00 b1 a2 c0
   0.045067      05 84 09 1a a1 00 85 1c 09 40 75 10 15 64 26 e6 00 b1 22 
85 1d 09 30 75 10
   0.045087      16 00 00 26 2c 01 b1 a2 85 1e 09 32 75 08 15 00 25 46 b1 
a2 c0 05 84 09 1c
   0.045107      a1 00 85 1f 09 35 75 08 15 00 25 64 b1 a2 85 20 09 40 75 
10 15 64 26 e6 00
   0.045127      b1 22 85 21 09 30 75 10 16 00 00 26 2c 01 b1 a2 85 22 09 
32 75 08 15 00 25
   0.045148      46 b1 a2 05 ff 85 23 09 57 75 10 16 00 00 27 ff ff 00 00 
b1 a2 85 24 09 56
   0.045168      75 10 16 00 00 27 ff ff 00 00 b1 a2 c0 05 84 09 16 a1 00 
85 2a 09 30 75 10
   0.045189      16 00 00 26 90 01 b1 a2 c0 05 84 85 06 09 01 79 05 b1 a2 
85 25 09 5a 75 08
   0.045209      15 01 25 03 b1 a2 09 02 a1 02 05 85 85 26 09 44 75 01 15 
00 25 01 b1 a2 09
   0.045229      45 b1 a2 09 d0 b1 a2 09 d1 b1 a2 09 42 b1 a2 09 43 b1 a2 
09 4b b1 a2 09 db
   0.045336      b1 a2 05 84 09 68 b1 a2 09 69 b1 a2 09 73 b1 a2 09 65 b1 
a2 09 6e b1 a2 09
   0.045392      6f b1 a2 09 71 b1 a2 06 86 ff 09 80 b1 a2 c0 85 27 05 84 
09 69 75 08 15 00
   0.045415      25 01 b1 a2 85 28 09 2f 75 08 95 07 15 00 26 ff 00 b1 a2 
06 86 ff 85 29 09
   0.045429      60 81 a2 09 60 b1 a2 c0
   0.045621     Using subdriver: PowerCOM HID 0.2
   0.046610     Report[get]: (2 bytes) => 01 01
   0.046650     Path: UPS.PowerSummary.iProduct, Type: Feature, ReportID: 
0x01, Offset: 0, Size: 8, Value: 1
   0.048644     Report[get]: (2 bytes) => 02 02
   0.048687     Path: UPS.PowerSummary.iSerialNumber, Type: Feature, 
ReportID: 0x02, Offset: 0, Size: 8, Value: 2
   0.050632     Report[get]: (2 bytes) => 03 03
   0.050668     Path: UPS.PowerSummary.iManufacturer, Type: Feature, 
ReportID: 0x03, Offset: 0, Size: 8, Value: 3
   0.052610     Report[get]: (2 bytes) => 04 03
   0.052653     Path: UPS.PowerSummary.iOEMInformation, Type: Feature, 
ReportID: 0x04, Offset: 0, Size: 8, Value: 3
   0.054628     Report[get]: (2 bytes) => 05 04
   0.054665     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x05, Offset: 0, Size: 8, Value: 4
   0.056629     Report[get]: (2 bytes) => 07 01
   0.056666     Path: UPS.PowerSummary.Rechargeable, Type: Feature, 
ReportID: 0x07, Offset: 0, Size: 8, Value: 1
   0.058620     Report[get]: (2 bytes) => 08 02
   0.058657     Path: UPS.PowerSummary.CapacityMode, Type: Feature, 
ReportID: 0x08, Offset: 0, Size: 8, Value: 2
   0.060634     Report[get]: (3 bytes) => 09 64 64
   0.060685     Path: UPS.PowerSummary.DesignCapacity, Type: Feature, 
ReportID: 0x09, Offset: 0, Size: 8, Value: 100
   0.060700     Report[buf]: (3 bytes) => 09 64 64
   0.060716     Path: UPS.PowerSummary.FullChargeCapacity, Type: Feature, 
ReportID: 0x09, Offset: 8, Size: 8, Value: 100
   0.062637     Report[get]: (2 bytes) => 0a 64
   0.062695     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
   0.062709     Report[buf]: (2 bytes) => 0a 64
   0.062724     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
   0.064629     Report[get]: (2 bytes) => 0b 1e
   0.064668     Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, 
ReportID: 0x0b, Offset: 0, Size: 8, Value: 30
   0.066621     Report[get]: (2 bytes) => 0c 0a
   0.066660     Path: UPS.PowerSummary.RemainingCapacityLimit, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 10
   0.068622     Report[get]: (3 bytes) => 0d 21 3c
   0.068663     Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, 
ReportID: 0x0d, Offset: 0, Size: 16, Value: 15393
   0.070595     Report[get]: (3 bytes) => 0e 00 09
   0.070642     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 2304
   0.070656     Report[buf]: (3 bytes) => 0e 00 09
   0.070671     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 2304
   0.072662     Report[get]: (3 bytes) => 0f 00 00
   0.072704     Path: UPS.PowerSummary.[87], Type: Feature, ReportID: 0x0f, 
Offset: 0, Size: 16, Value: 0
   0.074621     Report[get]: (3 bytes) => 10 00 00
   0.074658     Path: UPS.PowerSummary.[86], Type: Feature, ReportID: 0x10, 
Offset: 0, Size: 16, Value: 0
   0.076621     Report[get]: (3 bytes) => 11 dc 00
   0.076677     Path: UPS.PowerSummary.ConfigVoltage, Type: Feature, 
ReportID: 0x11, Offset: 0, Size: 16, Value: 220
   0.078617     Report[get]: (3 bytes) => 12 dc 00
   0.078661     Path: UPS.PowerSummary.Voltage, Type: Feature, ReportID: 
0x12, Offset: 0, Size: 16, Value: 220
   0.080627     Report[get]: (2 bytes) => 13 01
   0.080670     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.082622     Report[get]: (3 bytes) => 14 0c 00
   0.082661     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
   0.082674     Report[buf]: (3 bytes) => 14 0c 00
   0.082689     Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x14, Offset: 0, Size: 1, Value: 0
   0.082702     Report[buf]: (3 bytes) => 14 0c 00
   0.082717     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
   0.082729     Report[buf]: (3 bytes) => 14 0c 00
   0.082743     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
   0.082756     Report[buf]: (3 bytes) => 14 0c 00
   0.082771     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
   0.082784     Report[buf]: (3 bytes) => 14 0c 00
   0.082798     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
   0.082811     Report[buf]: (3 bytes) => 14 0c 00
   0.082825     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
   0.082838     Report[buf]: (3 bytes) => 14 0c 00
   0.082852     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Feature, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
   0.082865     Report[buf]: (3 bytes) => 14 0c 00
   0.082879     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
   0.082892     Report[buf]: (3 bytes) => 14 0c 00
   0.082906     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
   0.082919     Report[buf]: (3 bytes) => 14 0c 00
   0.082933     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
   0.082946     Report[buf]: (3 bytes) => 14 0c 00
   0.082960     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
   0.082973     Report[buf]: (3 bytes) => 14 0c 00
   0.082987     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
   0.083000     Report[buf]: (3 bytes) => 14 0c 00
   0.083013     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
