Arnaud Quette wrote (2012-02-02 14:13): I did a test with an older version of my UPS, same model, but no USB connector. This time, everything worked fine: Feb 4 12:01:37 b1 upsmon[1494]: UPS upsb1@localhost on battery Feb 4 12:18:52 b1 upsmon[1494]: UPS upsb1@localhost battery is low Feb 4 12:18:52 b1 upsmon[1494]: Executing automatic power-fail shutdown Feb 4 12:18:52 b1 upsmon[1494]: Auto logout and shutdown proceeding [...] Feb 4 12:19:06 b1 upsd[1480]: mainloop: Interrupted system call [...] Feb 4 12:19:10 b1 syslogd: exiting on signal 15
> /etc/killpower is cleared at upsmon startup, in case it exists. It was this time, but not when the shutdown had failed. > you have not answered to my question on where "upsdrvctl shutdown" is > called in the process? > as told, on Debian, it's handled by the halt script. It's in /usr/local/etc/rc.d/nut, which is called when entering shutdown "runlevel". I watched the upsc output during that test. It started with ups.alarm: INPUT_AC_UNDER_VOLTAGE INPUT_UNDER_OR_OVER_FREQ UTILITY_NOT_PRESENT BATTERY_TOTALLY_DISCHARGED LOAD_DUMPED ups.beeper.status: enabled ups.status: ALARM OB I disabled the beeper with the button at the fron panel, but it still said enabled. The LOAD_DUMPED output is nonsense, this UPS cannot dump load (except for dumping everything, which it didn't) and the battery was not totally discharged when I started the test. Later on it said: battery.charge: 70 battery.runtime: 95 battery.voltage: 10.49 ups.alarm: INPUT_AC_UNDER_VOLTAGE INPUT_UNDER_OR_OVER_FREQ UTILITY_FAIL UTILITY_NOT_PRESENT BATTERY_TOTALLY_DISCHARGED LOAD_DUMPED ups.status: FSD ALARM OB LB So finally, the utility which was not present (see above) now failed. :-) I guess, Ill configure that timer thing, just to be sure shutdown works. _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser