2012/6/6 Marius Gavrilescu <[email protected]>:
> On Wed, Jun 06, 2012 at 08:00:37PM +0200, Arnaud Quette wrote:
>> thanks for your update.
>> is shutdown working as expected?
>
> Never tried it. I'm a beginner to NUT, what command(s) should I try?

http://www.networkupstools.org/docs/user-manual.chunked/ar01s06.html#Shutdown_design

>> could you please also report the various things requested here (uspc,
>> upsrw, ..;):
>
> -------- shell output -------
> # upsc ups
> battery.voltage: 13.60
> battery.voltage.nominal: 12.0
> beeper.status: enabled
> device.type: ups
> driver.name: blazer_ser
> driver.parameter.pollinterval: 2
> driver.parameter.port: /dev/ttyS0
> driver.version: 2.6.3
> driver.version.internal: 1.51
> input.current.nominal: 2.0
> input.frequency: 50.1
> input.frequency.nominal: 50
> input.voltage: 236.7
> input.voltage.fault: 236.7
> input.voltage.nominal: 230
> output.voltage: 236.7
> ups.delay.shutdown: 30
> ups.delay.start: 180
> ups.load: 14
> ups.status: OL
> ups.temperature: 25.0
> ups.type: offline / line interactive
> # upscmd -l ups
> Instant commands supported on UPS [ups]:
>
> beeper.toggle - Toggle the UPS beeper
> load.off - Turn off the load immediately
> load.on - Turn on the load immediately
> shutdown.return - Turn off the load and return when power is back
> shutdown.stayoff - Turn off the load and remain off
> shutdown.stop - Stop a shutdown in progress
> test.battery.start - Start a battery test
> test.battery.start.deep - Start a deep battery test
> test.battery.start.quick - Start a quick battery test
> test.battery.stop - Stop the battery test
> ------- cut here -------
>
> Running `upsrw ups` returns nothing, am I doing something wrong?

no

> PS: In the e-mail subject I said 'REDi Blazer 600VA'.
> While the UPS was branded like this, after some searching
> I found out that this UPS is actually made by Centralion.
>
> Product details from Centralion here:
> http://www.centralion.com/html/product/back-Product-ups-blazer400.htm

most (if not all) blazer supported units come from there ;-)

> Exact picture and specifications [in romanian] of my UPS here:
> http://www.emag.ro/ups-redi-blazer-600va-blazer600c/pd/EX5X2BBBM/
>
> Hope this helps!

yep, thanks.

cheers,
Arnaud

_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to