   0.083026     Report[buf]: (3 bytes) => 14 0c 00
   0.083041     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
   0.083054     Report[buf]: (3 bytes) => 14 0c 00
   0.083068     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Feature, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
   0.083081     Report[buf]: (3 bytes) => 14 0c 00
   0.083095     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
   0.083108     Report[buf]: (3 bytes) => 14 0c 00
   0.083121     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Feature, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
   0.083134     Report[buf]: (3 bytes) => 14 0c 00
   0.083148     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
   0.083161     Report[buf]: (3 bytes) => 14 0c 00
   0.083174     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Feature, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
   0.083187     Report[buf]: (3 bytes) => 14 0c 00
   0.083201     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
   0.083214     Report[buf]: (3 bytes) => 14 0c 00
   0.083227     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Feature, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
   0.083240     Report[buf]: (3 bytes) => 14 0c 00
   0.083254     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
   0.083267     Report[buf]: (3 bytes) => 14 0c 00
   0.083280     Path: UPS.PowerSummary.PresentStatus.Overload, Type: 
Feature, ReportID: 0x14, Offset: 11, Size: 1, Value: 0
   0.083293     Report[buf]: (3 bytes) => 14 0c 00
   0.083307     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
   0.083319     Report[buf]: (3 bytes) => 14 0c 00
   0.083333     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Feature, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
   0.084621     Report[get]: (2 bytes) => 15 01
   0.084658     Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, 
Offset: 0, Size: 8, Value: 1
   0.086621     Report[get]: (2 bytes) => 16 01
   0.086658     Path: UPS.Battery.Initialized, Type: Feature, ReportID: 
0x16, Offset: 0, Size: 8, Value: 1
   0.088621     Report[get]: (3 bytes) => 17 21 3c
   0.088662     Path: UPS.Battery.ManufacturerDate, Type: Feature, 
ReportID: 0x17, Offset: 0, Size: 16, Value: 15393
   0.090986     Report[get]: (2 bytes) => 18 64
   0.091023     Path: UPS.Battery.RemainingCapacity, Type: Feature, 
ReportID: 0x18, Offset: 0, Size: 8, Value: 100
   0.092590     Report[get]: (3 bytes) => 19 dc 00
   0.092630     Path: UPS.Battery.ConfigVoltage, Type: Feature, ReportID: 
0x19, Offset: 0, Size: 16, Value: 220
   0.094622     Report[get]: (3 bytes) => 1a dc 00
   0.094661     Path: UPS.Battery.Voltage, Type: Feature, ReportID: 0x1a, 
Offset: 0, Size: 16, Value: 220
   0.096622     Report[get]: (3 bytes) => 1b 00 00
   0.096660     Path: UPS.Battery.[86], Type: Feature, ReportID: 0x1b, 
Offset: 0, Size: 16, Value: 0
   0.098622     Report[get]: (3 bytes) => 1c dc 00
   0.098662     Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 
0x1c, Offset: 0, Size: 16, Value: 220
   0.100570     Report[get]: (3 bytes) => 1d dc 00
   0.100616     Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, 
Offset: 0, Size: 16, Value: 220
   0.102639     Report[get]: (2 bytes) => 1e 32
   0.102686     Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
Offset: 0, Size: 8, Value: 50
   0.104621     Report[get]: (2 bytes) => 1f 14
   0.104660     Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 
0x1f, Offset: 0, Size: 8, Value: 20
   0.106620     Report[get]: (3 bytes) => 20 dc 00
   0.106661     Path: UPS.Output.ConfigVoltage, Type: Feature, ReportID: 
0x20, Offset: 0, Size: 16, Value: 220
   0.108617     Report[get]: (3 bytes) => 21 dc 00
   0.108661     Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, 
Offset: 0, Size: 16, Value: 220
   0.110607     Report[get]: (2 bytes) => 22 32
   0.110652     Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, 
Offset: 0, Size: 8, Value: 50
   0.112623     Report[get]: (3 bytes) => 23 00 00
   0.112661     Path: UPS.Output.[87], Type: Feature, ReportID: 0x23, 
Offset: 0, Size: 16, Value: 0
   0.114622     Report[get]: (3 bytes) => 24 00 00
   0.114659     Path: UPS.Output.[86], Type: Feature, ReportID: 0x24, 
Offset: 0, Size: 16, Value: 0
   0.116622     Report[get]: (3 bytes) => 2a 5a 01
   0.116661     Path: UPS.PowerConverter.Voltage, Type: Feature, ReportID: 
0x2a, Offset: 0, Size: 16, Value: 346
   0.118617     refresh_report_buffer: expected 3 bytes, but got 2 instead
   0.118651     Report[err]: (2 bytes) => 06 05
   0.118668     Path: UPS.iName, Type: Feature, ReportID: 0x06, Offset: 0, 
Size: 16, Value: 5
   0.120595     Report[get]: (2 bytes) => 25 01
   0.120637     Path: UPS.AudibleAlarmControl, Type: Feature, ReportID: 
0x25, Offset: 0, Size: 8, Value: 1
   0.122615     Report[get]: (3 bytes) => 26 0c 00
   0.122652     Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 
0x26, Offset: 0, Size: 1, Value: 0
   0.122665     Report[buf]: (3 bytes) => 26 0c 00
   0.122679     Path: UPS.PresentStatus.Discharging, Type: Feature, 
ReportID: 0x26, Offset: 1, Size: 1, Value: 0
   0.122692     Report[buf]: (3 bytes) => 26 0c 00
   0.122706     Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 
0x26, Offset: 2, Size: 1, Value: 1
   0.122718     Report[buf]: (3 bytes) => 26 0c 00
   0.122732     Path: UPS.PresentStatus.BatteryPresent, Type: Feature, 
ReportID: 0x26, Offset: 3, Size: 1, Value: 1
   0.122745     Report[buf]: (3 bytes) => 26 0c 00
   0.122758     Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
   0.122771     Report[buf]: (3 bytes) => 26 0c 00
   0.122784     Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: 
Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
   0.122796     Report[buf]: (3 bytes) => 26 0c 00
   0.122810     Path: UPS.PresentStatus.NeedReplacement, Type: Feature, 
ReportID: 0x26, Offset: 6, Size: 1, Value: 0
   0.122822     Report[buf]: (3 bytes) => 26 0c 00
   0.122836     Path: UPS.PresentStatus.VoltageNotRegulated, Type: Feature, 
ReportID: 0x26, Offset: 7, Size: 1, Value: 0
   0.122849     Report[buf]: (3 bytes) => 26 0c 00
