Hi Jorge, 2012/1/20 Jorge Infante <[email protected]>: > Ok, Arnaud. Thanks for your response. > > My powerware is 9120 (I did a mistake with the model of ups). > I'm using openfiler ESA 2.99.1 (64 bits version) > I'did compile the nut from sources. I'm using nut 2.4.1.
if you can, you should try the latest 2.6.3. There is a few improvements and fixes that have happen since 2.4.1 on this driver... > My configuration files: > > [root@myhost etc]# more upsd.conf > ACL all 0.0.0.0/0 > ACL localhost 127.0.0.1/32 > ACCEPT localhost > REJECT all > > [root@myhost etc]# more upsd.users > [admin] > password = xxxxxxxxxxx > actions = SET > instcmds = ALL > > [root@myhost etc]# more ups.conf > [server] > #driver = megatec > #driver = liebert-hid > #driver = liebert > #driver = usbhid-ups > #port = auto > driver = bcmxcp_usb ------------> I can't use usb with another driver bcmxcp_usb is indeed the right driver for your unit. > port = /dev/usb8 setting port to "auto" should be sufficient. > shutdown_delay = 120 -----------> This parameter is ignored > > [root@myhost etc]# more upssched.conf > CMDSCRIPT /scripts/upssched.sh > PIPEFN /scripts/upssched.pipe > LOCKFN /scripts/upssched.lock > AT ONBATT * START-TIMER onbattwarn 180 > AT ONBATT * EXECUTE upsonbatt > AT ONLINE * CANCEL-TIMER onbattwarn > AT ONLINE * EXECUTE backonpower > > [root@myhost etc]# more upsmon.conf > MONITOR server 1 admin xxxxxxxxxx master > MINSUPPLIES 1 > SHUTDOWNCMD "/scripts/upsshutdown.sh" > #NOTIFYCMD "/scripts/upsnotify.sh" > NOTIFYCMD "/sbin/upssched" > POLLFREQ 5 > POLLFREQALERT 5 > HOSTSYNC 15 > DEADTIME 15 > RBWARNTIME 43200 > NOCOMMWARNTIME 300 > FINALDELAY 5 > NOTIFYMSG ONLINE "UPS is back online" > NOTIFYMSG ONBATT "UPS is on battery" > NOTIFYMSG LOWBATT "UPS has a low battery (if also on battery, it's > 'critical')" > NOTIFYMSG FSD "UPS is being shutdown by the master (FSD = 'Forced > Shutdown')" > NOTIFYMSG COMMOK "Communications established with the UPS" > NOTIFYMSG COMMBAD "Communications lost to the UPS" > NOTIFYMSG SHUTDOWN "The system is being shutdown" > NOTIFYMSG REPLBATT "The UPS battery is bad and needs to be replaced" > NOTIFYMSG NOCOMM "A UPS is unavailable (can't be contacted for > monitoring)" > NOTIFYMSG NOPARENT "The process that shuts down the system has died > (shutdown impossible)" > NOTIFYFLAG ONLINE SYSLOG+WALL+EXEC > NOTIFYFLAG ONBATT SYSLOG+WALL+EXEC > NOTIFYFLAG LOWBATT SYSLOG+WALL+EXEC > NOTIFYFLAG FSD SYSLOG+WALL+EXEC > NOTIFYFLAG COMMOK SYSLOG+WALL+EXEC > NOTIFYFLAG COMMBAD SYSLOG+WALL+EXEC > NOTIFYFLAG SHUTDOWN SYSLOG+WALL+EXEC > NOTIFYFLAG REPLBATT SYSLOG+WALL+EXEC > NOTIFYFLAG NOCOMM SYSLOG+WALL+EXEC > NOTIFYFLAG NOPARENT SYSLOG+WALL+EXEC > > on upsshutdown.sh, I'm suspending my virtual machines (in another hosts), > and, at end, I'm executing shutdown of "myhost". > > [root@myhost scripts]# more upssched.sh > #!/bin/sh > export MAILTO="[email protected]" > case $1 in > upsonbatt) > echo "En 3 minutos se iniciara el apagado de equipos." | mailx -s "MUNI: > Corte de luz" ${MAILTO} > ;; > backonpower) > echo "Se cancelo el apagado." | mailx -s "MUNI: Volvio la luz" ${MAILTO} > ;; > onbattwarn) > echo "Hace 3 minutos que no hay luz." | mailx -s "MUNI: Se inicia el > apagado > " ${MAILTO} > /sbin/upsmon -c fsd <---- This command run the script upsshutdown.sh, > but don't stop the ups > ;; > esac > > [root@myhost scripts]# upsc server > ambient.temperature: 40 > ambient.temperature.high: 40 > battery.charge: 100 > battery.runtime: 2610 > battery.voltage: 54.9 > driver.name: bcmxcp_usb > driver.parameter.pollinterval: 2 > driver.parameter.port: /dev/usb8 > driver.parameter.shutdown_delay: 120 > driver.version: 2.4.1 > driver.version.internal: 0.21 > input.frequency: 50.0 > input.frequency.high: 52 > input.frequency.low: 48 > input.frequency.nominal: 50 > input.transfer.boost.high: 176 > input.transfer.high: 276 > input.transfer.low: 160 > ambient.temperature: 40 > ambient.temperature.high: 40 > battery.charge: 100 > battery.runtime: 2610 > battery.voltage: 54.8 > driver.name: bcmxcp_usb > driver.parameter.pollinterval: 2 > driver.parameter.port: /dev/usb8 > driver.parameter.shutdown_delay: 120 > driver.version: 2.4.1 > driver.version.internal: 0.21 > input.frequency: 50.0 > input.frequency.high: 52 > input.frequency.low: 48 > input.frequency.nominal: 50 > input.transfer.boost.high: 176 > input.transfer.high: 276 > input.transfer.low: 160 > input.transfer.trim.low: 254 > input.voltage: 228 > input.voltage.nominal: 