Hi,

I have more information, I did some more digging and found a debugging
mode for the driver.. So this what I'm seeing. Any ideas how I get
around the "PW_COMMAND_START_BYTE"?

Thanks for any help.
Greg


<snip>
root@omen:/lib/nut# ./bcmxcp -a powerware  -DDDDDDD  -i 5 -x baud_rate=9600
Network UPS Tools - BCMXCP UPS driver 0.23 (2.4.3)
RS-232 communication subdriver 0.17
   0.000000     debug level is '7'
   0.871186     Connected to UPS on /dev/ttyS0 with baudrate 9600
   0.871200     send_to_all: SETINFO device.type "ups"
   0.871206     send_to_all: SETINFO driver.version "2.4.3"
   0.871211     send_to_all: SETINFO driver.version.internal "0.23"
   0.871216     send_to_all: SETINFO driver.name "bcmxcp"
   1.155038     send_to_all: SETINFO ups.firmware "Cont:01.32 Inve:01.08
Rect:01.08 "
   1.155050     send_to_all: SETINFO ups.power.nominal "500000"
   1.155055     send_to_all: SETINFO output.phases "3"
   1.155061     send_to_all: SETINFO ups.mfr "Eaton"
   1.155070     send_to_all: SETINFO ups.model "Powerware Plus  500000i"
   1.155073     Length of meter map: 81

   1.155077     Index   Offset  Format  NUT

   1.155083     0000    0000    f0      output.L1-L2.voltage
   1.155088     0001    0004    f0      output.L2-L3.voltage
   1.155094     0002    0008    f0      output.L3-L1.voltage
   1.155099     0003    0012    f0      input.L1-L2.voltage
   1.155104     0004    0016    f0      input.L2-L3.voltage
   1.155109     0005    0020    f0      input.L3-L1.voltage
   1.155114     0009    0024    f0      None
   1.155119     0010    0028    f0      None
   1.155124     0011    0032    f0      None
   1.155129     0018    0036    f0      input.L1.current
   1.155134     0019    0040    f0      input.L2.current
   1.155139     0020    0044    f0      input.L3.current
   1.155152     0021    0048    f0      None
   1.155158     0022    0052    f0      None
   1.155163     0023    0056    f0      ups.power
   1.155168     0024    0060    f0      None
   1.155173     0025    0064    42      None
   1.155178     0026    0068    42      None
   1.155183     0027    0072    f0      output.frequency
   1.155188     0028    0076    f0      input.frequency
   1.155193     0029    0080    f0      None
   1.155198     0030    0084    f0      None
   1.155203     0032    0088    61      battery.current
   1.155208     0033    0092    f0      battery.voltage
   1.155213     0034    0096    f0      battery.charge
   1.155218     0035    0100    f0      battery.runtime
   1.155223     0059    0104    f0      None
   1.155228     0060    0108    f0      None
   1.155233     0061    0112    f0      None
   1.155238     0065    0116    f0      output.L1.current
   1.155244     0066    0120    f0      output.L2.current
   1.155249     0067    0124    f0      output.L3.current
   1.155254     0068    0128    f0      output.L1.current.nominal
   1.155259     0069    0132    f0      output.L2.current.nominal
   1.155264     0070    0136    f0      output.L3.current.nominal
   1.155269     0071    0140    f0      None
   1.155274     0072    0144    f0      None
   1.155279     0073    0148    f0      None
   1.155284     0078    0152    f0      output.L1-N.voltage
   1.155289     0079    0156    f0      output.L2-N.voltage
   1.155294     0080    0160    f0      output.L3-N.voltage
   1.155299     

