On 18.4.2013 г. 22:24 ч., Arnaud Quette wrote:

2013/4/18 Pladi Computers Ltd. <[email protected] <mailto:[email protected]>>

    UPS:
    
http://www.eaton.com/Eaton/ESeriesUPS/DXUPS/index.htm?wtredirect=www.eaton.com/DXUPS

    I have the same problem on two different computers. The first one
is running Ubuntu 12.10 i386 , the second one is running Debian 6.0 x64. Both of them are updated. I tried using different serial
    cable but the result is the same.
    The connection to the ups using Windows 7 and Winpower is working
    fine on the computer I tested.

    The nut version on the Debian pc is 2.4.3-1.1squeeze2 and on the
    Ubuntu one is 2.6.3-1ubuntu2. Both of them are installed from the
    repositories.

    I tried adding "pollinterval=20" to ups.conf, "MAXAGE25" to
    upsd.conf and "DEADTIME25" to upsmon.conf but I still get stale
    errors in syslog and null information about all the stats.

    #ups.conf
    [ups0]
    driver = mge-utalk
    port = /dev/ttyS0
    pollinterval = 20

    The logs are in the attached file.


mge-utalk was fixed in the development branch, but was not yet released.
You can download from github either the tree or just the patch:
https://github.com/networkupstools/nut/commit/9257cc0b68b8bdb65f97b7a15fc3b8d947dfaee8

cheers,
Arnaud
--
NUT (Network UPS Tools) Project Leader - http://www.networkupstools.org
Debian Developer - http://www.debian.org
Free Software Developer - http://arnaud.quette.fr

I downloaded and compiled the tree but I still get zeroes and it takes a lot more time to get them.
./mge-utalk -DDD -a ups0
Network UPS Tools - MGE UPS SYSTEMS/U-Talk driver 0.93 (2.6.5)
   0.000000     debug level is '3'
   2.105848     Got model name: NAK
   3.193505     Syst Stat >NAK<
   3.741509     Batt Stat >NAK<
   4.280759     Load Stat > <
   4.828750     Bypass Stat >ACK<
   5.376322     Syst Stat >NAK<
   5.924311     Batt Stat >NAK<
   6.464392     Load Stat > <
   7.012386     Bypass Stat >ACK<
   7.559960     Syst Stat >NAK<
   8.107945     Batt Stat >NAK<
   8.647195     Load Stat > <
   9.194774     Bypass Stat >ACK<
   9.742346     Syst Stat >NAK<
  10.291167     Batt Stat >NAK<
  10.831247     Load Stat > <
  11.379657     Bypass Stat >ACK<
  11.927647     Syst Stat >NAK<
  12.476077     Batt Stat >NAK<
  13.015299     Load Stat > <
  13.562878     Bypass Stat >ACK<
  14.110449     Syst Stat >NAK<
  14.658466     Batt Stat >NAK<
  15.197700     Load Stat > <
  15.745685     Bypass Stat >ACK<
  16.293254     Syst Stat >NAK<
  16.841260     Batt Stat >NAK<
  17.380907     Load Stat > <
  17.928482     Bypass Stat >ACK<
  18.476057     Syst Stat >NAK<
  19.024072     Batt Stat >NAK<
  19.564127     Load Stat > <
  20.112120     Bypass Stat >ACK<
  20.661797     Syst Stat >NAK<
  21.209370     Batt Stat >NAK<
  21.749011     Load Stat > <
  22.296625     Bypass Stat >ACK<
  22.844228     Syst Stat >NAK<
  23.391765     Batt Stat >NAK<
  23.930986     Load Stat > <
  24.479007     Bypass Stat >ACK<
  25.026991     Syst Stat >NAK<
  25.574981     Batt Stat >NAK<
  26.114199     Load Stat > <
  26.662221     Bypass Stat >ACK<
  27.218154     Got model name: NAK