   0.122862     Path: UPS.PresentStatus.ShutdownRequested, Type: Feature, 
ReportID: 0x26, Offset: 8, Size: 1, Value: 0
   0.122874     Report[buf]: (3 bytes) => 26 0c 00
   0.122887     Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, 
ReportID: 0x26, Offset: 9, Size: 1, Value: 0
   0.122900     Report[buf]: (3 bytes) => 26 0c 00
   0.122913     Path: UPS.PresentStatus.CommunicationLost, Type: Feature, 
ReportID: 0x26, Offset: 10, Size: 1, Value: 0
   0.122926     Report[buf]: (3 bytes) => 26 0c 00
   0.122939     Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 
0x26, Offset: 11, Size: 1, Value: 0
   0.122951     Report[buf]: (3 bytes) => 26 0c 00
   0.122964     Path: UPS.PresentStatus.Boost, Type: Feature, ReportID: 
0x26, Offset: 12, Size: 1, Value: 0
   0.122976     Report[buf]: (3 bytes) => 26 0c 00
   0.122989     Path: UPS.PresentStatus.Buck, Type: Feature, ReportID: 
0x26, Offset: 13, Size: 1, Value: 0
   0.123002     Report[buf]: (3 bytes) => 26 0c 00
   0.123014     Path: UPS.PresentStatus.Tested, Type: Feature, ReportID: 
0x26, Offset: 14, Size: 1, Value: 0
   0.123027     Report[buf]: (3 bytes) => 26 0c 00
   0.123039     Path: UPS.PresentStatus.POWERCOM3, Type: Feature, ReportID: 
0x26, Offset: 15, Size: 1, Value: 0
   0.124638     Report[get]: (2 bytes) => 27 00
   0.124682     Path: UPS.ShutdownImminent, Type: Feature, ReportID: 0x27, 
Offset: 0, Size: 8, Value: 0
   0.126628     Report[get]: (8 bytes) => 28 de 11 14 64 6e 6e 32
   0.126668     Path: UPS.POWERCOM1, Type: Feature, ReportID: 0x28, Offset: 
0, Size: 8, Value: 222
   0.128661     Can't retrieve Report 29: Broken pipe
   0.128696     Path: UPS.POWERCOM2, Type: Input, ReportID: 0x29, Offset: 
0, Size: 8
   0.130601     Can't retrieve Report 29: Broken pipe
   0.130648     Path: UPS.POWERCOM2, Type: Feature, ReportID: 0x29, Offset: 
0, Size: 8
   0.130687     Report descriptor retrieved (Reportlen = 747)
   0.130697     Found HID device
   0.130708     Detected a UPS: POWERCOM Co.,LTD /  UPS  WOW--500U FW3.A4
   0.130759     Report[buf]: (3 bytes) => 14 0c 00
   0.130773     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
   0.130800     Report[buf]: (3 bytes) => 14 0c 00
   0.130811     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Feature, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
   0.130835     Report[buf]: (3 bytes) => 14 0c 00
   0.130847     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
   0.130870     Report[buf]: (3 bytes) => 14 0c 00
   0.130881     Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x14, Offset: 0, Size: 1, Value: 0
   0.130946     Report[buf]: (3 bytes) => 14 0c 00
   0.130958     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Feature, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
   0.130980     Report[buf]: (3 bytes) => 14 0c 00
   0.130992     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
   0.131014     Report[buf]: (3 bytes) => 14 0c 00
   0.131025     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
   0.131045     Report[buf]: (3 bytes) => 14 0c 00
   0.131056     Path: UPS.PowerSummary.PresentStatus.Overload, Type: 
Feature, ReportID: 0x14, Offset: 11, Size: 1, Value: 0
   0.131079     Report[buf]: (3 bytes) => 14 0c 00
   0.131090     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
   0.131111     Report[buf]: (3 bytes) => 14 0c 00
   0.131122     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Feature, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
   0.131145     Report[buf]: (3 bytes) => 26 0c 00
   0.131156     Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 
0x26, Offset: 2, Size: 1, Value: 1
   0.131178     Report[buf]: (3 bytes) => 26 0c 00
   0.131189     Path: UPS.PresentStatus.BatteryPresent, Type: Feature, 
ReportID: 0x26, Offset: 3, Size: 1, Value: 1
   0.131211     Report[buf]: (3 bytes) => 26 0c 00
   0.131222     Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
   0.131242     Report[buf]: (3 bytes) => 26 0c 00
   0.131253     Path: UPS.PresentStatus.Boost, Type: Feature, ReportID: 
0x26, Offset: 12, Size: 1, Value: 0
   0.131272     Report[buf]: (3 bytes) => 26 0c 00
   0.131283     Path: UPS.PresentStatus.Buck, Type: Feature, ReportID: 
0x26, Offset: 13, Size: 1, Value: 0
   0.131304     Report[buf]: (3 bytes) => 26 0c 00
   0.131316     Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 
0x26, Offset: 0, Size: 1, Value: 0
   0.131335     Report[buf]: (3 bytes) => 26 0c 00
   0.131346     Path: UPS.PresentStatus.CommunicationLost, Type: Feature, 
ReportID: 0x26, Offset: 10, Size: 1, Value: 0
   0.131367     Report[buf]: (3 bytes) => 26 0c 00
   0.131378     Path: UPS.PresentStatus.Discharging, Type: Feature, 
ReportID: 0x26, Offset: 1, Size: 1, Value: 0
   0.131399     Report[buf]: (3 bytes) => 26 0c 00
   0.131410     Path: UPS.PresentStatus.NeedReplacement, Type: Feature, 
ReportID: 0x26, Offset: 6, Size: 1, Value: 0
   0.131429     Report[buf]: (3 bytes) => 26 0c 00
   0.131440     Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 
0x26, Offset: 11, Size: 1, Value: 0
   0.131462     Report[buf]: (3 bytes) => 26 0c 00
   0.131473     Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: 
Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
   0.131492     Report[buf]: (3 bytes) => 26 0c 00
   0.131503     Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, 
ReportID: 0x26, Offset: 9, Size: 1, Value: 0
   0.131548     Report[buf]: (2 bytes) => 0a 64
   0.131563     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
   0.131597     Report[buf]: (2 bytes) => 0c 0a
   0.131609     Path: UPS.PowerSummary.RemainingCapacityLimit, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 10
   0.131635     Report[buf]: (2 bytes) => 0b 1e
   0.131647     Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, 
ReportID: 0x0b, Offset: 0, Size: 8, Value: 30
   0.131681     Report[buf]: (3 bytes) => 0e 00 09
   0.131694     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 2304
   0.131722     Report[buf]: (3 bytes) => 17 21 3c
   0.131734     Path: UPS.Battery.ManufacturerDate, Type: Feature, 
ReportID: 0x17, Offset: 0, Size: 16, Value: 15393