   1.155303     Length of alarm map: 25

   1.155306     Index   Alarm   Supported

   1.155311     0000    INVERTER_AC_OVER_VOLTAGE        Yes
   1.155316     0001    INVERTER_AC_UNDER_VOLTAGE       Yes
   1.155321     0002    INVERTER_OVER_OR_UNDER_FREQ     Yes
   1.155325     0003    BYPASS_AC_OVER_VOLTAGE  Yes
   1.155330     0004    BYPASS_AC_UNDER_VOLTAGE Yes
   1.155334     0005    BYPASS_OVER_OR_UNDER_FREQ       Yes
   1.155339     0006    INPUT_AC_OVER_VOLTAGE   Yes
   1.155343     0007    INPUT_AC_UNDER_VOLTAGE  Yes
   1.155348     0008    INPUT_UNDER_OR_OVER_FREQ        Yes
   1.155352     0009    OUTPUT_OVER_VOLTAGE     Yes
   1.155357     0010    OUTPUT_UNDER_VOLTAGE    Yes
   1.155361     0011    OUTPUT_UNDER_OR_OVER_FREQ       Yes
   1.155366     -001    REMOTE_EMERGENCY_PWR_OFF        No
   1.155370     -001    REMOTE_GO_TO_BYPASS     No
   1.155375     0012    BUILDING_ALARM_6        Yes
   1.155379     0013    BUILDING_ALARM_5        Yes
   1.155384     0014    BUILDING_ALARM_4        Yes
   1.155388     0015    BUILDING_ALARM_3        Yes
   1.155392     0016    BUILDING_ALARM_2        Yes
   1.155397     0017    BUILDING_ALARM_1        Yes
   1.155404     -001    STATIC_SWITCH_OVER_TEMP No
   1.155409     -001    CHARGER_OVER_TEMP       No
   1.155413     -001    CHARGER_LOGIC_PWR_FAIL  No
   1.155417     -001    CHARGER_OVER_VOLTAGE_OR_CURRENT No
   1.155422     -001    INVERTER_OVER_TEMP      No
   1.155427     0018    OUTPUT_OVERLOAD Yes
   1.155431     -001    RECTIFIER_INPUT_OVER_CURRENT    No
   1.155436     -001    INVERTER_OUTPUT_OVER_CURRENT    No
   1.155440     0019    DC_LINK_OVER_VOLTAGE    Yes
   1.155445     0020    DC_LINK_UNDER_VOLTAGE   Yes
   1.155449     0021    RECTIFIER_FAILED        Yes
   1.155453     -001    INVERTER_FAULT  No
   1.155458     0022    BATTERY_CONNECTOR_FAIL  Yes
   1.155462     0023    BYPASS_BREAKER_FAIL     Yes
   1.155467     -001    CHARGER_FAIL    No
   1.155471     -001    RAMP_UP_FAILED  No
   1.155476     -001    STATIC_SWITCH_FAILED    No
   1.155480     -001    ANALOG_AD_REF_FAIL      No
   1.155485     -001    BYPASS_UNCALIBRATED     No
   1.155489     0024    RECTIFIER_UNCALIBRATED  Yes
   1.155494     0025    OUTPUT_UNCALIBRATED     Yes
   1.155498     0026    INVERTER_UNCALIBRATED   Yes
   1.155503     -001    DC_VOLT_UNCALIBRATED    No
   1.155507     -001    OUTPUT_CURRENT_UNCALIBRATED     No
   1.155512     -001    RECTIFIER_CURRENT_UNCALIBRATED  No
   1.155516     -001    BATTERY_CURRENT_UNCALIBRATED    No
   1.155521     -001    INVERTER_ON_OFF_STAT_FAIL       No
   1.155525     0027    BATTERY_CURRENT_LIMIT   Yes
   1.155530     0028    INVERTER_STARTUP_FAIL   Yes
   1.155534     -001    ANALOG_BOARD_AD_STAT_FAIL       No
   1.155539     0029    OUTPUT_CURRENT_OVER_100 Yes
   1.155543     -001    BATTERY_GROUND_FAULT    No
   1.155548     -001    WAITING_FOR_CHARGER_SYNC        No
   1.155552     -001    NV_RAM_FAIL     No
   1.155557     -001    ANALOG_BOARD_AD_TIMEOUT No
   1.155561     0030    SHUTDOWN_IMMINENT       Yes
   1.155566     0031    BATTERY_LOW     Yes
   1.155570     -001    UTILITY_FAIL    No
   1.155575     -001    OUTPUT_SHORT_CIRCUIT    No
   1.155579     -001    UTILITY_NOT_PRESENT     No
   1.155584     -001    FULL_TIME_CHARGING      No
   1.155588     -001    FAST_BYPASS_COMMAND     No
   1.155593     -001    AD_ERROR        No
   1.155597     -001    INTERNAL_COM_FAIL       No
   1.155602     -001    RECTIFIER_SELFTEST_FAIL No
   1.155606     -001    RECTIFIER_EEPROM_FAIL   No
