On 2013-06-14 23:16, ML mail wrote:
Thanks for the help, with the apcsmart-old driver it works again! Didn't
notice my UPS is now so "old" ;-)

Here is the output of upsc with apcsmart-old driver:

battery.alarm.threshold: 0
battery.charge: 100.0
battery.charge.restart: 00
battery.date: 11/22/06
battery.packs: 001
battery.packs.bad: 000
battery.runtime: 540
battery.runtime.low: 120
battery.voltage: 53.73
battery.voltage.nominal: 048
device.mfr: APC
device.model: Smart-UPS RT 2000 XL
device.serial:
device.type: ups
driver.name: apcsmart-old
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS7
driver.version: 2.6.4
driver.version.internal: 2.1
input.frequency: 49.98
input.quality: FF
input.sensitivity: A
input.transfer.high: 253
input.transfer.low: 161
input.transfer.reason: simulated power failure or UPS test
input.voltage: 233.2
input.voltage.maximum: 233.2
input.voltage.minimum: 233.2
output.voltage: 229.3
output.voltage.nominal: 230
ups.delay.shutdown: 020
ups.delay.start: 000
ups.display.language: E
ups.firmware: 416.7.I
ups.firmware.old: 5YI
ups.id: UPS_IDEN
ups.load: 063.0
ups.mfr: APC
ups.mfr.date: 11/22/06
ups.model: Smart-UPS RT 2000 XL
ups.serial:
ups.status: OL
ups.temperature: 034.6
ups.test.interval: 1209600
ups.test.result: NO

and here with apcsmart driver:

battery.charge: 100.0
battery.voltage: 53.73
device.mfr: APC
device.model: Smart-UPS RT 2000 XL
device.serial:
device.type: ups
driver.name: apcsmart
driver.parameter.pollinterval: 2
driver.parameter.port: /dev/ttyS7
driver.version: 2.6.4
driver.version.internal: 3.04
input.voltage: 233.2
output.voltage: 229.3
ups.firmware: 416.7.I
ups.load: 063.0
ups.mfr: APC
ups.model: Smart-UPS RT 2000 XL
ups.serial:
ups.status: OL
ups.temperature: 034.6


The "new" output is extremely terse, suggesting that it failed some regex check and went back to barebone essentials in panic. Anything in logs ?

If you could start the driver manually with

apcsmart -DDDDDDDDD -a <id>

and send me output, that would likely shed some light on the issue.

Thanks.


_______________________________________________
Nut-upsuser mailing list
[email protected]
http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser

Reply via email to