  28.305355     Syst Stat >NAK<
  28.853759     Batt Stat >NAK<
  29.393839     Load Stat > <
  29.942250     Bypass Stat >ACK<
  30.490239     Syst Stat >NAK<
  31.038643     Batt Stat >NAK<
  31.577892     Load Stat > <
  32.125467     Bypass Stat >ACK<
  32.673042     Syst Stat >NAK<
  33.221031     Batt Stat >NAK<
  33.760281     Load Stat > <
  34.308272     Bypass Stat >ACK<
  34.855846     Syst Stat >NAK<
  35.403832     Batt Stat >NAK<
  35.943082     Load Stat > <
  36.490662     Bypass Stat >ACK<
  37.038232     Syst Stat >NAK<
  37.586645     Batt Stat >NAK<
  38.126741     Load Stat > <
  38.674711     Bypass Stat >ACK<
  39.223530     Syst Stat >NAK<
  39.771965     Batt Stat >NAK<
  40.311603     Load Stat > <
  40.859191     Bypass Stat >ACK<
  41.406753     Syst Stat >NAK<
  41.954768     Batt Stat >NAK<
  42.493990     Load Stat > <
  43.041567     Bypass Stat >ACK<
  43.589139     Syst Stat >NAK<
  44.137151     Batt Stat >NAK<
  44.676379     Load Stat > <
  45.224383     Bypass Stat >ACK<
  45.771941     Syst Stat >NAK<
  46.319959     Batt Stat >NAK<
  46.859592     Load Stat > <
  47.408005     Bypass Stat >ACK<
  47.955579     Syst Stat >NAK<
  48.504429     Batt Stat >NAK<
  49.043649     Load Stat > <
  49.591226     Bypass Stat >ACK<
  50.138799     Syst Stat >NAK<
  50.686814     Batt Stat >NAK<
  51.226039     Load Stat > <
  51.774032     Bypass Stat >ACK<
  52.329958     Got model name: NAK
  53.418006     Syst Stat >NAK<
  53.966009     Batt Stat >NAK<
  54.505259     Load Stat > <
  55.052837     Bypass Stat >ACK<
  55.601246     Syst Stat >NAK<
  56.149231     Batt Stat >NAK<
  56.688898     Load Stat > <
  57.236470     Bypass Stat >ACK<
  57.784042     Syst Stat >NAK<
  58.332033     Batt Stat >NAK<
  58.871281     Load Stat > <
  59.419276     Bypass Stat >ACK<
  59.967263     Syst Stat >NAK<
  60.515673     Batt Stat >NAK<
  61.055747     Load Stat > <
  61.604164     Bypass Stat >ACK<
  62.151731     Syst Stat >NAK<
  62.699726     Batt Stat >NAK<
  63.238974     Load Stat > <
  63.786961     Bypass Stat >ACK<
  64.334121     Syst Stat >NAK<
  64.882108     Batt Stat >NAK<
  65.421357     Load Stat > <
  65.968936     Bypass Stat >ACK<
  66.516507     Syst Stat >NAK<
  67.064497     Batt Stat >NAK<
  67.603748     Load Stat > <
  68.151322     Bypass Stat >ACK<
  68.698898     Syst Stat >NAK<
  69.247715     Batt Stat >NAK<
  69.786965     Load Stat > <
  70.334544     Bypass Stat >ACK<
  70.881703     Syst Stat >NAK<
  71.430104     Batt Stat >NAK<
  71.969768     Load Stat > <
  72.517348     Bypass Stat >ACK<
  73.064917     Syst Stat >NAK<
  73.612493     Batt Stat >NAK<
  74.152156     Load Stat > <
  74.700153     Bypass Stat >ACK<
  75.248560     Syst Stat >NAK<
  75.796131     Batt Stat >NAK<
  76.335377     Load Stat > <
  76.882950     Bypass Stat >ACK<
  77.438881     Got model name: NAK
  78.525657     Syst Stat >NAK<
  79.073686     Batt Stat >NAK<
  79.613743     Load Stat > <
  80.162151     Bypass Stat >ACK<
  80.709749     Syst Stat >NAK<
  81.257324     Batt Stat >NAK<
  81.796547     Load Stat > <
  82.344123     Bypass Stat >ACK<