   1.155611     -001    RECTIFIER_EPROM_FAIL    No
   1.155615     -001    INPUT_LINE_VOLTAGE_LOSS No
   1.155620     0032    BATTERY_DC_OVER_VOLTAGE Yes
   1.155624     -001    POWER_SUPPLY_OVER_TEMP  No
   1.155629     0033    POWER_SUPPLY_FAIL       Yes
   1.155633     -001    POWER_SUPPLY_5V_FAIL    No
   1.155638     -001    POWER_SUPPLY_12V_FAIL   No
   1.155642     0034    HEATSINK_OVER_TEMP      Yes
   1.155647     0035    HEATSINK_TEMP_SENSOR_FAIL       Yes
   1.155651     -001    RECTIFIER_CURRENT_OVER_125      No
   1.155656     -001    RECTIFIER_FAULT_INTERRUPT_FAIL  No
   1.155660     -001    RECTIFIER_POWER_CAPASITOR_FAIL  No
   1.155665     -001    INVERTER_PROGRAM_STACK_ERROR    No
   1.155669     -001    INVERTER_BOARD_SELFTEST_FAIL    No
   1.155674     -001    INVERTER_AD_SELFTEST_FAIL       No
   1.155678     -001    INVERTER_RAM_SELFTEST_FAIL      No
   1.155683     -001    NV_MEMORY_CHECKSUM_FAIL No
   1.155687     -001    PROGRAM_CHECKSUM_FAIL   No
   1.155692     -001    INVERTER_CPU_SELFTEST_FAIL      No
   1.155696     0036    NETWORK_NOT_RESPONDING  Yes
   1.155701     -001    FRONT_PANEL_SELFTEST_FAIL       No
   1.155705     -001    NODE_EEPROM_VERIFICATION_ERROR  No
   1.155710     -001    OUTPUT_AC_OVER_VOLT_TEST_FAIL   No
   1.155715     -001    OUTPUT_DC_OVER_VOLTAGE  No
   1.155719     0037    INPUT_PHASE_ROTATION_ERROR      Yes
   1.155724     -001    INVERTER_RAMP_UP_TEST_FAILED    No
   1.155728     -001    INVERTER_OFF_COMMAND    No
   1.155733     -001    INVERTER_ON_COMMAND     No
   1.155737     -001    TO_BYPASS_COMMAND       No
   1.155742     -001    FROM_BYPASS_COMMAND     No
   1.155746     -001    AUTO_MODE_COMMAND       No
   1.155750     0038    EMERGENCY_SHUTDOWN_COMMAND      Yes
   1.155755     -001    SETUP_SWITCH_OPEN       No
   1.155760     -001    INVERTER_OVER_VOLT_INT  No
   1.155764     -001    INVERTER_UNDER_VOLT_INT No
   1.155769     -001    ABSOLUTE_DCOV_ACOV      No
   1.155773     -001    PHASE_A_CURRENT_LIMIT   No
   1.155777     -001    PHASE_B_CURRENT_LIMIT   No
   1.155782     -001    PHASE_C_CURRENT_LIMIT   No
   1.155786     0039    BYPASS_NOT_AVAILABLE    Yes
   1.155791     -001    RECTIFIER_BREAKER_OPEN  No
   1.155795     0040    BATTERY_CONTACTOR_OPEN  Yes
   1.155800     0041    INVERTER_CONTACTOR_OPEN Yes
   1.155804     -001    BYPASS_BREAKER_OPEN     No
   1.155809     -001    INV_BOARD_ACOV_INT_TEST_FAIL    No
   1.155813     -001    INVERTER_OVER_TEMP_TRIP No
   1.155818     -001    INV_BOARD_ACUV_INT_TEST_FAIL    No
   1.155823     -001    INVERTER_VOLTAGE_FEEDBACK_ERROR No
   1.155827     -001    DC_UNDER_VOLTAGE_TIMEOUT        No
   1.155832     -001    AC_UNDER_VOLTAGE_TIMEOUT        No
   1.155836     -001    DC_UNDER_VOLTAGE_WHILE_CHARGE   No
   1.155841     -001    INVERTER_VOLTAGE_BIAS_ERROR     No
   1.155845     -001    RECTIFIER_PHASE_ROTATION        No
   1.155850     -001    BYPASS_PHASER_ROTATION  No
   1.155855     -001    SYSTEM_INTERFACE_BOARD_FAIL     No
   1.155859     -001    PARALLEL_BOARD_FAIL     No
   1.155863     -001    LOST_LOAD_SHARING_PHASE_A       No
   1.155868     -001    LOST_LOAD_SHARING_PHASE_B       No
   1.155872     -001    LOST_LOAD_SHARING_PHASE_C       No
   1.155877     -001    DC_OVER_VOLTAGE_TIMEOUT No
   1.155936     0042    BATTERY_TOTALLY_DISCHARGED      Yes
   1.155943     -001    INVERTER_PHASE_BIAS_ERROR       No
   1.155948     -001    INVERTER_VOLTAGE_BIAS_ERROR_2   No
   1.155953     -001    DC_LINK_BLEED_COMPLETE  No
   1.155957     -001    LARGE_CHARGER_INPUT_CURRENT     No
