Arnaud Quette wrote:

2012/6/28 Tmima Pliroforikis Perifereiakis Enotitas Pierias
<[email protected] <mailto:[email protected]>>

    28/6/2012, Arnaud Quette wrote:

    Just checked with the FreeBSD ports tree and the latest available is
    2.6.1, so I'll recheck in 2-3 weeks for a newer NUT and will
    follow-up with my findings on this list.


so, in the meantime, prefer to revert back to mge-shut and modify
temporarily your setting of ups.delay.* through upsrw by
ondelay/offdelay in ups.conf. Using ups.timer will directly start the
countdown, which is probably not the desired behavior (equivalent to
calling shutdown.return, with using ondelay/offdelay in ups.conf).

I have reverted back to mge-shut, thanks again for the info.

What I do remember is that when I modified the nut startup script some 5+ years ago, I employed those 2 upsrw commands specifically because I was unsuccessful in having the UPS power-off as well...

I need to make sure we are talking about the same here. I've been employing the following 2 commands (which do not work anymore as you've informed me) with mge-shut: ${nut_prefix}/bin/upsrw -s ups.delay.shutdown=80 -u user -p pass mailfw@localhost ${nut_prefix}/bin/upsrw -s ups.delay.start=15 -u user -p pass mailfw@localhost

IIRC, I had these two commands to make sure that on battery low, during the system shutdown process and when the /usr/local/etc/rc.d/nut script would be called with the stop parameter, the UPS would be configured to:
* Turn off in 80"
* when the power returns, the load should be powered not immediately, but after 15" in order to make sure that UPS gets some "juice"

That is, the expected sequence would be:
(power loss) -> (battery low) -> (initiate system shutdown) -> (run nut script with "stop" argument) -> (at time t1: configure ups to turn off after 80") -> (proceed) with the rest of system shutdown) -> (system halts) -> (at time t1+80": UPS turns off)

and when power returns:

(power returns) -> (time t1: ups starts charging, without powering the load) -> (time t1+15" UPS starts powering the load)

Is my understanding correct of how these two should work? I'm asking here because it seems that I might have misunderstood how ups.delay.startup works... Is ups.delay.startup used only to restart the load during

According to the mge-shut man page, ondelay sets "... the timer before the UPS is turned off after the kill powercommand is sent (via the -k switch).

So it seems that is something entirely different.

Confused a bit..

M.-