  82.892137     Syst Stat >NAK<
  83.440127     Batt Stat >NAK<
  83.979350     Load Stat > <
  84.526926     Bypass Stat >ACK<
  85.074524     Syst Stat >NAK<
  85.622931     Batt Stat >NAK<
  86.162154     Load Stat > <
  86.710561     Bypass Stat >ACK<
  87.258162     Syst Stat >NAK<
  87.806150     Batt Stat >NAK<
  88.345373     Load Stat > <
  88.892950     Bypass Stat >ACK<
  89.440548     Syst Stat >NAK<
  89.988536     Batt Stat >NAK<
  90.528173     Load Stat > <
  91.075753     Bypass Stat >ACK<
  91.623770     Syst Stat >NAK<
  92.171757     Batt Stat >NAK<
  92.710980     Load Stat > <
  93.258559     Bypass Stat >ACK<
  93.806572     Syst Stat >NAK<
  94.354985     Batt Stat >NAK<
  94.894200     Load Stat > <
  95.441800     Bypass Stat >ACK<
  95.989376     Syst Stat >NAK<
  96.537367     Batt Stat >NAK<
  97.077003     Load Stat > <
  97.625023     Bypass Stat >ACK<
  98.173009     Syst Stat >NAK<
  98.721000     Batt Stat >NAK<
  99.260225     Load Stat > <
  99.807828     Bypass Stat >ACK<
 100.355400     Syst Stat >NAK<
 100.903388     Batt Stat >NAK<
 101.443885     Load Stat > <
 101.992295     Bypass Stat >ACK<
 102.548194     Got model name: NAK
 103.635417     Syst Stat >NAK<
 104.183000     Batt Stat >NAK<
 104.722252     Load Stat > <
 105.270247     Bypass Stat >ACK<
 105.817819     Syst Stat >NAK<
 106.366219     Batt Stat >NAK<
 106.905904     Load Stat > <
 107.453461     Bypass Stat >ACK<
 108.001056     Syst Stat >NAK<
 108.549051     Batt Stat >NAK<
 109.088271     Load Stat > <
 109.635856     Bypass Stat >ACK<
 110.183840     Syst Stat >NAK<
 110.731833     Batt Stat >NAK<
 111.271083     Load Stat > <
 111.818689     Bypass Stat >ACK<
 112.366716     Syst Stat >NAK<
 112.914664     Batt Stat >NAK<
 113.453885     Load Stat > <
 114.001878     Bypass Stat >ACK<
 114.549473     Syst Stat >NAK<
 115.097431     Batt Stat >NAK<
 115.636685     Load Stat > <
 116.184263     Bypass Stat >ACK<
 116.731834     Syst Stat >NAK<
 117.280263     Batt Stat >NAK<
 117.819921     Load Stat > <
 118.367487     Bypass Stat >ACK<
 118.915053     Syst Stat >NAK<
 119.463093     Batt Stat >NAK<
 120.002297     Load Stat > <
 120.549872     Bypass Stat >ACK<
 121.097441     Syst Stat >NAK<
 121.645455     Batt Stat >NAK<
 122.184712     Load Stat > <
 122.732261     Bypass Stat >ACK<
 123.279830     Syst Stat >NAK<
 123.828676     Batt Stat >NAK<
 124.367922     Load Stat > <
 124.915490     Bypass Stat >ACK<
 125.463048     Syst Stat >NAK<
 126.010686     Batt Stat >NAK<
 126.549882     Load Stat > <
 127.097484     Bypass Stat >ACK<
 127.653378     Got model name: NAK
 128.740599     Syst Stat >NAK<
 129.289014     Batt Stat >NAK<
 129.828236     Load Stat > <
 130.376254     Bypass Stat >ACK<
 130.923836     Syst Stat >NAK<
 131.471818     Batt Stat >NAK<
 132.011039     Load Stat > <
 132.558645     Bypass Stat >ACK<
 133.106216     Syst Stat >NAK<
 133.654204     Batt Stat >NAK<
 134.193428     Load Stat > <
 134.741032     Bypass Stat >ACK<
 135.288605     Syst Stat >NAK<
 135.837005     Batt Stat >NAK<
 136.376233     Load Stat > <
 136.923831     Bypass Stat >ACK<