220 > outlet.1.delay.shutdown: -1 > outlet.1.delay.start: 60 > outlet.1.id: 1 > outlet.1.status: On > outlet.2.delay.shutdown: -1 > outlet.2.delay.start: 60 > outlet.2.id: 2 > outlet.2.status: On > output.current: 1.6 > output.current.nominal: 6.8 > output.frequency: 50.0 > output.phases: 1 > output.voltage: 221 > output.voltage.nominal: 220 > ups.beeper.status: enabled > ups.firmware: Cont:02.05 Inve:02.05 > ups.load: 22.9 > ups.model: PW9120 1500VA > ups.power: 344 > ups.power.nominal: 1500 > ups.serial: RY095A0163 > ups.status: OL > > [root@myhost scripts]# upscmd -l server > Instant commands supported on UPS [server]: > outlet.1.shutdown.return - Description unavailable > outlet.2.shutdown.return - Description unavailable > shutdown.return - Turn off the load and return when power is back > shutdown.stayoff - Turn off the load and remain off > test.battery.start - Start a battery test > > [root@myhost scripts]# upsrw -s ups.delay.shutdown=120 -u admin -p > xxxxxxxxxx server > Unexpected response from upsd: ERR VAR-NOT-SUPPORTED you can obtain the list of supported settings using: $ upsrw server > I'm starting the nut with: > > upsdrvctl -u root -D start > upsd -D -u root & FYI: running upsd in debug mode (Ie '-D') prevent it from writing its pid file. > pidof_upsd >/var/state/ups/upsd.pid > upslog -s server -u root -l /var/log/ups.log > pidof_upslog >/var/state/ups/upslog.pid > upsmon -u root -p the need to run nut components as root could be avoided if the pid and run directories exist and have a mode of 750 at least, and root:nut (or the 'nut' equivalent username) > I'm not using the nut provided for openfiler, because is not working with my > ups. > I did replace all programs for my version compiled from sources. > I'm thinking the command "/sbin/upsmon -c fsd" is used for the poweroff > (waiting to delay in the ups). > > Well. If you need more information, please email me. > I'm specting about ideas. I'm still interested in understanding where nut 'powerdown' is called. it's generally the task of /etc/init.d/halt, which calls this final action. and the nut script should check for 'upsmon -K' return code (EXIT_SUCCESS or EXIT_FAILURE) to see if calling 'upsdrvctl shutdown' is needed. I would also be interested in the following test: - power down your system, and remove it from the UPS (to be sure not to crash your computer during the tests) - replace your computer by a light bulb or equivalent, - restart everything, - start on the nut driver (stop nut if necessary) in debug mode. Ie: $ /path/to/bcmxcp_usb -DDDDD -a upsname - now call the 'shutdown.return' command, $ upscmd -u admin -p xxxxxxxxxx server shutdown.return - when done, stop the driver (Ctrl+C) and send me back the driver debug output. cheers, Arnaud -- Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ Debian Developer - http://www.debian.org Free Software Developer - http://arnaud.quette.free.fr/ > 2012/1/20 Arnaud Quette <[email protected]> >> >> Hi Jorge, >> >> 2012/1/19 Jorge Infante <[email protected]>: >> > Hi! >> > I'm using nut to control a ups powerware 9135. >> > All are working, but, in the shutdown, the ups don't poweroff. >> > I did check with upsc, and I can't see a ups.delay.shutdown variable to >> > set >> > the time of automatic poweroff, when I did complete the shutdown of >> > machines. >> > Before, I did use a propietary program to work with this ups, and the >> > daemon >> > did poweroff the ups without problems. >> > But, now, I have only a openfiler based machine, and the propietary >> > program >> > don't run (but, I did find nut to replace it). >> > Can any help me? >> >> sure, but I'll need some more information: >> - which Openfiler version are you using? >> - which NUT version and driver (or port of your UPS) are you using? >> - any configuration files, and more specifically, upsmon.conf (trimmed >> from passwords!), >> - upsc/upsrw/upscmd outputs. >> >> I would also need to see the system halt script (/etc/init.d/halt) or >> equivalent on Openfiler, to see how the nut script gets called to >> poweroff the UPS. >> I've not been able to find the sources, so any pointer to it would be >> appreciated. >> >> cheers, >> Arnaud >> -- >> Linux / Unix Expert R&D - Eaton - http://powerquality.eaton.com >> Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org/ >> Debian Developer - http://www.debian.org >> Free Software Developer - http://arnaud.quette.free.fr/ > > _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser