On Jun 29, 2013, at 9:45 AM, Mike. wrote: > On 6/29/2013 at 9:14 AM Mike. wrote: > > |NUT 2.6.5 on FreeBSD 9.1 > | > | > |Why isn't the variable outlet.1.delay.shutdown set with the following > |command? > | > | > | > |# upsc PW5125@localhost | grep "outlet.1.delay.shutdown" > |outlet.1.delay.shutdown: -1 > | > |# upsrw -u au -p ap -s outlet.1.delay.shutdown PW5125@localhost > |Enter new value for outlet.1.delay.shutdown: 10 > |OK > | > |# upsc PW5125@localhost | grep "outlet.1.delay.shutdown" > |outlet.1.delay.shutdown: -1 > | > | > | > | > |Am I missing something obvious? > ============= > > > Forgot to add ups.conf: > > > [PW5125] > driver = bcmxcp > port = /dev/cuau0 > baud_rate = 9600 > desc = "PW 5125 - 1500"
I was just going to gripe about the lack of driver information :-) Sounds similar to Pascal's question: http://lists.alioth.debian.org/pipermail/nut-upsuser/2013-June/008462.html Do you see anything from syslog at LOG_NOTICE? In theory, the bcmxcp driver should log a message if the parameter change is refused by the UPS. If not, you could try re-running the driver with a few -D flags. That will show some information on the commands and responses. We also have a bcmxcp branch that has a few fixes beyond v2.6.5, but none of them seem particularly relevant. Arnaud mentioned that some of the PowerWare devices have a USB HID interface that may be more fully mapped out. If you have a USB port on the UPS, you could try changing the parameter with usbhid-ups, then switching back to bcmxcp for long-term monitoring. -- Charles Lepple clepple@gmail _______________________________________________ Nut-upsuser mailing list [email protected] http://lists.alioth.debian.org/cgi-bin/mailman/listinfo/nut-upsuser