 137.471822     Syst Stat >NAK<
 138.019810     Batt Stat >NAK<
 138.559060     Load Stat > <
 139.106640     Bypass Stat >ACK<
 139.654212     Syst Stat >NAK<
 140.202232     Batt Stat >NAK<
 140.742286     Load Stat > <
 141.290311     Bypass Stat >ACK<
 141.838262     Syst Stat >NAK<
 142.386667     Batt Stat >NAK<
 142.926339     Load Stat > <
 143.473910     Bypass Stat >ACK<
 144.021481     Syst Stat >NAK<
 144.569510     Batt Stat >NAK<
 145.109553     Load Stat > <
 145.657966     Bypass Stat >ACK<
 146.205119     Syst Stat >NAK<
 146.753108     Batt Stat >NAK<
 147.292357     Load Stat > <
 147.839933     Bypass Stat >ACK<
 148.387511     Syst Stat >NAK<
 148.935079     Batt Stat >NAK<
 149.474328     Load Stat > <
 150.021905     Bypass Stat >ACK<
 150.569481     Syst Stat >NAK<
 151.117468     Batt Stat >NAK<
 151.656718     Load Stat > <
 152.204323     Bypass Stat >ACK<
 152.760223     Got model name: NAK
 153.847413     Syst Stat >NAK<
 154.395441     Batt Stat >NAK<
 154.934664     Load Stat > <
 155.482241     Bypass Stat >ACK<
 156.030231     Syst Stat >NAK<
 156.579078     Batt Stat >NAK<
 157.118714     Load Stat > <
 157.666295     Bypass Stat >ACK<
 158.213864     Syst Stat >NAK<
 158.761879     Batt Stat >NAK<
 159.301104     Load Stat > <
 159.848680     Bypass Stat >ACK<
 160.396671     Syst Stat >NAK<
 160.944683     Batt Stat >NAK<
 161.483909     Load Stat > <
 162.031533     Bypass Stat >ACK<
 162.579062     Syst Stat >NAK<
 163.127073     Batt Stat >NAK<
 163.666299     Load Stat > <
 164.213873     Bypass Stat >ACK<
 164.761444     Syst Stat >NAK<
 165.309464     Batt Stat >NAK<
 165.848686     Load Stat > <
 166.396260     Bypass Stat >ACK<
 166.943828     Syst Stat >NAK<
 167.491432     Batt Stat >NAK<
 168.030653     Load Stat > <
 168.578233     Bypass Stat >ACK<
 169.126220     Syst Stat >NAK<
 169.675067     Batt Stat >NAK<
 170.214318     Load Stat > <
 170.761901     Bypass Stat >ACK<
 171.309474     Syst Stat >NAK<
 171.857486     Batt Stat >NAK<
 172.396682     Load Stat > <
 172.944255     Bypass Stat >ACK<
 173.492302     Syst Stat >NAK<
 174.040676     Batt Stat >NAK<
 174.579895     Load Stat > <
 175.127520     Bypass Stat >ACK<
 175.675504     Syst Stat >NAK<
 176.223488     Batt Stat >NAK<
 176.762703     Load Stat > <
 177.310309     Bypass Stat >ACK<
 177.866237     Got model name: NAK
 178.953439     Syst Stat >NAK<
 179.501457     Batt Stat >NAK<
 180.040707     Load Stat > <
 180.588261     Bypass Stat >ACK<
 181.136242     Syst Stat >NAK<
 181.684237     Batt Stat >NAK<
 182.223494     Load Stat > <
 182.771056     Bypass Stat >ACK<
 183.318215     Syst Stat >NAK<
 183.866207     Batt Stat >NAK<
 184.405452     Load Stat > <
 184.953029     Bypass Stat >ACK<
 185.500602     Syst Stat >NAK<
 186.048590     Batt Stat >NAK<
 186.588674     Load Stat > <
 187.137081     Bypass Stat >ACK<
 187.684653     Syst Stat >NAK<
 188.232644     Batt Stat >NAK<
 188.771893     Load Stat > <
 189.319468     Bypass Stat >ACK<
 189.867048     Syst Stat >NAK<
 190.415030     Batt Stat >NAK<
 190.954279     Load Stat > <
 191.502273     Bypass Stat >ACK<
 192.049845     Syst Stat >NAK<