   0.131763     Report[buf]: (2 bytes) => 05 04
   0.131774     Path: UPS.PowerSummary.iDeviceChemistry, Type: Feature, 
ReportID: 0x05, Offset: 0, Size: 8, Value: 4
   0.134646     Report[buf]: (2 bytes) => 13 01
   0.134679     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.134711     Report[buf]: (2 bytes) => 1f 14
   0.134725     Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 
0x1f, Offset: 0, Size: 8, Value: 20
   0.134752     Report[buf]: (3 bytes) => 0d 21 3c
   0.134765     Path: UPS.PowerSummary.ManufacturerDate, Type: Feature, 
ReportID: 0x0d, Offset: 0, Size: 16, Value: 15393
   0.134788     Report[buf]: (2 bytes) => 15 01
   0.134800     Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, 
Offset: 0, Size: 8, Value: 1
   0.134854     Report[buf]: (3 bytes) => 1d dc 00
   0.134866     Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, 
Offset: 0, Size: 16, Value: 220
   0.134889     Report[buf]: (3 bytes) => 1c dc 00
   0.134901     Path: UPS.Input.ConfigVoltage, Type: Feature, ReportID: 
0x1c, Offset: 0, Size: 16, Value: 220
   0.134923     Report[buf]: (2 bytes) => 1e 32
   0.134934     Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
Offset: 0, Size: 8, Value: 50
   0.140352     Report[buf]: (3 bytes) => 21 dc 00
   0.140374     Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, 
Offset: 0, Size: 16, Value: 220
   0.140400     Report[buf]: (3 bytes) => 20 dc 00
   0.140413     Path: UPS.Output.ConfigVoltage, Type: Feature, ReportID: 
0x20, Offset: 0, Size: 16, Value: 220
   0.140437     Report[buf]: (2 bytes) => 22 32
   0.140449     Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, 
Offset: 0, Size: 8, Value: 50
   0.140473     Report[buf]: (2 bytes) => 13 01
   0.140485     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x13, Offset: 0, Size: 8, Value: 1
   0.140504     Report[buf]: (2 bytes) => 15 01
   0.140515     Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, 
Offset: 0, Size: 8, Value: 1
   0.140555     find_nut_info: unknown info type: load.off.delay
   0.140566     find_nut_info: unknown info type: load.on.delay
   0.140578     find_nut_info: unknown info type: load.off.delay
   0.140600     upsdrv_initinfo...
   0.140624     upsdrv_updateinfo...
   0.160296     Report[int]: (3 bytes) => 14 0c 00
   0.160330     Got 13 HID objects...
   0.160343     Report[buf]: (3 bytes) => 14 0c 00
   0.160361     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
   0.160376     Report[buf]: (3 bytes) => 14 0c 00
   0.160392     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
   0.160405     Report[buf]: (3 bytes) => 14 0c 00
   0.160420     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
   0.160434     Report[buf]: (3 bytes) => 14 0c 00
   0.160448     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
   0.160462     Report[buf]: (3 bytes) => 14 0c 00
   0.160476     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
   0.160490     Report[buf]: (3 bytes) => 14 0c 00
   0.160504     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
   0.160519     Report[buf]: (3 bytes) => 14 0c 00
   0.160533     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
   0.160547     Report[buf]: (3 bytes) => 14 0c 00
   0.160561     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
   0.160573     NUT doesn't use this HID object
   0.160584     Report[buf]: (3 bytes) => 14 0c 00
   0.160597     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
   0.160609     NUT doesn't use this HID object
   0.160620     Report[buf]: (3 bytes) => 14 0c 00
   0.160633     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
   0.160647     Report[buf]: (3 bytes) => 14 0c 00
   0.160661     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
   0.160676     Report[buf]: (3 bytes) => 14 0c 00
   0.160689     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
   0.160703     Report[buf]: (3 bytes) => 14 0c 00
   0.160717     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
   0.160728     NUT doesn't use this HID object
   0.160739     Quick update...
   0.160885     dstate_init: sock /var/state/ups/usbhid-ups-xen-home open 
on fd 5
   0.160915     upsdrv_updateinfo...
   0.190182     Report[int]: (2 bytes) => 0a 64
   0.190218     Got 1 HID objects...
   0.190231     Report[buf]: (2 bytes) => 0a 64
   0.190251     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
   0.190269     Quick update...
   2.170222     upsdrv_updateinfo...
   2.171520     Report[int]: (3 bytes) => 0e 00 09
   2.171554     Got 1 HID objects...
   2.171568     Report[buf]: (3 bytes) => 0e 00 09
   2.171589     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 2304
   2.171607     Quick update...
   4.179988     upsdrv_updateinfo...
   4.187460     Report[int]: (2 bytes) => 15 01
   4.187494     HIDGetEvents: unexpected input report (ignored)
   4.187505     Got 0 HID objects...
   4.187518     Quick update...
   5.341103     new connection on fd 6
   6.189965     upsdrv_updateinfo...
   6.209950     Report[int]: (3 bytes) => 14 0c 00
   6.209988     Got 13 HID objects...
   6.210003     Report[buf]: (3 bytes) => 14 0c 00
   6.210022     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
   6.210039     Report[buf]: (3 bytes) => 14 0c 00
   6.210055     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
   6.210069     Report[buf]: (3 bytes) => 14 0c 00
   6.210084     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
   6.210097     Report[buf]: (3 bytes) => 14 0c 00
   6.210112     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
   6.210126     Report[buf]: (3 bytes) => 14 0c 00
   6.210140     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
   6.210154     Report[buf]: (3 bytes) => 14 0c 00
   6.210168     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
   6.210183     Report[buf]: (3 bytes) => 14 0c 00
   6.210197     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
   6.210211     Report[buf]: (3 bytes) => 14 0c 00
   6.210225     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
   6.210237     NUT doesn't use this HID object
   6.210248     Report[buf]: (3 bytes) => 14 0c 00
   6.210261     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