   1.155962     -001    INV_VOLT_TOO_LOW_FOR_RAMP_LEVEL No
   1.155967     -001    LOSS_OF_REDUNDANCY      No
   1.155971     -001    LOSS_OF_SYNC_BUS        No
   1.155976     -001    RECTIFIER_BREAKER_SHUNT_TRIP    No
   1.155983     -001    LOSS_OF_CHARGER_SYNC    No
   1.155994     -001    INVERTER_LOW_LEVEL_TEST_TIMEOUT No
   1.155999     -001    OUTPUT_BREAKER_OPEN     No
   1.156003     -001    CONTROL_POWER_ON        No
   1.156008     -001    INVERTER_ON     No
   1.156014     -001    CHARGER_ON      No
   1.156019     -001    BYPASS_ON       No
   1.156023     -001    BYPASS_POWER_LOSS       No
   1.156028     -001    ON_MANUAL_BYPASS        No
   1.156033     -001    BYPASS_MANUAL_TURN_OFF  No
   1.156037     -001    INVERTER_BLEEDING_DC_LINK_VOLT  No
   1.156042     -001    CPU_ISR_ERROR   No
   1.156046     -001    SYSTEM_ISR_RESTART      No
   1.156051     -001    PARALLEL_DC     No
   1.156055     -001    BATTERY_NEEDS_SERVICE   No
   1.156060     -001    BATTERY_CHARGING        No
   1.156068     0043    BATTERY_NOT_CHARGED     Yes
   1.156073     -001    DISABLED_BATTERY_TIME   No
   1.156079     -001    SERIES_7000_ENABLE      No
   1.156085     -001    OTHER_UPS_ON    No
   1.156090     -001    PARALLEL_INVERTER       No
   1.156096     -001    UPS_IN_PARALLEL No
   1.156101     -001    OUTPUT_BREAKER_REALY_FAIL       No
   1.156106     -001    CONTROL_POWER_OFF       No
   1.156110     -001    LEVEL_2_OVERLOAD_PHASE_A        No
   1.156115     -001    LEVEL_2_OVERLOAD_PHASE_B        No
   1.156121     -001    LEVEL_2_OVERLOAD_PHASE_C        No
   1.156126     -001    LEVEL_3_OVERLOAD_PHASE_A        No
   1.156132     -001    LEVEL_3_OVERLOAD_PHASE_B        No
   1.156137     -001    LEVEL_3_OVERLOAD_PHASE_C        No
   1.156143     -001    LEVEL_4_OVERLOAD_PHASE_A        No
   1.156148     -001    LEVEL_4_OVERLOAD_PHASE_B        No
   1.156155     -001    LEVEL_4_OVERLOAD_PHASE_C        No
   1.156159     0044    UPS_ON_BATTERY  Yes
   1.156165     0045    UPS_ON_BYPASS   Yes
   1.156170     0046    LOAD_DUMPED     Yes
   1.156176     -001    LOAD_ON_INVERTER        No
   1.156180     -001    UPS_ON_COMMAND  No
   1.156185     -001    UPS_OFF_COMMAND No
   1.156191     -001    LOW_BATTERY_SHUTDOWN    No
   1.156197     -001    AUTO_ON_ENABLED No
   1.156202     -001    SOFTWARE_INCOMPABILITY_DETECTED No
   1.156206     -001    INVERTER_TEMP_SENSOR_FAILED     No
   1.156212     -001    DC_START_OCCURED        No
   1.156219     -001    IN_PARALLEL_OPERATION   No
   1.156225     -001    SYNCING_TO_BYPASS       No
   1.156229     -001    RAMPING_UPS_UP  No
   1.156235     -001    INVERTER_ON_DELAY       No
   1.156240     -001    CHARGER_ON_DELAY        No
   1.156245     -001    WAITING_FOR_UTIL_INPUT  No
   1.156250     -001    CLOSE_BYPASS_BREAKER    No
   1.156256     -001    TEMPORARY_BYPASS_OPERATION      No
   1.156261     -001    SYNCING_TO_OUTPUT       No
   1.156267     -001    BYPASS_FAILURE  No
   1.156272     -001    AUTO_OFF_COMMAND_EXECUTED       No
   1.156277     -001    AUTO_ON_COMMAND_EXECUTED        No
   1.156283     -001    BATTERY_TEST_FAILED     No
   1.156289     -001    FUSE_FAIL       No
   1.156293     0047    FAN_FAIL        Yes
   1.156299     -001    SITE_WIRING_FAULT       No
   1.156304     -001    BACKFEED_CONTACTOR_FAIL No
   1.156338     -001    ON_BUCK No
   1.156343     -001    ON_BOOST        No
   1.156347     -001    ON_DOUBLE_BOOST No
   1.156352     -001    BATTERIES_DISCONNECTED  No
   1.156356     