 192.597453     Batt Stat >NAK<
 193.136667     Load Stat > <
 193.685106     Bypass Stat >ACK<
 194.232650     Syst Stat >NAK<
 194.780644     Batt Stat >NAK<
 195.319891     Load Stat > <
 195.867468     Bypass Stat >ACK<
 196.415037     Syst Stat >NAK<
 196.963021     Batt Stat >NAK<
 197.502307     Load Stat > <
 198.049857     Bypass Stat >ACK<
 198.597460     Syst Stat >NAK<
 199.145828     Batt Stat >NAK<
 199.685084     Load Stat > <
 200.232657     Bypass Stat >ACK<
 200.779813     Syst Stat >NAK<
 201.327802     Batt Stat >NAK<
 201.866640     Load Stat > <
 202.414247     Bypass Stat >ACK<
 202.970143     Got model name: NAK
 204.057767     Syst Stat >NAK<
 204.607045     Batt Stat >NAK<
 205.146665     Load Stat > <
 205.694706     Bypass Stat >ACK<
 206.243108     Syst Stat >NAK<
 206.791501     Batt Stat >NAK<
 207.331596     Load Stat > <
 207.880000     Bypass Stat >ACK<
 208.427163     Syst Stat >NAK<
 208.975165     Batt Stat >NAK<
 209.514792     Load Stat > <
 210.062369     Bypass Stat >ACK<
 210.609943     Syst Stat >NAK<
 211.158348     Batt Stat >NAK<
 211.698012     Load Stat > <
 212.245593     Bypass Stat >ACK<
 212.792748     Syst Stat >NAK<
 213.340735     Batt Stat >NAK<
 213.879985     Load Stat > <
 214.427984     Bypass Stat >ACK<
 214.975589     Syst Stat >NAK<
 215.523535     Batt Stat >NAK<
 216.062793     Load Stat > <
 216.610400     Bypass Stat >ACK<
 217.158358     Syst Stat >NAK<
 217.706340     Batt Stat >NAK<
 218.245590     Load Stat > <
 218.792752     Bypass Stat >ACK<
 219.340328     Syst Stat >NAK<
 219.888730     Batt Stat >NAK<
 220.427981     Load Stat > <
 220.975557     Bypass Stat >ACK<
 221.522712     Syst Stat >NAK<
 222.070701     Batt Stat >NAK<
 222.609535     Load Stat > <
 223.157112     Bypass Stat >ACK<
 223.705102     Syst Stat >NAK<
 224.253507     Batt Stat >NAK<
 224.792762     Load Stat > <
 225.340361     Bypass Stat >ACK<
 225.889568     Syst Stat >NAK<
 226.437179     Batt Stat >NAK<
 226.976810     Load Stat > <
 227.524384     Bypass Stat >ACK<
 228.079910     Got model name: NAK
 229.166669     Syst Stat >NAK<
 229.714741     Batt Stat >NAK<
 230.254791     Load Stat > <
 230.802755     Bypass Stat >ACK<
 231.350765     Syst Stat >NAK<
 231.898337     Batt Stat >NAK<
 232.438002     Load Stat > <
 232.985558     Bypass Stat >ACK<
 233.533151     Syst Stat >NAK<
 234.081138     Batt Stat >NAK<
 234.620369     Load Stat > <
 235.167941     Bypass Stat >ACK<
 235.715956     Syst Stat >NAK<
 236.264361     Batt Stat >NAK<
 236.804415     Load Stat > <
 237.352056     Bypass Stat >ACK<
 237.899628     Syst Stat >NAK<
 238.447616     Batt Stat >NAK<
 238.987255     Load Stat > <
 239.534849     Bypass Stat >ACK<
 240.082423     Syst Stat >NAK<
 240.630384     Batt Stat >NAK<
 241.169189     Load Stat > <
 241.716800     Bypass Stat >ACK<
 242.264819     Syst Stat >NAK<
 242.812362     Batt Stat >NAK<
 243.352448     Load Stat > <
 243.900448     Bypass Stat >ACK<
 244.448423     Syst Stat >NAK<
 244.996435     Batt Stat >NAK<
 245.536491     Load Stat > <
 246.084063     Bypass Stat >ACK<
 246.632475     Syst Stat >NAK<