   6.210273     NUT doesn't use this HID object
   6.210284     Report[buf]: (3 bytes) => 14 0c 00
   6.210297     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
   6.210311     Report[buf]: (3 bytes) => 14 0c 00
   6.210325     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
   6.210340     Report[buf]: (3 bytes) => 14 0c 00
   6.210353     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
   6.210367     Report[buf]: (3 bytes) => 14 0c 00
   6.210381     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
   6.210392     NUT doesn't use this HID object
   6.210403     Quick update...
   8.198031     upsdrv_updateinfo...
   8.219839     Report[int]: (2 bytes) => 0a 64
   8.219877     Got 1 HID objects...
   8.219890     Report[buf]: (2 bytes) => 0a 64
   8.219910     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
   8.219927     Quick update...
  10.209722     upsdrv_updateinfo...
  10.239735     Report[int]: (3 bytes) => 0e 00 09
  10.239773     Got 1 HID objects...
  10.239787     Report[buf]: (3 bytes) => 0e 00 09
  10.239807     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 2304
  10.239826     Quick update...
  12.219667     upsdrv_updateinfo...
  12.259635     Report[int]: (2 bytes) => 15 01
  12.259677     HIDGetEvents: unexpected input report (ignored)
  12.259689     Got 0 HID objects...
  12.259703     Quick update...
  14.229601     upsdrv_updateinfo...
  14.235029     Report[int]: (3 bytes) => 14 0c 00
  14.235066     Got 13 HID objects...
  14.235081     Report[buf]: (3 bytes) => 14 0c 00
  14.235101     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
  14.235119     Report[buf]: (3 bytes) => 14 0c 00
  14.235136     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
  14.235151     Report[buf]: (3 bytes) => 14 0c 00
  14.235166     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
  14.235181     Report[buf]: (3 bytes) => 14 0c 00
  14.235196     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
  14.235212     Report[buf]: (3 bytes) => 14 0c 00
  14.235227     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
  14.235242     Report[buf]: (3 bytes) => 14 0c 00
  14.235257     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
  14.235273     Report[buf]: (3 bytes) => 14 0c 00
  14.235287     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
  14.235302     Report[buf]: (3 bytes) => 14 0c 00
  14.235317     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
  14.235330     NUT doesn't use this HID object
  14.235342     Report[buf]: (3 bytes) => 14 0c 00
  14.235356     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
  14.235369     NUT doesn't use this HID object
  14.235381     Report[buf]: (3 bytes) => 14 0c 00
  14.235395     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
  14.235410     Report[buf]: (3 bytes) => 14 0c 00
  14.235425     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
  14.235441     Report[buf]: (3 bytes) => 14 0c 00
  14.235455     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
  14.235470     Report[buf]: (3 bytes) => 14 0c 00
  14.235485     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
  14.235497     NUT doesn't use this HID object
  14.235509     Quick update...
  16.239486     upsdrv_updateinfo...
  16.259516     Report[int]: (2 bytes) => 0a 64
  16.259554     Got 1 HID objects...
  16.259568     Report[buf]: (2 bytes) => 0a 64
  16.259588     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 100
  16.259606     Quick update...
  18.249379     upsdrv_updateinfo...
  18.269384     Report[int]: (3 bytes) => 0e 80 04
  18.269423     Got 1 HID objects...
  18.269438     Report[buf]: (3 bytes) => 0e 80 04
  18.269458     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 1152
  18.269495     Quick update...
  20.259261     upsdrv_updateinfo...
  20.289329     Report[int]: (2 bytes) => 15 01
  20.289367     HIDGetEvents: unexpected input report (ignored)
  20.289378     Got 0 HID objects...
  20.289391     Quick update...
  22.269187     upsdrv_updateinfo...
  22.299209     Report[int]: (3 bytes) => 14 0a 00
  22.299250     Got 13 HID objects...
  22.299264     Report[buf]: (3 bytes) => 14 0a 00
  22.299284     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
  22.299301     Report[buf]: (3 bytes) => 14 0a 00
  22.299318     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 1
  22.299333     Report[buf]: (3 bytes) => 14 0a 00
  22.299348     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 0
  22.299363     Report[buf]: (3 bytes) => 14 0a 00
  22.299378     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
  22.299393     Report[buf]: (3 bytes) => 14 0a 00
  22.299408     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
  22.299422     Report[buf]: (3 bytes) => 14 0a 00
  22.299437     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
  22.299452     Report[buf]: (3 bytes) => 14 0a 00
  22.299466     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
  22.299480     Report[buf]: (3 bytes) => 14 0a 00
  22.299495     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
  22.299511     NUT doesn't use this HID object
  22.299523     Report[buf]: (3 bytes) => 14 0a 00
  22.299538     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
  22.299550     NUT doesn't use this HID object
  22.299562     Report[buf]: (3 bytes) => 14 0a 00
  22.299575     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
  22.299590     Report[buf]: (3 bytes) => 14 0a 00
  22.299605     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
  22.299620     Report[buf]: (3 bytes) => 14 0a 00
  22.299634     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
  22.299649     Report[buf]: (3 bytes) => 14 0a 00
  22.299663     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
  22.299675     NUT doesn't use this HID object
  22.299687     Quick update...
  24.279087     upsdrv_updateinfo...
  24.282605     Report[int]: (2 bytes) => 0a 46
  24.282641     Got 1 HID objects...
  24.282655     Report[buf]: (2 bytes) => 0a 46
  24.282674     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 70
  24.282709     Quick update...