   1.156360     Length of Config_block: 48

   1.156366     Length of statistics map: 62

   1.156371     Length of command list: 4047

   1.156375     Length of outlet_block: 33650

   1.156380     Length of alarm_block: 34179

   2.157495     Receive error (PW_COMMAND_START_BYTE): 0!!!

   3.158599     Receive error (PW_COMMAND_START_BYTE): 0!!!

   4.159701     Receive error (PW_COMMAND_START_BYTE): 0!!!

   4.159712     Communications with UPS lost: Error executing command
   4.159717     Could not communicate with the ups
</snip>


On Thu, Jan 12, 2012 at 2:38 PM, Gregory Skelton
<[email protected]> wrote:
> Hi All,
>
> I'm a system administrator of a large data center, and I've recently
> replaced the machine that acted as the nut master for our
> cluster/cloud. The machine that was interfacing with our Powerware
> 9135 450KVA 3 phase UPS, not to confused with Eaton's Powerware 9135,
> and was a Fedora Core 4 box running nut version 2.0.3-4 connected by a
> serial cable.
>
> We are using these versions of nut on our FC4 machine:
> Network UPS Tools - UPS driver controller 2.1.0
> Network UPS Tools - BCMXCP UPS driver 0.11 (2.1.0)
>
> We've had intermittent UPS driver problem, but it worked. Now I'm
> trying to connect to our UPS using this new machine and I get this:
>
> root@omen:/etc/nut# upsdrvctl start
> Network UPS Tools - UPS driver controller 2.4.3
> Network UPS Tools - BCMXCP UPS driver 0.23 (2.4.3)
> RS-232 communication subdriver 0.17
> Connected to UPS on /dev/ttyS0 with baudrate 9600
> Communications with UPS lost: Error executing command
> Could not communicate with the ups
> Driver failed to start (exit status=1)
>
> I've tried to google for an answer and found a great reference, but I
> haven't been able to communicate with the UPS
> http://blog.shadypixel.com/monitoring-a-ups-with-nut-on-debian-or-ubuntu-linux/
>
> Is there any diagnostics or log files I can create to track down this
> problem? "Driver failed to start (exit status=1)" isn't all that
> helpful
>
> Thanks in advance for any and all help.
>
> Best,
> Greg
>
> PS I have both machines, so if I missed anything I can get it for you.

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to