 247.180046     Batt Stat >NAK<
 247.719291     Load Stat > <
 248.266872     Bypass Stat >ACK<
 248.814859     Syst Stat >NAK<
 249.362846     Batt Stat >NAK<
 249.902518     Load Stat > <
 250.450086     Bypass Stat >ACK<
 250.997663     Syst Stat >NAK<
 251.546068     Batt Stat >NAK<
 252.085733     Load Stat > <
 252.634139     Bypass Stat >ACK<
 253.190482     Got model name: NAK
 254.277716     Syst Stat >NAK<
 254.826125     Batt Stat >NAK<
 255.365760     Load Stat > <
 255.913335     Bypass Stat >ACK<
 256.460937     Syst Stat >NAK<
 257.008505     Batt Stat >NAK<
 257.548562     Load Stat > <
 258.096973     Bypass Stat >ACK<
 258.645025     Syst Stat >NAK<
 259.193004     Batt Stat >NAK<
 259.732638     Load Stat > <
 260.280248     Bypass Stat >ACK<
 260.827798     Syst Stat >NAK<
 261.375819     Batt Stat >NAK<
 261.915034     Load Stat > <
 262.462606     Bypass Stat >ACK<
 263.010613     Syst Stat >NAK<
 263.558586     Batt Stat >NAK<
 264.098219     Load Stat > <
 264.645824     Bypass Stat >ACK<
 265.194643     Syst Stat >NAK<
 265.742672     Batt Stat >NAK<
 266.282298     Load Stat > <
 266.829882     Bypass Stat >ACK<
 267.377872     Syst Stat >NAK<
 267.925466     Batt Stat >NAK<
 268.465108     Load Stat > <
 269.012709     Bypass Stat >ACK<
 269.560259     Syst Stat >NAK<
 270.108656     Batt Stat >NAK<
 270.648321     Load Stat > <
 271.196315     Bypass Stat >ACK<
 271.744726     Syst Stat >NAK<
 272.293124     Batt Stat >NAK<
 272.832821     Load Stat > <
 273.379957     Bypass Stat >ACK<
 273.927941     Syst Stat >NAK<
 274.476344     Batt Stat >NAK<
 275.015594     Load Stat > <
 275.563172     Bypass Stat >ACK<
 276.111158     Syst Stat >NAK<
 276.659604     Batt Stat >NAK<
 277.199644     Load Stat > <
 277.747226     Bypass Stat >ACK<
 277.747283     Could not get multiplier table: using raw readings.
 278.295270     initinfo: battery.charge == >000.0<
 278.842839     initinfo: battery.runtime == >00000<
 279.390856     initinfo: battery.voltage == >000.0<
 279.947187     initinfo: battery.charge.low == >00<
 280.503475     initinfo: battery.voltage.nominal == >000.0<
 281.051047     initinfo: ups.temperature == >000.0<
 281.590714     initinfo: ups.load == >000.0<
 282.146660     initinfo: ups.delay.start == >000<
 282.702980     initinfo: ups.delay.shutdown == >000<
 283.259275     initinfo: ups.test.interval == >000<
 283.799355     initinfo: output.voltage == >000.0<
 284.338585     initinfo: output.current == >000.0<
 284.878253     initinfo: input.voltage == >000.0<
 285.417533     initinfo: input.frequency == >00.00<
 285.965501     initinfo: input.transfer.low == >000.0<
 286.513072     initinfo: input.transfer.boost.low == >000.0<
 287.061470     initinfo: input.transfer.boost.high == >000.0<
 287.609884     initinfo: input.transfer.trim.low == >000.0<
 288.157929     initinfo: input.transfer.high == >000.0<
 288.706306     initinfo: input.transfer.trim.high == >000.0<
...........Detected NAK on /dev/ttyS0
 290.803627     Syst Stat >NAK<
 291.351221     Batt Stat >NAK<
 291.890860     Load Stat > <
 292.438438     Bypass Stat >ACK<
 292.986035     Syst Stat >NAK<
