Hi Fabio

2012/9/6 Fabio Cecamore <[email protected]>

>  Hello,
> i've a problem, this is my configuration:
> - Atlantis Land UPS with serial port
> - a generic RS232 to USB cable adapter (QinHeng Electronics HL-340
> USB-Serial adapter for linux).
>
> The problem is in the syslog file where i find:
> [...]
> Aug 19 09:07:25 ProLiant megatec[1126]: Communications with UPS lost: No
> status from UPS.
> Aug 19 09:07:26 ProLiant megatec[1126]: Communications with UPS
> re-established
> Aug 19 09:09:36 ProLiant megatec[1126]: Communications with UPS lost: No
> status from UPS.
> Aug 19 09:09:36 ProLiant megatec[1126]: Communications with UPS
> re-established
> [...]
>
> and using the driver (blazer_ser or megatec, is the same) in debug mode i
> read:
>
> 0.000000 debug level is '12'
> 0.037842 DTR=1, RTS=0
> 0.041830 send_to_all: SETINFO device.type "ups"
> 0.041906 send_to_all: SETINFO driver.version "2.4.3"
> 0.041924 send_to_all: SETINFO driver.version.internal "1.6"
> 0.041942 send_to_all: SETINFO driver.name "megatec"
> [........]
> 413.251768 Asking for UPS status [Q1]...
> 415.854720 Q1 => FAILED [timeout]
> 415.854786 Poll failure [1].
> 415.854803 Communications with UPS lost: No status from UPS.
> 415.854825 Asking for UPS status [Q1]...
> 416.455619 Q1 => OK [(229.8 140.0 229.8 004 49.8 13.6 30.7 00001001]
> 416.455723 Q1 VALUES => [229.8 140.0 229.8 4.0 49.8 13.6 30.7 00001001]
> 416.455739 Communications with UPS re-established
> 416.455766 send_to_all: SETINFO input.voltage "229.8"
> 416.455791 send_to_all: SETINFO output.voltage "229.8"
> 416.455813 send_to_all: SETINFO input.frequency "49.8"
> [........]
>
> with a infinite loop of this timeout.
> What can be the problem ?
>

this old megatec driver, which has since been replaced by blazer, was not
as flexible when it comes to transient communication errors.
thus, it was syslog'ing every such failures, and declaring staleness more
quickly.

you should consider updating to a more recent NUT version, such as 2.6.5,
along with moving to the blazer drivers.

cheers,
Arnaud
-- 
Linux / Unix / Opensource Engineering Expert - Eaton -
http://opensource.eaton.com
Network UPS Tools (NUT) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to