Broadcast message from ups (Mon Aug  1 10:04:39 2011):

UPS xen-home@localhost on battery
  26.289046     upsdrv_updateinfo...
  26.298500     Report[int]: (3 bytes) => 0e 40 03
  26.298537     Got 1 HID objects...
  26.298551     Report[buf]: (3 bytes) => 0e 40 03
  26.298572     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 832
  26.298607     Quick update...
  28.298922     upsdrv_updateinfo...
  28.318982     Report[int]: (2 bytes) => 15 01
  28.319021     HIDGetEvents: unexpected input report (ignored)
  28.319033     Got 0 HID objects...
  28.319046     Quick update...
  30.308875     upsdrv_updateinfo...
  30.338882     Report[int]: (3 bytes) => 14 0a 00
  30.338923     Got 13 HID objects...
  30.338937     Report[buf]: (3 bytes) => 14 0a 00
  30.338958     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 0
  30.338975     Report[buf]: (3 bytes) => 14 0a 00
  30.338992     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 1
  30.339008     Report[buf]: (3 bytes) => 14 0a 00
  30.339023     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 0
  30.339038     Report[buf]: (3 bytes) => 14 0a 00
  30.339053     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
  30.339069     Report[buf]: (3 bytes) => 14 0a 00
  30.339083     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
  30.339098     Report[buf]: (3 bytes) => 14 0a 00
  30.339113     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
  30.339128     Report[buf]: (3 bytes) => 14 0a 00
  30.339143     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
  30.339158     Report[buf]: (3 bytes) => 14 0a 00
  30.339173     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
  30.339185     NUT doesn't use this HID object
  30.339197     Report[buf]: (3 bytes) => 14 0a 00
  30.339212     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
  30.339224     NUT doesn't use this HID object
  30.339236     Report[buf]: (3 bytes) => 14 0a 00
  30.339250     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
  30.339265     Report[buf]: (3 bytes) => 14 0a 00
  30.339280     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
  30.339295     Report[buf]: (3 bytes) => 14 0a 00
  30.339310     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
  30.339325     Report[buf]: (3 bytes) => 14 0a 00
  30.339339     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
  30.339351     NUT doesn't use this HID object
  30.339363     Full update...
  30.339375     Report[buf]: (3 bytes) => 14 0a 00
  30.339387     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Feature, ReportID: 0x14, Offset: 2, Size: 1, Value: 0
  30.339401     Report[buf]: (3 bytes) => 14 0a 00
  30.339413     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Feature, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
  30.339427     Report[buf]: (3 bytes) => 14 0a 00
  30.339438     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Feature, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
  30.339452     Report[buf]: (3 bytes) => 14 0a 00
  30.339463     Path: UPS.PowerSummary.PresentStatus.Charging, Type: 
Feature, ReportID: 0x14, Offset: 0, Size: 1, Value: 0
  30.339477     Report[buf]: (3 bytes) => 14 0a 00
  30.339488     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Feature, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
  30.339502     Report[buf]: (3 bytes) => 14 0a 00
  30.339514     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Feature, ReportID: 0x14, Offset: 1, Size: 1, Value: 1
  30.339527     Report[buf]: (3 bytes) => 14 0a 00
  30.339538     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Feature, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
  30.339552     Report[buf]: (3 bytes) => 14 0a 00
  30.339563     Path: UPS.PowerSummary.PresentStatus.Overload, Type: 
Feature, ReportID: 0x14, Offset: 11, Size: 1, Value: 0
  30.339576     Report[buf]: (3 bytes) => 14 0a 00
  30.339588     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Feature, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
  30.339602     Report[buf]: (3 bytes) => 14 0a 00
  30.339613     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Feature, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
  30.340252     Report[get]: (3 bytes) => 26 0a 00
  30.340287     Path: UPS.PresentStatus.ACPresent, Type: Feature, ReportID: 
0x26, Offset: 2, Size: 1, Value: 0
  30.340303     Report[buf]: (3 bytes) => 26 0a 00
  30.340316     Path: UPS.PresentStatus.BatteryPresent, Type: Feature, 
ReportID: 0x26, Offset: 3, Size: 1, Value: 1
  30.340330     Report[buf]: (3 bytes) => 26 0a 00
  30.340342     Path: UPS.PresentStatus.BelowRemainingCapacityLimit, Type: 
Feature, ReportID: 0x26, Offset: 4, Size: 1, Value: 0
  30.340356     Report[buf]: (3 bytes) => 26 0a 00
  30.340368     Path: UPS.PresentStatus.Boost, Type: Feature, ReportID: 
0x26, Offset: 12, Size: 1, Value: 0
  30.340381     Report[buf]: (3 bytes) => 26 0a 00
  30.340393     Path: UPS.PresentStatus.Buck, Type: Feature, ReportID: 
0x26, Offset: 13, Size: 1, Value: 0
  30.340406     Report[buf]: (3 bytes) => 26 0a 00
  30.340418     Path: UPS.PresentStatus.Charging, Type: Feature, ReportID: 
0x26, Offset: 0, Size: 1, Value: 0
  30.340431     Report[buf]: (3 bytes) => 26 0a 00
  30.340442     Path: UPS.PresentStatus.CommunicationLost, Type: Feature, 
ReportID: 0x26, Offset: 10, Size: 1, Value: 0
  30.340456     Report[buf]: (3 bytes) => 26 0a 00
  30.340468     Path: UPS.PresentStatus.Discharging, Type: Feature, 
ReportID: 0x26, Offset: 1, Size: 1, Value: 1
  30.340481     Report[buf]: (3 bytes) => 26 0a 00
  30.340493     Path: UPS.PresentStatus.NeedReplacement, Type: Feature, 
ReportID: 0x26, Offset: 6, Size: 1, Value: 0