 293.533610     Batt Stat >NAK<
 294.073247     Load Stat > <
 294.620827     Bypass Stat >ACK<
 295.168423     Syst Stat >NAK<
 295.715997     Batt Stat >NAK<
 296.255222     Load Stat > <
 296.802797     Bypass Stat >ACK<
 297.350371     Syst Stat >NAK<
 297.897972     Batt Stat >NAK<
 298.437191     Load Stat > <
 298.984770     Bypass Stat >ACK<
 299.532784     Syst Stat >NAK<
 300.080773     Batt Stat >NAK<
 300.619997     Load Stat > <
 301.167156     Bypass Stat >ACK<
 301.714730     Syst Stat >NAK<
 302.262327     Batt Stat >NAK<
 302.801966     Load Stat > <
 303.349129     Bypass Stat >ACK<
 303.896701     Syst Stat >NAK<
 304.444301     Batt Stat >NAK<
 304.983940     Load Stat > <
 305.531936     Bypass Stat >ACK<
 306.080778     Syst Stat >NAK<
 306.628768     Batt Stat >NAK<
 307.168407     Load Stat > <
 307.715568     Bypass Stat >ACK<
 308.263168     Syst Stat >NAK<
 308.810739     Batt Stat >NAK<
 309.349963     Load Stat > <
 309.897539     Bypass Stat >ACK<
 310.445139     Syst Stat >NAK<
 310.993128     Batt Stat >NAK<
 311.533183     Load Stat > <
 312.081202     Bypass Stat >ACK<
 312.628777     Syst Stat >NAK<
 313.176346     Batt Stat >NAK<
 313.715572     Load Stat > <
 314.262757     Bypass Stat >ACK<
 314.262813     updateinfo: Cannot update system status
 314.262826     disable_ups_comm()
 317.359033     updateinfo: battery.charge == >000.0<
 317.907030     updateinfo: battery.runtime == >00000<
 318.455858     updateinfo: battery.voltage == >000.0<
 319.011767     updateinfo: battery.charge.low == >00<
 319.568085     updateinfo: battery.voltage.nominal == >000.0<
 320.115682     updateinfo: ups.temperature == >000.0<
 320.655320     updateinfo: ups.load == >000.0<
 321.211235     updateinfo: ups.delay.start == >000<
 321.767154     updateinfo: ups.delay.shutdown == >000<
 322.323044     updateinfo: ups.test.interval == >000<
 322.862714     updateinfo: output.voltage == >000.0<
 323.401970     updateinfo: output.current == >000.0<
 323.941198     updateinfo: input.voltage == >000.0<
 324.480453     updateinfo: input.frequency == >00.00<
 325.028439     updateinfo: input.transfer.low == >000.0<
 325.576017     updateinfo: input.transfer.boost.low == >000.0<
 326.124002     updateinfo: input.transfer.boost.high == >000.0<
 326.671994     updateinfo: input.transfer.trim.low == >000.0<
 327.220004     updateinfo: input.transfer.high == >000.0<
 327.767993     updateinfo: input.transfer.trim.high == >000.0<
 327.780022     dstate_init: sock /var/state/ups/mge-utalk-ups0 open on fd 5
 329.876572     Syst Stat >NAK<
 330.424171     Batt Stat >NAK<
 330.963824     Load Stat > <
 331.511400     Bypass Stat >ACK<
 332.059387     Syst Stat >NAK<
 332.607403     Batt Stat >NAK<
 333.147042     Load Stat > <
 333.694618     Bypass Stat >ACK<
 334.242192     Syst Stat >NAK<
 334.789791     Batt Stat >NAK<
 335.329845     Load Stat > <
 335.877837     Bypass Stat >ACK<
 336.425853     Syst Stat >NAK<
 336.973426     Batt Stat >NAK<
 337.513093     Load Stat > <
 338.061063     Bypass Stat >ACK<
 338.608689     Syst Stat >NAK<
_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to