Hi,

One of my APC devices reports: "unacceptable utility voltage rate of change".
I believe it has something to do with input voltage fluctuating too fast maybe 
even beneath or over the input voltage thresholds.
Should I worry about this?
should I measure input voltage? (I suppose I'd need more than multimeter 
readings. Maybe an oscilloscope or a multimeter that can record statistics? - 
I'm no expert in this field...)

battery.alarm.threshold         :       0
battery.charge  :       100.0
battery.charge.restart  :       00
battery.date    :       09/02/08
battery.packs   :       000
battery.runtime         :       960
battery.runtime.low     :       120
battery.voltage         :       55.05
battery.voltage.nominal         :       048
device.mfr      :       APC
device.model    :       SMART-UPS 5000 RM DL4
device.serial   :       AS0836160289
device.type     :       ups
driver.name     :       apcsmart
driver.parameter.pollinterval   :       2
driver.parameter.port   :       /dev/UPS-1
driver.version  :       2.6.3
driver.version.internal         :       3.0
input.frequency         :       50.00
input.quality   :       FF
input.sensitivity       :       H
input.transfer.high     :       253
input.transfer.low      :       196
input.transfer.reason   :       unacceptable utility voltage rate of change
input.voltage   :       226.2
input.voltage.maximum   :       226.2
input.voltage.minimum   :       226.2
output.voltage  :       226.2
output.voltage.nominal  :       230
ups.delay.shutdown      :       020
ups.delay.start         :       000
ups.firmware    :       112.1DL4.I
ups.id  :       UPS_IDEN
ups.load        :       039.0
ups.mfr         :       APC
ups.mfr.date    :       09/02/08
ups.model       :       SMART-UPS 5000 RM DL4
ups.serial      :       AS0836160289
ups.status      :       OL
ups.temperature         :       022.5
ups.test.interval       :       1209600
ups.test.result         :       NO

Thanks,

Vieri


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to