  30.340506     Report[buf]: (3 bytes) => 26 0a 00
  30.340518     Path: UPS.PresentStatus.Overload, Type: Feature, ReportID: 
0x26, Offset: 11, Size: 1, Value: 0
  30.340531     Report[buf]: (3 bytes) => 26 0a 00
  30.349071     Path: UPS.PresentStatus.RemainingTimeLimitExpired, Type: 
Feature, ReportID: 0x26, Offset: 5, Size: 1, Value: 0
  30.349095     Report[buf]: (3 bytes) => 26 0a 00
  30.349108     Path: UPS.PresentStatus.ShutdownImminent, Type: Feature, 
ReportID: 0x26, Offset: 9, Size: 1, Value: 0
  30.350268     Report[get]: (2 bytes) => 0a 43
  30.350381     Path: UPS.PowerSummary.RemainingCapacity, Type: Feature, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 67
  30.352272     Report[get]: (2 bytes) => 0c 0a
  30.352314     Path: UPS.PowerSummary.RemainingCapacityLimit, Type: 
Feature, ReportID: 0x0c, Offset: 0, Size: 8, Value: 10
  30.354280     Report[get]: (2 bytes) => 0b 1e
  30.354315     Path: UPS.PowerSummary.WarningCapacityLimit, Type: Feature, 
ReportID: 0x0b, Offset: 0, Size: 8, Value: 30
  30.356280     Report[get]: (3 bytes) => 0e 40 03
  30.356316     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Feature, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 832
  30.358293     Report[get]: (2 bytes) => 13 01
  30.358333     Path: UPS.PowerSummary.AudibleAlarmControl, Type: Feature, 
ReportID: 0x13, Offset: 0, Size: 8, Value: 1
  30.360300     Report[get]: (2 bytes) => 1f 18
  30.360342     Path: UPS.Output.PercentLoad, Type: Feature, ReportID: 
0x1f, Offset: 0, Size: 8, Value: 24
  30.362305     Report[get]: (2 bytes) => 15 01
  30.362346     Path: UPS.Battery.Test, Type: Feature, ReportID: 0x15, 
Offset: 0, Size: 8, Value: 1
  30.364280     Report[get]: (3 bytes) => 1d 00 00
  30.364315     Path: UPS.Input.Voltage, Type: Feature, ReportID: 0x1d, 
Offset: 0, Size: 16, Value: 0
  30.366301     Report[get]: (2 bytes) => 1e 00
  30.366341     Path: UPS.Input.Frequency, Type: Feature, ReportID: 0x1e, 
Offset: 0, Size: 8, Value: 0
  30.368302     Report[get]: (3 bytes) => 21 de 00
  30.368343     Path: UPS.Output.Voltage, Type: Feature, ReportID: 0x21, 
Offset: 0, Size: 16, Value: 222
  30.370299     Report[get]: (2 bytes) => 22 32
  30.370342     Path: UPS.Output.Frequency, Type: Feature, ReportID: 0x22, 
Offset: 0, Size: 8, Value: 50
  32.318753     upsdrv_updateinfo...
  32.348780     Report[int]: (2 bytes) => 0a 43
  32.348818     Got 1 HID objects...
  32.348832     Report[buf]: (2 bytes) => 0a 43
  32.348852     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 67
  32.348871     Quick update...
  34.328687     upsdrv_updateinfo...
  34.330117     Report[int]: (3 bytes) => 0e 80 03
  34.330150     Got 1 HID objects...
  34.330164     Report[buf]: (3 bytes) => 0e 80 03
  34.330184     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 896
  34.330220     Quick update...
  36.338567     upsdrv_updateinfo...
  36.346072     Report[int]: (2 bytes) => 15 01
  36.346108     HIDGetEvents: unexpected input report (ignored)
  36.346120     Got 0 HID objects...
  36.346133     Quick update...
  38.348471     upsdrv_updateinfo...
  38.368525     Report[int]: (3 bytes) => 14 0d 00
  38.368564     Got 13 HID objects...
  38.368579     Report[buf]: (3 bytes) => 14 0d 00
  38.368599     Path: UPS.PowerSummary.PresentStatus.Charging, Type: Input, 
ReportID: 0x14, Offset: 0, Size: 1, Value: 1
  38.368616     Report[buf]: (3 bytes) => 14 0d 00
  38.368632     Path: UPS.PowerSummary.PresentStatus.Discharging, Type: 
Input, ReportID: 0x14, Offset: 1, Size: 1, Value: 0
  38.368647     Report[buf]: (3 bytes) => 14 0d 00
  38.368662     Path: UPS.PowerSummary.PresentStatus.ACPresent, Type: 
Input, ReportID: 0x14, Offset: 2, Size: 1, Value: 1
  38.368677     Report[buf]: (3 bytes) => 14 0d 00
  38.368691     Path: UPS.PowerSummary.PresentStatus.BatteryPresent, Type: 
Input, ReportID: 0x14, Offset: 3, Size: 1, Value: 1
  38.368706     Report[buf]: (3 bytes) => 14 0d 00
  38.368721     Path: 
UPS.PowerSummary.PresentStatus.BelowRemainingCapacityLimit, Type: Input, 
ReportID: 0x14, Offset: 4, Size: 1, Value: 0
  38.368735     Report[buf]: (3 bytes) => 14 0d 00
  38.368750     Path: 
UPS.PowerSummary.PresentStatus.RemainingTimeLimitExpired, Type: Input, 
ReportID: 0x14, Offset: 5, Size: 1, Value: 0
  38.368765     Report[buf]: (3 bytes) => 14 0d 00
  38.368779     Path: UPS.PowerSummary.PresentStatus.NeedReplacement, Type: 
Input, ReportID: 0x14, Offset: 6, Size: 1, Value: 0
  38.368794     Report[buf]: (3 bytes) => 14 0d 00
  38.368808     Path: UPS.PowerSummary.PresentStatus.VoltageNotRegulated, 
Type: Input, ReportID: 0x14, Offset: 7, Size: 1, Value: 0
  38.368820     NUT doesn't use this HID object
  38.368832     Report[buf]: (3 bytes) => 14 0d 00
  38.368846     Path: UPS.PowerSummary.PresentStatus.ShutdownRequested, 
Type: Input, ReportID: 0x14, Offset: 8, Size: 1, Value: 0
  38.368858     NUT doesn't use this HID object
  38.368870     Report[buf]: (3 bytes) => 14 0d 00
  38.368883     Path: UPS.PowerSummary.PresentStatus.ShutdownImminent, 
Type: Input, ReportID: 0x14, Offset: 9, Size: 1, Value: 0
  38.368898     Report[buf]: (3 bytes) => 14 0d 00
  38.368913     Path: UPS.PowerSummary.PresentStatus.CommunicationLost, 
Type: Input, ReportID: 0x14, Offset: 10, Size: 1, Value: 0
  38.368928     Report[buf]: (3 bytes) => 14 0d 00
  38.368942     Path: UPS.PowerSummary.PresentStatus.Overload, Type: Input, 
ReportID: 0x14, Offset: 11, Size: 1, Value: 0
  38.368956     Report[buf]: (3 bytes) => 14 0d 00
  38.368970     Path: UPS.PowerSummary.PresentStatus.POWERCOM3, Type: 
Input, ReportID: 0x14, Offset: 15, Size: 1, Value: 0
  38.368982     NUT doesn't use this HID object
  38.368994     Quick update...

Broadcast message from ups (Mon Aug  1 10:04:54 2011):

UPS xen-home@localhost on line power
  40.358431     upsdrv_updateinfo...
  40.378411     Report[int]: (2 bytes) => 0a 50
  40.378450     Got 1 HID objects...
  40.378464     Report[buf]: (2 bytes) => 0a 50
  40.378484     Path: UPS.PowerSummary.RemainingCapacity, Type: Input, 
ReportID: 0x0a, Offset: 0, Size: 8, Value: 80
  40.378518     Quick update...
  42.368374     upsdrv_updateinfo...
  42.398315     Report[int]: (3 bytes) => 0e 80 07
  42.398355     Got 1 HID objects...
  42.398370     Report[buf]: (3 bytes) => 0e 80 07
  42.398391     Path: UPS.PowerSummary.RunTimeToEmpty, Type: Input, 
ReportID: 0x0e, Offset: 0, Size: 16, Value: 1920
  42.398428     Quick update...
  44.378263     upsdrv_updateinfo...
  44.418258     Report[int]: (2 bytes) => 15 01
  44.418305     HIDGetEvents: unexpected input report (ignored)
  44.418317     Got 0 HID objects...
  44.418331     Quick update...
^C  45.768243   Signal 2: exiting
  45.768284     upsdrv_cleanup...
[root@xen-home bin]#
===

Below are my conf-files (significant lines):
ups.conf:
===
user = ups

[xen-home]

# USB
        driver = usbhid-ups
        port = auto
        desc = "Xensource host UPS"
===

upsd.conf
===
LISTEN 127.0.0.1 3493
===

upsmon.conf:
===
MONITOR xen-home@localhost 1 upsmon ***** master
MINSUPPLIES 1
###SHUTDOWNCMD "/sbin/shutdown -h +0"
SHUTDOWNCMD "date >> /var/log/nutlog"
POLLFREQ 5
POLLFREQALERT 5
HOSTSYNC 15
DEADTIME 15
POWERDOWNFLAG /etc/killpower
RBWARNTIME 43200
NOCOMMWARNTIME 300
## Default 5
FINALDELAY 90 
===

upsd.users:
===
[admin]
        password = *****
        actions = SET
        instcmds = ALL

[upsmon]
        password  = *****
        upsmon master

===

> 
> cheers,
> Arno
> 

WBR,
Sergei Dubrov

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to