Hello,

schrieb Arnaud Quette, Am 16.02.2012 18:48:

> Can you please counter check, and report back upsc/upsrw/upscmd

upsc:
# upsc YQ450
battery.voltage: 13.40
beeper.status: disabled
device.type: ups
driver.name: blazer_usb
driver.parameter.pollinterval: 2
driver.parameter.port: auto
driver.parameter.productid: 0002
driver.parameter.protocol: zinto
driver.parameter.subdriver: cypress
driver.parameter.vendorid: 06da
driver.version: 2.6.3
driver.version.internal: 0.04
input.frequency: 50.0
input.voltage: 232.0
input.voltage.fault: 1.0
output.voltage: 232.0
ups.delay.shutdown: 30
ups.delay.start: 180
ups.load: 0
ups.productid: 0002
ups.status: OL BYPASS
ups.temperature: 25.0
ups.type: offline / line interactive
ups.vendorid: 06da

# upsrw -u xxx -p xxx -s ups.delay.start YQ450
Enter new value for ups.delay.start: 90
Unexpected response from upsd: ERR ACCESS-DENIED
# upsrw -u xxx -p xxx -s ups.delay.shutdown YQ450
Enter new value for ups.delay.shutdown: 90
Unexpected response from upsd: ERR ACCESS-DENIED

# upscmd -u xxx -p xxx YQ450 shutdown.return 1
Unexpected response from upsd: ERR ACCESS-DENIED

> output, along with the shutdown test:
> http://www.networkupstools.org/docs/user-manual.chunked/ar01s06.html#Shutdown_design
> 

while doing shutdown
# upslog -s yq450 -i 2 -l -
 Network UPS Tools upslog 2.6.3
 logging status of yq450 to - (2s intervals)
 20120227 091805 NA 0.0 0 [OB] 25.0 0.0
 20120227 091807 NA 0.0 0 [OB] 25.0 0.0
 20120227 091809 NA 0.0 0 [OB] 25.0 0.0
 20120227 091811 NA 0.0 0 [OB] 25.0 0.0
 20120227 091957 NA NA NA [FSD WAIT] NA 0.0
 20120227 091959 NA 0.0 0 [FSD OB] 25.0 0.0
 20120227 092001 NA 0.0 0 [FSD OB LB] 25.0 0.0
 20120227 092003 NA 0.0 0 [FSD OB LB] 25.0 0.0
so, no battery voltage is displayed

parallel
/lib/nut/blazer_usb -a YQ450 -DDDDD
   23.832061     read: (000.0 001.0 230.0 000 00.0 12.5 25.0 10001000
   25.472224     send: Q1
   25.816057     read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
   25.816249     send_to_all: SETINFO ups.status "OB LB"
   27.473243     send: Q1
   27.832053     read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
   29.476227     send: Q1
   29.848055     read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
   31.478227     send: Q1
   31.832056     read: (000.0 001.0 230.0 000 00.0 12.5 25.0 11001000
   32.070549     send_to_one: PONG

Temperature is always 25.0°C
When cutting off power to the UPS, power to the outlets isn't switched off
despite the low battery warning (at least 15 minutes after cutting power)
Do I have a faulty UPS?2

Thomas

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to